Insulation Resistance

12/24/2020 5:55 AM

Dear all

When we checked the insulation resistance for generator we show there are a difference

between reading:

R-E =320 M ohm ,S-E = 305 M ohm ,T-E = 240 M ohm

please what is the possible causes of this difference and are this difference

acceptable ,are there any standard value for difference in insulation between phases

thanks for all

Register to Reply
Pathfinder Tags: Insulation Resistance
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Insulation Resistance

12/24/2020 7:33 AM

<...are this difference acceptable...>

Carrying out a test without knowing where the acceptability criterion lays beforehand is abstruse.

The acceptability criterion needs to be in the test protocol before the test is carried out, and the protocol has been withheld from the forum. Without a defined acceptability, a test is not a test, merely a measurement.

<... what is the possible causes of this difference ...>

How about the quality of the insulation across <...R...S...[and]...T...>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Insulation Resistance

12/24/2020 8:34 AM

There is no reason the three phase insulation resistances should be the same. They are electrically isolated.

"Insulation resistance should be approximately one megohm for each 1,000 volts of operating voltage, with a minimum value of one megohm. ... In practice, megohm readings normally are considerably above this minimum value in new equipment or when insulation is in good condition"

https://www.instrumart.com/assets/Megger-Guide-to-Insulation-Testing.pdf

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Insulation Resistance

12/24/2020 9:04 AM

Before the generator was turned ON a spider spun a web from T to E. ZAP

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Insulation Resistance

12/24/2020 1:07 PM

An interesting possibility. GA

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#5

Re: Insulation Resistance

12/24/2020 11:14 PM

Resistances that high are usually measured using direct current. If you reverse the tester's leads the readings will change. Try heating the generator to near 100C to dry it, then allow it to cool. The moisture paths will go and higher resistances will be seen.

Zaf

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#6

Re: Insulation Resistance

12/25/2020 12:25 AM

These readings look acceptable to me. Is this an automobile generator? Please explain its usage.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Insulation Resistance

12/25/2020 9:45 AM

No one will be able to answer your question unless until complete details of the Generator, Measuring instrument, conditions of testing, purpose of the testing are specified. So please come out with as much details as you have.

Are you a supplier of the generator or the operator /owner of the generator?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#8

Re: Insulation Resistance

12/25/2020 3:18 PM

When we checked the insulation resistance for generator we show there are a difference

between reading:

R-E =320 M ohm ,S-E = 305 M ohm ,T-E = 240 M ohm

please what is the possible causes of this difference and are this difference

acceptable ,are there any standard value for difference in insulation between phases

You are missing the point. These numbers are not supposed to be equal, they are all supposed to be as high as possible.

There are many reasons for low insulation resistance. My experience is that the salty air in maritime environments is a prime cause. Salt deposits from the air draw moisture which provides a conductive layer.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: Insulation Resistance

12/25/2020 3:33 PM

I'm not even certain what the letters of R, S, T and E stand for. E might be chassis Earth but the other three might be Stator, Rotor and Terminal (aka Neutral, Common). On the other hand these sequential letters might be the three output phases in a star configuration with a floating common.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#10
In reply to #9

Re: Insulation Resistance

12/25/2020 6:12 PM

RST = three phases, E = earth or ground. I'm guessing that since there are different values of insulation resistance that the three phase stator windings are connected externally and disconnected (isolated) before meggaring.

https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=43105#:~:text=R%2DS%2DT%20was%20the%20general%20designation,Y%2C%20and%20W%20to%20Z.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #10

Re: Insulation Resistance

12/26/2020 9:18 AM

Yes, some three phase generator manufacturers use these letters for the three phases. But some brushed single phase manufacturers have used these same letters to identify Rotor, Stator and Terminal. Without an identification by the OP to a model number, manufacturer, age or era of the generator or anything at all that describes the generator but what the OP doesn't understand then we are just as uninformed as the OP about what they have.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#11

Re: Insulation Resistance

12/26/2020 6:19 AM

Rating of Generator in KVA?You can try standard methods to improve IR values and see if it improves .what is out Pput voltage?

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Mar 2019
Posts: 29
#13
In reply to #11

Re: Insulation Resistance

12/26/2020 12:41 PM

Dear all

Thanks for all the responses.

generator rating 31 MVA ,5.5KV

R,S,T = Three phase

E=Earth

thanks

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#15
In reply to #13

Re: Insulation Resistance

12/27/2020 6:07 AM

Kindly provide more information like, type of cooling (I hope that it is air cooled generator), type of insulation, like epoxy, bitumen etc, where the coolers are mounted, within the generator casing or out side? Voltage of the megger used for measuring the insulation resistance. Please also measure if not measured and provide the polarisation (PI) value and value of insulation resistance between the phases. This would help in advising on the subject.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#19
In reply to #13

Re: Insulation Resistance

12/28/2020 5:31 AM

Value is high enough to use it.Difference could be due to some defects developing in that phase insulation It could be due to various reasons.How old is the machine? Are the windings original or rewound or patch repaired any time? Try heating by circulating current using a low voltage source taking care .If still value continues to be low some defects are developing in the insulation of that phase

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Mar 2019
Posts: 29
#20
In reply to #11

Re: Insulation Resistance

12/29/2020 2:56 AM

Dear all

Thanks for all the responses.

generator rating 31 MVA ,5.5KV

R,S,T = Three phase

E=Earth

thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #20

Re: Insulation Resistance

12/29/2020 1:56 PM

Deep joy. A pint of keggy brewflade, please.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #21

Re: Insulation Resistance

12/29/2020 5:22 PM

I prefer a little spider if you don't mind.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #20

Re: Insulation Resistance

01/02/2021 1:37 PM

Could the forum now please learn the outcome of the discussions that have taken place with the original equipment manufacturer?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#24
In reply to #20

Re: Insulation Resistance

01/03/2021 3:34 AM

Henry,

the value of the insulation resistance after 15 and 60 seconds of measurement and their ratio are important .If it's less than 1.3 it says a lot about his condition and maybe more than the maximum value you got .

On internet are good scripts on the subject of insulation resistance testing and I suggest you study one well before deciding and turn on the generator on .

Good luck and Happy New Year .

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#14

Re: Insulation Resistance

12/26/2020 4:22 PM

...a bit of damp/moisture/humidity somewhere....?

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#16

Re: Insulation Resistance

12/27/2020 10:14 AM

Another important piece of data is the history of insulation resistance tests in the past. From this you will see a trend which is important in assessing the condition of the machine.

--JMM

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Insulation Resistance

12/27/2020 12:05 PM

How do these figures compare with those taken when the equipment was originally commissioned?

What did the equipment manufacturer say during the telephone call(s) made on this topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#18

Re: Insulation Resistance

12/27/2020 6:46 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Register to Reply 24 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

henry98 (2); horace40 (1); jmueller (1); nesubra (2); Panta SD (1); pcchatur (2); PWSlack (5); redfred (4); Rixter (3); SolarEagle (1); StandardsGuy (1); Zaf (1)