AC Leakage In Third Harmonic Current Tester

11/02/2007 12:29 AM

Plz suggest how to measure the third harminics leakage current.The testing system voltage is 600kv.Leakage current up to 7 mili-amp.for the detection of the health of the product.(arrestor) If any company is providing the same instrument plz tell me.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ac leakage current third harmonic tester

11/02/2007 7:29 AM

<third harminics leakage current>

Eh?

The third harmonic is a waveform distortion, at three times the fundamental frequency, that is an expression of the departure of a waveform from a pure sine-wave shape at the fundamental frequency. To use a musical analogy, the G in the second octave above middle C is its third harmonic. Harmonics can be measured using a frequency-domain instrument such as a spectrum analyser.

Leakage current in an electrical system is the difference between the vector sum of the instantaneous currents on each phase conductor and the instantaneous current vector in the neutral conductor. This current appears in the earth conductor and its presence is mostly used to determine and isolate an insulation fault among the other conductors. A simple ammeter placed in the earth conductor would measure this current, though it needs to be carried out under closely-controlled conditions to prevent user electric shock.

Without further information, they are two unrelated concepts.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2006
Location: Cape Town
Posts: 88
Good Answers: 1
#3
In reply to #1

Re: ac leakage current third harmonic tester

11/03/2007 4:42 AM

The missing information that you asked for, is the "arrestor" that tecspert did mention ie. surge-arrestor; these are non-linear devices that conduct more as the 50Hz (or 60Hz) sine voltage increases. The surge-arrestor will conduct exponentially increasing amounts of current as the 50Hz sine voltage goes through its peaks. This leakage current can have high levels of 3rd harmonic (and other odd harmonics). It is therefore useful to measure the 3rd harmonic content of current through the surge-arrestor to test its health and also monitor whether the correct surge-arrestor type has been installed.

Register to Reply
Commentator

Join Date: Oct 2006
Location: Cape Town
Posts: 88
Good Answers: 1
#2

Re: AC Leakage In Third Harmonic Current Tester

11/02/2007 11:37 PM

We may be able to help you... take a look at our website and drop me an email, and we can talk about physical configurations and other requirements etc.

www.suretech.co.za

NeilJ

Register to Reply
Register to Reply 3 comments

Previous in Forum: Mosfet Parallel   Next in Forum: Harmonics

Advertisement