BUSBAR CALCULATIONS FOR MDB'S

12/09/2007 12:59 AM

Dear All,

I work as an Electrical engineer for an Automation Firm. Here i had encontered a situation where in the consultant had asked us to give them the SC calculation for the busbar of our MDB. When asked to our fabricator he gave me the following calculation (unfortunately) with out much explanation. Could somebody pls enlighten me on this:

As per the designed we had been asked to have a system that could withstand 50KA of SC current:

So formula (for calculating the area of cross section for a given SC current)

goes like this,

I = Area of cross section of busbar x 160A/mm2 x 0.8

where 160 is the current density of copper at 200deg Centigrade(as per the Nomogram table provided by the manufacturer).But the fabricator is not able to explain what that 0.8 factor is? Can somebody please explain:

Thanks in advance.

Register to Reply
Pathfinder Tags: busbar calculations
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Feb 2007
Location: India
Posts: 6
#1

Re: BUSBAR CALCULATIONS FOR MDB'S

12/09/2007 5:04 AM

You given the equation for current carriying capacity of busbar and not the SC Current.

SC Current is calculated by knowing the Fault MVA of the system connected to the Busbar. The factor 0.8 will be PF or any thumb rule factor

Register to Reply
Member

Join Date: Oct 2007
Posts: 5
#5
In reply to #1

Re: BUSBAR CALCULATIONS FOR MDB'S

12/12/2007 2:36 AM

Could you please explain more on your statement since iam a novice. What is the difference between the SC calculation and a current withstand capability of busbar. I thought they were the same.My requirement is for the given the system, i have to check whether the busbar selected(for dimensions and material) is an optimum one.

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: BUSBAR CALCULATIONS FOR MDB'S

12/10/2007 11:34 AM

0.8 is a safety factor.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#3

Re: BUSBAR CALCULATIONS FOR MDB'S

12/11/2007 6:37 AM

I agree with electrical@wonderla.com. The equation provided is for current carrying capacity of busbar and not the SC Current withstand rating. As to the 0.8 factor, it may be an uncertainty factor or temperature correction factor.

Calculating the short current withstand capability of busbar has to take into consideration the spacing between the bus bars and mechanical bracing of them.

Register to Reply
Anonymous Poster
#4

Re: BUSBAR CALCULATIONS FOR MDB'S

12/11/2007 7:13 AM

dear friend ,

we are working in auotmated dairy compnay in Riyadh . we are using the siematic-7 &

PROFIBUS bus bar . pl porvide the basic knowledge about it . can u suugest the books which give basic knowledge .

any body can teaching siematic -7 & programing .

00966-566285854

nagarjun68@yahoo.com

regards

NAGARJUN

Register to Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: BUSBAR CALCULATIONS FOR MDB'S

12/13/2007 6:31 AM

Short Circuit current is calculated depending on the percentage Impedance and line voltage. Line voltage( V L ) is multiplied by 1.1 to take carte of the 10 % rise in voltage and Z .

As an example , In 3 phase 1000KVA Transformer ( single ), 22/ 0.415 kV,

the % Z = 5.25 and

Short Circuit Current

...... 1.1 x V L

I = -----------

......... √ 3 x Z

The Impedance Z should be calculated in ohms

........→ % Z x 10 x kV2

Z = ----------------- say in this case 0.009 (calculated)

............→ kVA

..................................→ 1.1 x 415

Short circuit current I = ----------------- = 29.3 kA

. ................................√3 x 0.009

The 0.8 given is a derating factor depending on the heat dispensing of the enclosure considering the panel is installed in indoor in well-ventilated room. .

Register to Reply
Anonymous Poster
#7

Re: BUSBAR CALCULATIONS FOR MDB'S

12/15/2007 11:13 PM

Look at the Copper Development Association website - it has a book called "Copper for Busbars" for free with everything you need to know. This is the definitive reference.

Register to Reply
Anonymous Poster
#8
In reply to #7

Re: BUSBAR CALCULATIONS FOR MDB'S

07/25/2008 10:31 PM

Please provide a link to that book..

Thanks.

Register to Reply
Anonymous Poster
#9

Re: BUSBAR CALCULATIONS FOR MDB'S

01/29/2009 6:48 AM

hi yaar

0.8 is noyhing but it is a derating factor.

Register to Reply
Anonymous Poster
#10

Re: BUSBAR CALCULATIONS FOR MDB'S

04/07/2010 6:03 AM

.8 is the current per mm

Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#11

Re: BUSBAR CALCULATIONS FOR MDB'S

05/09/2010 4:04 AM

it is the correction or derating factor

__________________
Correct me if i am wrong i am learner
Register to Reply
Anonymous Poster
#12

Re: BUSBAR CALCULATIONS FOR MDB'S

05/22/2010 3:01 AM

ok Sir, This is for 50ka if required more then 50ka like 70ka and all then what is the factor

Register to Reply Off Topic (Score 5)
Member

Join Date: Jan 2011
Posts: 7
#13

Re: BUSBAR CALCULATIONS FOR MDB'S

06/13/2011 10:15 AM

I = Size buss * 160/SQRT(TIME_breaker_OFF) => 1/SQRT(TIME_breaker_OFF) = 0.8

Register to Reply