please can explain how the start relay in the attach drawing work,because in our diesel generator when we give start command the sequence of events was as follows:
start prepare
run coil on
start relay on (diesel generator on)
after 3 sec the start relay become off (diesel generator off)
thanks
Pathfinder Tags: start relay
Re: starter relay
06/29/2023 12:05 PM
sorry because picture not clear
Re: starter relay
06/29/2023 2:44 PM
You need a qualified troubleshooter....my guess is it's off on low oil pressure....but there are any number of safety mechanisms at play here....does the generator give a blink code? What is the brand and model#...
Re: starter relay
06/29/2023 4:43 PM
There are no any alarm and the generator not give a blink code, when we give start command the sequence of events was as follows :
start prepare
run coil on
start relay on (diesel generator running)
after 3 sec the message (start relay off )appear then suddenly diesel generator stoped
Re: starter relay
06/29/2023 5:02 PM
the type of controller (DEIF Automatic Gen-set controller)
Re: starter relay
06/29/2023 6:35 PM
So check your in and outs for voltage and find the control break...additionally the fuel level sensor might be bad...or you might actually be low on fuel....or oil...or bad pump...
https://www.deif.com/media/2oge2ny4/sgc-110-user-manual-4189341228-uk.pdf
Re: starter relay
06/29/2023 11:33 PM
Could also be radiator level low if it has that protection or motor not running (loss of speed output) lots of other protections are often included.
Hare today, goon tomorrow!
Re: starter relay
06/30/2023 6:57 AM
...among an unknown number of other possibilities.
Re: starter relay
07/04/2023 9:53 AM
Indeed.
Not the least of which may be if this is existing equipment in situ that has mysteriously stopped operation, or existing equipment moved and being recommissioned, or renovation to facility has added 26 kW to generator load...
Perhaps an explanation of why the starter relay is suspect?
Re: starter relay
06/30/2023 6:26 AM
Indeed. That's what it says in the opener to this thread. Repetition is unnecessary.
It's impossible to see from here; has the <...we...> checked for circuit continuity on the output wiring all the way to the connected equipment?
Re: starter relay
06/30/2023 6:53 AM
...and the input wiring?
Good Answers: 27
Re: starter relay
06/30/2023 6:58 AM
Check the generator fuel.
Diesel generator engine will only stop when fuel is cutoff..
vsar
Re: starter relay
06/30/2023 3:34 AM
What did the <...diesel generator...> manufacturer say over the phone?
Re: starter relay
06/30/2023 4:22 AM
I checked all protection like
(H.W.T),(L.O.P),(L.W.L) NO one operated.
Re: starter relay
06/30/2023 4:54 AM
You might have a fuse blown or an open winding or failure to reach operating speed...In any case you need to do a step by step test of every component until you find the problem, that's what troubleshooting is....The controller itself should tell you what's wrong, you need to refer to the operators manual to find the information you need...navigate the controller...
Re: starter relay
06/30/2023 6:21 AM
Did the equipment manufacturer help with those TLAs over the phone?
Re: starter relay
07/04/2023 10:09 AM
Surely the manufacturer can quote for an appropriately-qualified Technician to come in and fix it? What was the outcome of the phone call(s)?