What size standard steel I-Beam is needed to span a 14ft door opening in a concrete block wall and support a second floor parts storage mezzanine above?
Assumptions:
1) Mezzanine floor is rated at 125 lb/ft^2 capacity. (Is this typical?)
2) Beam carries an evenly distributed load. (Wooden trusses rest on top of beam, perpendicular to beam)
3) A 20ft long beam can be used to span the 14' opening with 3ft resting on the wall on each end.
4) Ideal I-Beam height/width is 8"x8" because of space contraint. When using Max Displacement = -(5*p*L^4)/(384EI) the displacement continues to calculate (using a W8x31) over 1" deflection. Even when calculating with a W10x45 the defection is high. Please help.
Pathfinder Tags: beam
Re: Simple Beam Calculation
11/20/2007 3:36 PM
Additional Assumption:
The opposite wall from the beam supporting the mezzanine is 13ft away.
Is the load (lb/ft) on the beam then 13*125 lb/ft^2 = 1625 lb/ft ?
Good Answers: 137
11/23/2007 7:24 AM
No, it is 1/2 that, assuming the wooden beam ends are simply supported at the far end and where they rest on the steel beam.
According to my calc, with the lightest 8" x 8" universal column (46 kg/m, 31 lb/ft) and ends simply supported on the walls, max deflection ~ 2.4 mm and max stress ~ 25 MPa (3675 psi). Properties are Ixx = 4564 cm4 (110in4), Zxx = 449.2 cm3 (27.4in3) need to check your's are similar.
125 lb/ft ~ 6 kN/m2, in UK typically use 5 kN/m2, so this looks OK, but depends what the room is used for.
Also if the 3' ends of the beam are built in to the wall, and the wall above is a reasonable height (you would need to decide what is reasonable!) the beam ends can be considered fixed and stress/deflection lower.
But picking up JohnDG's comments, you need to make sure you're happy with it before finalising.
Cheers......Codey
11/20/2007 5:13 PM
Sorry, but if you need to design something that could easily kill people if it failed, I'd advise you to go to a qualified design engineer, rather than risk getting some (possibly duff) information over the internet.
No offence intended to anyone on CR4.
John
11/21/2007 1:48 AM
This is not simply a simple beam calculation after all.
You have mentioned that the beam is loaded uniformly where in fact not. It also has to support concentrated loads from the wooden trusses perpendicular to it. The nature of support is also not simple.
My recommendation is for you to consult or seek the services of the right professional engineer.
"The more I learn, the more I know the less I've learnt"
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member
11/21/2007 7:29 AM
I agree with the reponders:
There is a reason that structural engineers are licensed - to protect the health safety and welfare of the public.
You seem to be able to run through the calculations without really realizing why structural shapes are designed as they are and seem to be baffled at how to counter the deflection - which shouldn't exceed L/360 for your application.
Go chat with your friendly neighborhood structural engineer.