Current carrying capacity

12/09/2007 11:47 AM

Hi,

Can any one help me to give me link to know the current carrying capacity of power cable?

I have to lay wire for @ 1200 Ampere load.

where to search data on net?

__________________
U.M.Patankar
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Current carrying capacity

12/09/2007 11:58 AM

Don't know what your local regs are (which is what matters), but to get an idea, IEE regs suggest you'd need something about 650mm2 c.s.a. (cable enclosed in conduit) for 1000A.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Aug 2007
Location: Dombivli, Maharashtra, India
Posts: 31
Good Answers: 1
#2
In reply to #1

Re: Current carrying capacity

12/09/2007 12:26 PM

Thanks.

__________________
U.M.Patankar
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3

Re: Current carrying capacity

12/09/2007 9:20 PM

Hello uday pr,

Cable current capacity is dependent on cable insulation type, whether single or multi-core, plus ambient temperature.

Also de-rated further if enclosed in conduit etc.

You perhaps need 800mm2 or 1000mm2 size dependent on your local installation requirements.

You will find excellent sets of Cable Tables right here:

http://www.myelectrical.com/pages/cables/cableCurrents.aspx?id=061112125012

Advise here further as necessary.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#4
In reply to #3

Re: Current carrying capacity

12/09/2007 11:26 PM

And the length of the cable run... perhaps this is the most neglected factor....in desgning cable size. 1200 amps at 50 metres length, and 1200 amps at 300 metres length......will not use the same cross sectional area cable. Good luck.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply Score 1 for Good Answer
Associate

Join Date: Aug 2007
Location: Dombivli, Maharashtra, India
Posts: 31
Good Answers: 1
#5
In reply to #4

Re: Current carrying capacity

12/10/2007 4:06 AM

The length is @ 250 Mtr.

Thanks.

__________________
U.M.Patankar
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #5

Re: Current carrying capacity

12/10/2007 4:36 AM

Hello again uday pr,

For any useful answer,

we need to know the following, because there are several variables:

  1. Supply Voltage
  2. AC or DC
  3. If AC single or 3 phase
  4. If 3 phase is Load across the 3 phases balanced fully
  5. Type of cable you plan to use: PVC/Polythene/Lead sheathed/Steel wire armoured/XLPE etc
  6. Cable buried direct: Advise sand/clay/soil etc - The ground material/soil will dry out over time, and the cable needs to allow for that, by being derated = A larger size than otherwise. There have been spectacular cable failures, around the World, after many years, because dry sand/clay/soil is a good thermal insulator.
  7. Cable in Plastic Pipe (heat builds up)
  8. Cable in Steel Conduit (Single core cable for AC must always be in the same "pipe" or magnetic induction problems occur)
  9. Single Core/multicore (multicore for AC have reactance to consider)
  10. Cable if in air: Local Annual Temperature Variations - Maximum/Minimum
  11. Allowable Volt Drop at Full Current: per phase or DC = each length
  12. There are further details required, but if you can supply the above, it should narrow down for your requirements.

Advise here please.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Anonymous Poster
#7

Re: Current carrying capacity

12/11/2007 2:28 AM

Plz refer the data sheet which is avaliable with power cable manufacturers and if the rating does not include for 1200 amps use parallel cables but of equal cross section to get the desired current rating.It is suggested to use a derating factor for the cable as 085.

Regards

Mulla

Register to Reply Off Topic (Score 5)
Member

Join Date: Feb 2007
Location: India
Posts: 6
#8

Re: Current carrying capacity

12/11/2007 2:48 AM

Current carriying capacity depends on many factors

Allowable voltage-drop for normal operating load.
Allowable voltage-drop for future operating load as determined by motor's Service Factor.
For 1200 Amps 2Rx400sqmm aluminium is sufficient
But it depends on legth of the cable. Calculate voltage drop it must be within 2.5%
Google it you will get

Register to Reply
Anonymous Poster
#9

Re: Current carrying capacity

01/18/2008 8:38 PM
Register to Reply
Participant

Join Date: Oct 2008
Posts: 3
#10

Re: Current carrying capacity

11/02/2008 1:31 AM

Hi,

This is Nitin Jogi, Pleses go with maintenanceworld.com u can get lots of things there about electrical .

NITIN JOGI

nitinjogi@hotmail.com

Register to Reply
Participant

Join Date: Oct 2008
Posts: 3
#11

Re: Current carrying capacity

11/02/2008 6:00 AM

Hello,

As per ur load u can go with 300 sq.mm cable of five numbers. and also note that this capacity is max? or any additional is there. So u can go with this it will take the sum load of 1200 amp.( if ur gounding all the cables under)


nitin jogi

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); chaterpilar (1); electrical@wonderla.com (1); JohnDG (1); nitinjogi (2); Sparkstation (2); uday_pr (2)

Previous in Forum: Current density v current supply and a generator size questions   Next in Forum: 2-PH To 3-PH Converter

Advertisement