Dear all,

Any one can assist whether manhole can be waived while one handhole already provided in Air Receiver Tank (vessel) is 1.2m Dia x 1.8m T/T H. Is that any recommended practice can be used as reference?

Understand refer to ASME UG-46 a) stated that suitable manhole, handhole or other inspection opening for examination and cleaning.

For further information that air is dry clean air type where the Air Receiver Tank equipped with an auto liquid trap and moisture analyzer.

Meaning that there will be less maintenance for the Air Receiver Tank.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#1

Re: Manhole and Handhole Requirement

06/08/2020 8:17 AM

Is this an ASME vessel or are you building this pressure vessel to another set of rules ?

As per ASME Pressure Vessel Code Section VIII div 1, UG-46 :
"All vessels 18 in. (450 mm) to 36 in. (900 mm), inclusive, I.D. shall have a manhole or at least two handholes or two plugged, threaded inspection openings of not less than NPS 2 (DN 50)."

https://www.eng-tips.com/viewthread.cfm?qid=402958

I believe that you may need at least two handholes .....

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Associate

Join Date: Aug 2008
Posts: 25
#2
In reply to #1

Re: Manhole and Handhole Requirement

06/08/2020 10:40 PM

that vessel is new build, and realized there is only one handhole provided instead of manhole.

you are right that there is possibility to provide two hand hole (4 in) as per UG-49 f).

thanks

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Manhole and Handhole Requirement

06/08/2020 10:47 PM

Liquid traps malfunction, people can misunderstand or ignore analyzer readings, so there is good reason to expect moisture in the tank, rather than an application such as an argon processing plant where water contamination might be unexpected. Where a weld failure might lead to loss of life or property, not good to skimp on provisions to make inspection easy & fast. Just good common sense, for your business.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Manhole and Handhole Requirement

06/09/2020 5:08 AM

<...Any one can assist ...>

Yes. The Engineer/Surveyor for the company that is providing burst/collapse indemnity insurance cover on the equipment can certainly assist. Telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

MJCronin (1); PWSlack (1); rwilliams (1); Ynnor (1)

Previous in Forum: Parts Desperation   Next in Forum: Type of Bolt

Advertisement