09/13/2023 4:14 PM

Dear All, please can anyone assist in giving me the total equipment needed to be supplied. There is 4MVA, 11/0.4KV power xformer and one 10MVA, 33/11KV power xformer. I am a sales engineer who need help in identify the materials/equipments needed as per this drawing. Kindly assist me with the number of CTs/VTs, recloser, 11KV panels, etc. I look forward to hear from anyone who is willing to assist.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Single Line Diagram Equipments

09/13/2023 7:58 PM

That's a large task. And one outside of my areas of expertise. There may be more knowledgeable members on this forum that might be able to point you to the resources where you can better find your answers.

Hiring a consultant with the credentials approved by your AHJ (authority having jurisdiction) is probably the best approach to getting the proper answers for your project.

Best wishes on your quest.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#4
In reply to #1

Re: Single Line Diagram Equipments

09/14/2023 6:05 AM

Thank you @Brave, i do appreciate your response. I still look up to more responses from other members who have core knowledge area on this.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Single Line Diagram Equipments

09/13/2023 10:05 PM

You need to contact a major distributer of grid style electrical distribution equipment, and sign an MOU(memorandum of understanding) where you agree to buy all your equipment from them for this project, and have them agree to supply and site all the components of the substation and commissioning done within a certain timeframe...You submit to them your AHJ (authority having jurisdiction) approved plans and have them approve or modify these plans...then they should price out the entire project for you...

https://www.global.toshiba/ww/products-solutions/transmission/products-technical-services/substation-equipment.html

...or Siemens, or Schneider, or any large company that specializes in this type work....I would check to see what other distributors have done locally...

https://nairametrics.com/2022/12/04/electricity-distribution-companies-in-nigeria-and-the-states-they-cover/

https://www.lusha.com/company-search/utilities/56/nigeria/80/

https://projectsportal.afdb.org/dataportal/VProject/show/P-NG-FA0-011

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#5
In reply to #2

Re: Single Line Diagram Equipments

09/14/2023 6:07 AM

Thank you for your contributions..

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Single Line Diagram Equipments

09/13/2023 11:02 PM

You show perhaps 3 sets of battery limits, one around the switchgear, one around the generator and one around the transformer.

You also show 5 transformers, so some information is missing from your equipment you are supposed to supply.

You really need to go back and confirm the limits of your supply. Normally, the transformer supply would not include anything beyond matching the current transformers on the bushings with the CTs on the breakers and generators for differential protection. However, 400V transformers are rarely installed with differential protection.

For example, we can reasonably assume your supply does not include the generators shown connected to the step up transformers.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#6
In reply to #3

Re: Single Line Diagram Equipments

09/14/2023 6:09 AM

Yes Williams, the supply does not include the generators. Only the transformers and protection equipment and the panels.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#7

Re: Single Line Diagram Equipments

09/14/2023 7:42 AM

Dear All,

I was able to come up with the list below. Kindly assist to confirm.

DESCRIPTIONQTY.
Lightening Arrestor (33KV)2
SF6 Switchgear panel (33KV)1
SF6 Switchgear panel (11KV)4
10MVA, 33/11KV Transformer1
3MVA, 0.415/11KV Step down Transformer4
33KV SWITCHGEAR
SF6 Switchgear Panel 33KV, incomer1
SF6 Switchgear Panel 33KV, outgoing1
SF6 Switchgear Panel 33KV, Spare1
11KV SWITCHGEAR
SF6 Switchgear Panel 11KV, Outgoing4
SF6 Switchgear Panel 11KV, Incomer1
ACDB Panel1
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #7

Re: Single Line Diagram Equipments

09/14/2023 10:17 AM

You appear to need to include the neutral ground resistor for the wye connection to the generating station step up transformer.

There will be a set of documents that detail the desired protection standards, the environmental requirements and the limit of supply including design engineering, drawings, installation, and the short circuit capability of the power system you connect to, future generation, operation parameters of the generators, and short circuit capability of the generators themselves.

With this information, it will be very easy for the sales engineers for each of the classes of switchgear to provide a quote. This RFQ would not be handled by a single person, except as a common point of contact for a team of engineers.

Iwould expect ABB, Siemens, Schneider would be a single source quote for this project, but you might do better by shopping the components out, unless you need to do the installation. In that case, hire an engineering firm, probably a $25,000 job if your client gave you good information. Someone drew the single line, not likely the end user.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#10
In reply to #8

Re: Single Line Diagram Equipments

09/15/2023 8:05 AM

Thank you once again.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Single Line Diagram Equipments

09/15/2023 6:59 AM

No-one needs to operate on a task like this without having guidance. Ask the employer for appropriate training to carry it out. A Mentor would be of good value here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Keffi,Nigeria
Posts: 18
Good Answers: 1
#11
In reply to #9

Re: Single Line Diagram Equipments

09/15/2023 8:05 AM

Thank you. This is noted

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: Single Line Diagram Equipments

09/27/2023 7:39 AM

I do not think a single person has the knowledge,skills,or ability to perform this job at this time in your career.

That is why it is important to have an experienced engineering firm perform the job.

I respect and admire your ambition,but knowledge is gained a step at the time,and skipping a valuable step can result in catastrophe.

I am sure that with your open mind and thirst for knowledge you will learn much from the company selected to perform the job.

Good luck in your quest,and I wish you much success as you climb the ladder of knowledge.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); HiTekRedNek (1); komez (6); PWSlack (1); rwilliams (2); SolarEagle (1)

Previous in Forum: VSD Motor Directly Coupled to a Screw Motor   Next in Forum: UPS vs VFD — Double Conversion

Advertisement