VFDs temperature raise

10/07/2022 9:38 AM

How to claculate the temperarue raise of a 400 KW VFD panel?

Best Regards,

NVRSrinivas

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: VFDs temperature raise

10/07/2022 10:47 AM
__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: VFDs temperature rise

10/07/2022 12:27 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#3

Re: VFDs temperature raise

10/07/2022 12:30 PM

How efficient is the VFD? What is the ambient temperature? What is the airflow in stones per fortnight?

https://www.engineeringtoolbox.com/air-specific-heat-capacity-d_705.html

Typically, the VFD vendor may provide the thermal impedance of their unit. Or at least give you a range of acceptable temperature and humidity values.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: VFDs temperature raise

10/07/2022 11:54 PM

You say "VFD panel". This implies the VFD is inside a larger control enclosure. The VFD manufacturer's literature should give its efficiency under load, as well as some idea of its heat loss when only lightly loaded. Add this to the totals of all other heat sources in the enclosure (such as control transformers, contactor coils, inductor losses, etc.

The control enclosure has to be able to dissipate all this heat in some way, such as radiative cooling into the surrounding air, cold air streams, air conditioning units, cooling fans through filters, etc. If your VFD is designed with cooling fins for mounting through the wall of the enclosure (fins on the outside and all else inside) your heat loss into the enclosure will be much less--but you may need an external fan to push air past the fins and you would need a maintenance plan to keep it clean. Enclosure manufacturers have formulas to tell how much heat they can dissipate for a given ΔT between the inside and outside for a given surface area.

However, the best way is to use the VFD's on temperature sensor and program it to display on the VFD controller, so you know its actual temperature and can respond accordingly.

--JMM

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#5

Re: VFDs temperature raise

10/07/2022 11:55 PM

Maybe you are not looking for the temperature rise, but for the heat gain of the equipment so that you can size your cooling equipment?

The temperature rise of the VFD is determined or measured by the VFD manufacturer, using data and conditions not normally published for the end user. The end user usually has no need for this information, except perhaps in unusual explosion risk environments.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: VFDs temperature raise

10/12/2022 6:51 AM

The possibility of a flammable gas/air mixture near a <...VFD...> doesn't bear thinking about.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#8
In reply to #7

Re: VFDs temperature raise

10/12/2022 8:09 AM

A novice engineer, that doesn't know how to apply thermodynamic laws, designing anything in an explosive atmosphere is a recipe for disaster.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: VFDs temperature raise

10/12/2022 6:36 AM

One might pick up the phone and talk to the equipment manufacturer directly and without involving the forum, perhaps.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: VFDs temperature raise

10/14/2022 11:33 AM

If you cannot get the heat rejection values from the VFD manufacturer, or you have not selected a supplier yet so you want to be sure, modern VFDs are 96-97% efficient, so worst case you could use 4% of the power as their rejected heat. I have seen some that claim 98% eff., but those are “marketing values” and are of dubious engineering value.

Calculating the temperature rise of wherever / however that VFD is mounted then becomes a standard temperature rise procedure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Sep 2015
Location: Mumbai, India +91-7738003942 (whatsapp)
Posts: 1
#10

Re: VFDs temperature raise

12/06/2022 1:31 AM

Dear Mr. NVR Srinivas,
could you share your mobile number?

I will call you for discussions on various topics posted by you.

Hemant Sawarkar

TMEIC, Mumbai

__________________
Expert - MV Drives, MV Motors, UPS, Voltage Dip Compensation, Battery Energy Storage, High Current Power Supply for Green Hydrogen
Register to Reply