Diesel Generators And Power Factor

11/12/2007 11:59 AM

If I improve the power factor of a generator's load from 0.7 to 0.9, will there be some fuel savings to be made?

If so, how?

Register to Reply
Pathfinder Tags: Power Factor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#1

Re: Diesel Generators And Power Factor

11/12/2007 11:03 PM

Good question.

In theory no. The kW output of the engine would be the same.

However, the reduced current output of the alternator would give less internal losses. Thus a lower kW draw from the engine.

However however, since a reasonable size alternator is better than 90% efficient, this will not equate to a large difference.

Note that since genset output is traditionally quoted as "kVA @ 0.8pf", running at 0.7 is compromising your current draw.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#2

Re: Diesel Generators And Power Factor

11/13/2007 12:16 AM

The rated out put of Alternator are at 0.8 p.f

The connected load at improved p.f should not exceed the rated AMP of Alternator.

Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#3

Re: Diesel Generators And Power Factor

11/13/2007 3:07 AM

Dear Nezz,

Answer for your Question is No fuel saving is possible.If you operate the engine at higher power factor the full load current rating of Alternator will be reducing since the engine designed for a particular Power Factor.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#4

Re: Diesel Generators And Power Factor

11/14/2007 11:42 AM

In spite of what others are saying... The better PF will reduce the currents in the generator (and other circuits) and have an effect on the fuel consumption.

1. All electrical circuits have resistance ( including the generator windings)

2. Current through any resistance causes heat. W = I2 R (this is Gods Law)

3. Heat is energy and energy is power. Your Generator is supplying the power.

4. The power comes from the fuel.

Depending on the size and design of the machine, the energy savings may be large or insignificant.

What I am saying is that the RVA (I + jx ) currents are useless for extracting power but Resistance losses (due to reactive currents) must be generated by the generator.

Snakers

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2007
Location: Cleveland, Ohio
Posts: 100
Good Answers: 2
#5

Re: Diesel Generators And Power Factor

11/15/2007 1:49 PM

There is a way to get more fuel economy out of your generator.

Schaeffer Manufacturing has a fuel additive that typically reduces fuel consumption by 10%. Their engine oil should also contribute up to 5% savings.

Call me for info if you like: 216-401-1845 ( lubricants@rgreenwald.com )

__________________
THEOILGUY55
Register to Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#6

Re: Diesel Generators And Power Factor

12/11/2007 10:17 PM

PF correction does not save fuel. Reactive power is not watts, and the engine power (fuel consumption) demand is ONLY related to watts. Correcting power factor reduces amps, and that will save you some generator (alternator) insulation breakdown in the long term (less heat rise).

Hope this saves you a ton of money NOT buying power factor correction items. I am 100% sure of this.

__________________
If it eats, it's going to be trouble!
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BabyGuinness (1); G.Swaminathan (1); nascon (1); PetroPower (1); Snakers (1); THEOILGUY55 (1)