Dear all
We have thee winding transformer (YNdd11)(400/15/15 KV )(505/6736/6736 Amp.)(700/1-8000/1-8000/1 CT ratio).The current after CT (0.7213/0.842/0.842 Amp)
Minimum differential current is 0.2 pu
primary side Pickup differential current =0.723x0.2=144.26 mA
secondary side pickup differential current =0.842 x0.2=168.4 mA
Tertiary side pickup differential current =0.842 x0.2=168.4 mA
when I inject current at primary side the relay trip at current value 145mA same the setting value.but when I inject current at secondary side and tertiary side the relay trip at current value 335mA
My question is why in secondary and tertiary side the trip value (335mA) it double of setting value. why not the trip value is the same of setting (168.4mA)
Thanks for all