Relay's contact capacity

11/13/2007 8:47 AM

I have relay with contact: for 220 V DC; 0,2 A (L/R=40 ms). I am doubtful what I ought to do with this contact for 110 V DC ?. What capacity of contact for 110 v DC ?.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Sep 2007
Location: Reno, NV (USA)
Posts: 608
Good Answers: 66
#1

Re: Relay's contact capacity

11/13/2007 11:23 AM

If I understand your question correctly, amp rating will be the same at 110 VDC and 220 VDC.

__________________
Aequam memento rebus in arduis servare mentem.
Register to Reply Good Answer (Score 2)
Participant

Join Date: May 2007
Posts: 2
#2

Re: Relay's contact capacity

11/13/2007 4:14 PM

The Voltage rating tells you about the maximum Voltage you can apply irrespective of the current , and the current rating tells you about maximum current through closed contact ( when there is no voltage across the contacts ) irrespective of initial voltage .

Register to Reply
Anonymous Poster
#3

Re: Relay's contact capacity

11/14/2007 12:25 AM

Some big contactor manufacturers mention KW (VA) ratings on contactors along with normal current and voltage ratings. I think in this case you can safely use for 110V but can not exeed current.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Relay's contact capacity

11/14/2007 4:19 AM

To qualify the above, all of them worthy responses, it needs to be stated that these are the manufacturer's recommended maxima for current and voltage. Exceeding them may cause deterioration ranging from 'absolutely no effect' to 'total destruction of the device' in ways that have not been investigated, assessed or quantified. The ratings are therefore conservative and intended for the long-term survival of the device, which may be tested and rated by them for >105 operations, perhaps.

Closing this particular contact at 250V/0.3A, for example, might have very little effect, or it might go bang and start smoking, and therefore the user is outside the manufacturer's recommended comfort zone for the device. If in doubt, substitute a device with a higher rating that encompasses the intended range of currents and voltages to be anticipated in the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CSM Engineer (1); faramarzfaridani (1); PWSlack (1)

Previous in Forum: Fastest Rotation Of An Electric Motor   Next in Forum: Power Electronics Project

Advertisement