Neutral Wire Having Current

09/17/2020 10:16 AM

What causes the neutral conductor of a three phase four wire to have current when switched on load(the neutral having current and one of the phase becomes neutral with no current)? Before switching onto load, the four wires is complete three phase one neutral (with no current) .How can these be corrected?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral wire having current

09/17/2020 10:38 AM

https://en.wikipedia.org/wiki/Ground_and_neutral explains all.

Of course the neutral carries current. That is what it is there for. There is nothing to <... be corrected...>.

A current in the neutral merely indicates an imbalance between the phase currents. In the limit, i.e. zero load current on two of the three phases, the neutral current is the same as the phase current as it is the neutral conductor that is completing the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Neutral wire having current

09/17/2020 10:54 AM

This sounds like a homework question.

The only way the neutral conductor has current on it is if the vector sum of all three current phases is not zero. The simplest method to force this condition is to not connect the neutral to any load, including wiring leakage paths. Remove the neutral wire. Doing this and nothing else in addition will mean whatever is drawing the imbalanced power will now be without power.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate
Engineering Fields - Electrical Engineering - seek knowledge

Join Date: Sep 2007
Location: Nigeria
Posts: 50
#4
In reply to #2

Re: Neutral wire having current

09/17/2020 12:08 PM

If I did not connect the neutral of the supply before switching on load ,would that correct the anormally ,whereby it can be reconnected again? What about other electric equipment in the load system that is single phase and need the neutral to work?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Neutral wire having current

09/17/2020 12:12 PM

The <...single phase...equipment...> either wouldn't work or, if spread across more than one phase, would result in some really silly voltages appearing at their inlet terminals.

<...not connect the neutral of the supply before switching on load ,would that correct the anormally...> no, it wouldn't.

The phrase <...one of the phase becomes neutral with no current...> is nonsensical at present.

The thing to be embraced is that there is nothing to be corrected; that is the job of the neutral conductor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Neutral wire having current

09/17/2020 12:22 PM

Yes, the neutral is doing its job and there is no stated need to reduce the neutral current to zero.

On the off chance that there is a valid but unstated reason for reducing the neutral current to zero (I have no idea what this reason might be) while still powering something with the lower voltage of phase to neutral then a step down transformer could be added that takes phase to phase power to the desired voltage.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Neutral wire having current

09/17/2020 11:10 AM

Two reasons come to mind for neutral current in a 3 phase system. The first, of course, is an unbalanced load. The second is if the load is non-linear.

Even with a balanced load, for example, fluorescent lighting will generate neutral current at 3 times the line frequency (180 hz in US). This is because the current conducts at the voltage cycle peaks resulting in a non-sinusoidal waveform containing a large amount of third harmonic content. Each of the three phase currents add in phase for third and multiples of the third harmonic.

Fluorescent Light with Magnetic Ballast

https://www.researchgate.net/publication/319370332_Performance_analysis_of_fluorescent_and_led_lamp_system

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#7
In reply to #3

Re: Neutral wire having current

09/17/2020 5:30 PM

And more specifically on the issue of triplens harmonics:

https://electrical-engineering-portal.com/what-are-triplen-harmonics

Data centers with the plurality of the loads being non-linear (before power factor corrected supplies became de rigueur) used to have significant neutral currents.

Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8

Re: Neutral Wire Having Current

09/17/2020 10:59 PM

In your question, you state that one of the phases becomes neutral, which could be confusing. There is only one neutral, electrically, and it doesn’t move around.

It’s possible that one of your breaker poles is open circuited, or your load or wire has an open phase circuit.

If you have 3 phase heat connected, you are likely running at 2/3 capacity, a 3 phase rotating load such as induction motor will just sit & hum, draw lots of current, and not turn.

If you have just 2 single phase loads, everything is normal, as everyone else has stated.

Register to Reply Good Answer (Score 2)
Associate
Engineering Fields - Electrical Engineering - seek knowledge

Join Date: Sep 2007
Location: Nigeria
Posts: 50
#9
In reply to #8

Re: Neutral Wire Having Current

09/18/2020 3:44 AM

But the three phase motor are rotating well

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Neutral Wire Having Current

09/18/2020 4:37 AM

One wouldn't expect anything else.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#12
In reply to #9

Re: Neutral Wire Having Current

09/18/2020 10:40 AM

Friend,

A typical 3-phase 4-wire system has three phase (hot or live) wires and one neutral wire which is electrically in the center between the three phase wires. Picture this as an equilateral triangle with the three phase wires at the corners and the neutral in the very center of the triangle. Then draw lines from each corner to the center (and leave the lines between the corners in place). A single-phase load is between any corner and the neutral. A higher-voltage single-phase load (connected to two of the phase conductors without any connection to the neutral) is sometimes called a 2-phase load, but is electrically still a single-phase load. A 3-phase load is only between corners. [2-phase loads are with the phases 90-degrees apart and are drawn with 1-wire in the center and 2 or 4 wires on lines at right angles from the center. These are fairly rare, as are 6-phase circuits!]

So, a 3-phase motor will run if all three phases are energized and is independent of the neutral and the currents drawn on each phase should be equal. When you add single-phase loads, each one puts equal amounts of current on the phase and neutral wires attached to that load. If you have many single-phase circuits divided onto different phase-neutral loads the neutral will carry the sum of all the individual circuits. However since the waveform for each phase's currents are 120-degrees apart, the instantaneous currents in some are going positive while the currents in others are going negative and the actual sum is the imbalance (the vector sum) between all the phase currents, NOT the arithmetic (scalar) sum of them.

As others have pointed out, when you are dealing with loads that are not linear (typically those supplying electronic equipment) the loads impose harmonics (multiples) of the input wave form onto the wires. Certain ones of these harmonics do NOT cancel, so the neutral can carry current even if the non-linear loads are all equal. That is why the codes require the neutral conductor to be larger than the phase conductors for non-linear loads (while allowing it to be smaller otherwise)!

Have fun learning the physics and theory behind electricity, as well as the practical of what you will run into each day. The more you know, the better-equipped you will be to troubleshoot and fix the causes of problems you see in your work. You can reset a breaker that has tripped--that eliminates the symptom, but hasn't looked for and found the cause.

--JMM

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #9

Re: Neutral Wire Having Current

09/18/2020 11:38 AM

It’s possible we don’t understand the question, perhaps a table of the line to neutral voltages and line currents before & after closing the breaker?

Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#14

Re: Neutral Wire Having Current

09/18/2020 7:24 PM

Are you running a "Y" or Delta? I'm assuming Delta, since you're not expecting current on the neutral.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Associate
Engineering Fields - Electrical Engineering - seek knowledge

Join Date: Sep 2007
Location: Nigeria
Posts: 50
#15

Re: Neutral Wire Having Current

09/19/2020 11:08 AM

I am deeply thankful to all of your experiences,knowledge and expertise shared here.I was able to resolve this issues from ideas garnered here. Thank you all

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#17
In reply to #15

Re: Neutral Wire Having Current

09/22/2020 10:27 AM

So what was the outcome, Mildred?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#16

Re: Neutral Wire Having Current

09/20/2020 7:49 AM

Harmonics

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Autobroker (1); Brave Sir Robin (1); Crabtree (1); dgoldwaters (3); gutmonarch (1); jmueller (1); PWSlack (3); redfred (2); Rixter (1); rwilliams (2)

Previous in Forum: A Question of Speed   Next in Forum: Reversed Tear Drop

Advertisement