Spacing between same phase busbars

03/07/2023 9:57 AM

Hello everyone,
I'm watching a various switchboard busbars systems and I noticed that when we have two busbars per phase, in some switcboards they are spaced at some distance, while in other they just lay side by side. I attached picture for better understanding.
Is it correct to put two busbar of same phase without spacing? I know that when we connect two busbars it must be connected with appropriate number of bolts (depending on busbar size) so I just wondering is this correct or there should be some space between them?

I'm concern because if we have some cable which is not properly connected to circuit breaker terminal, that terminal and cable lug will be buried and become "black". Because I'm fearing that two bars placed side by side, without spacing will also have some "burning" between them...If you understand my concern..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Spacing between same phase busbars

03/07/2023 6:45 PM

Generally speaking, it doesn't make any difference either way unless you are trying to dissipate heat.

I would speculate that mechanical issues, e.g. connecting bus bars to equipment drive the spacing over any electrical issue. The reason you wouldn't bolt them together as a monolithic block (without an insulating layer or coating), has to do with skin depth of copper at 60 Hz (~8.5 mm). Hmmmmm . . . . ever wonder why most bus bars are manufactured out of 1/4 inch copper bar/plate?

https://en.wikipedia.org/wiki/Skin_effect

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#2
In reply to #1

Re: Spacing between same phase busbars

03/08/2023 2:06 AM

I haven't really wondered on the 1/4 bar plate because from my work life it can be any size from 1" square, 3x1" 4x1/2" it just depends on what the designer specified or what his mate had an excess of at the time.

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#3

Re: Spacing between same phase busbars

03/08/2023 2:11 AM

From the busbars I have worked the gap is often there for the take offs and direction changes to interleave said connections between the busbars. Outdoor ones have the gap to allow the rain to evaporate and not cause corrosion from airborne contaminants sitting wet between the contacting faces when bolted together.

__________________
Hare today, goon tomorrow!
Register to Reply
Active Contributor

Join Date: Jun 2020
Posts: 13
#5
In reply to #3

Re: Spacing between same phase busbars

03/08/2023 10:22 AM

Have you ever seen busbar placed side by side without gap? Should this be problem?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Spacing between same phase busbars

03/08/2023 3:20 AM

It would be a matter of concern if the <...we...> did not have design procedures that cover this matter.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Spacing between same phase busbars

03/08/2023 12:10 PM

Having two busbars without gap seems illogical as it could as well have been one single busbar of larger cross section in such a case.

Two smaller cross section busbars instead of one larger one are preferred to reduce the loss of current carrying capacity due to skin effect at large current ratings.

When the two busbars are provided, I have always seen a small gap between them with a positioning insulator holding the two busbars firmly and the busbars supported at regular intervals.

These are important for two reasons - busbar positioning with insulators to avoid clashing of busbars and regular supports to prevent busbars getting damaged due to dynamic forces when exposed to large currents during faults.

__________________
Raghunath
Register to Reply
Active Contributor

Join Date: Jun 2020
Posts: 13
#7
In reply to #6

Re: Spacing between same phase busbars

03/08/2023 2:04 PM

If you have 2500A, you need two busbars 100x10, you haven't 100x20 busbar, you can't buy it, because they are not produced.

Register to Reply
4
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#8

Re: Spacing between same phase busbars

03/10/2023 7:48 AM

Spacing between busbars is used for various reasons, e.g. more cooling (more surface area), ease of interleaving (fishplates), other connections. Downside is that bars of the same phase will "pinch" when subject to high fault levels (e.g. test conditions) and may need additional packers between the normal supports.

Not having a space is OK, subject to the rating required (and tested) and joint overlap etc. Thicker bars are also stronger of course.

Search out "publication 22" from copper development association for a lot of helpful design data (available online).

If you have not subjected the design to high fault level and temperature rise tests then please leave it to those who have - strange things can happen ;-)

__________________
rogerggbr
Register to Reply Good Answer (Score 4)
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); Designmen (2); PWSlack (1); raghun (1); rogerggbr (1); Stef (2)