Grounding - NEC Standards

11/07/2007 1:20 PM

Location US

Need to conform to NEC standards. I have been given uncertain answers about proper grounding.

Crude example^

Is it against NEC code (I've looked but I am just as confused afterward) to have the 480VAC ground to terminate to a ground lug on a components before going to the ground plate? Should it be connected directly to ground plate?

The back panel was redesigned and the ground plate remained in approximately the same location however the grounding wire will not reach. Available solution is to terminate to SCR ground lug Figure A (easier) or move ground plate to new location Figure B (harder as already installed in field).

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Grounding - NEC Standards

11/07/2007 2:20 PM

It will be difficult to make this pass. The extra connection will add resistance between the equipment and the ground. Even a straight wire will fail if it is too long.

The NEC code is based on a specific ohm maximum between the equipment and the ground plate.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Anonymous Poster
#2

Re: Grounding - NEC Standards

11/08/2007 5:05 AM

Assumption from examples given is that the application is an equipment ground and not the power supply ground or neutral.

If so, both methods are acceptable.

If you route the ground as in example "A", you should CADWELD "T" bond the two conductors together with a correctly sized "pigtail" extension and then attach the pigtail to the enclosure grounding connection/bus. This will ensure that a "high-resistance" connection is not created and the conductor then will be able to maintain the required "low-impedance" (<.7ohm) equipment grounding path.

If you choose to use example "B", both conductors must be either "bonded" (CADWELD or similar method of welded connection) or bolted together at the common point with crimped or welded terminals if attaching to an existing grounding grid connection.

Register to Reply
Associate

Join Date: Aug 2007
Location: Boston area
Posts: 38
#3

Re: Grounding - NEC Standards

11/08/2007 8:01 AM

Why would the manufacturer provide a ground lug and a ground pad and not connect them? Ask the manufacturer what they recommend.

Register to Reply
Anonymous Poster
#4

Re: Grounding - NEC Standards

11/08/2007 10:04 AM

I think it depends on how your grounds are actually protection grounding. It looks like your controller probably separates itself from the main power system before it sends power to your motor. I vote for A because it would be the shortest grounding wire for the power system input and the controller output.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#5

Re: Grounding - NEC Standards

11/10/2007 8:16 AM

Earth ground is terminated at the service entrance or distribution point. The equipment ground is run with the circuit wiring and bonds all equipment along it's path. Don't hesitate to ask ths inspector how he wants the ground designed. He will appreciate the request and things will go much smoother.

250.24C1 "shall be routed with the phase conductors..."

Good luck,

James

__________________
" adapt, improvise, overcome "
Register to Reply