Which method is used to determine the short circuit current at a light fixture's terminals to ensure that circuit breaker ahead of it trips in case of a short circuit? Is the calculation typically done using the conventional method starting from the source till the fault location? or by earth fault loop impedance calculation?
Is the fault current same between these methods conventional Vs Earth fault loop impedance?
Does the earth loop impedance calculation adequately consider the impedance of the upstream power source/supply? Max Zs = Uo / Ia
Zs is the earth fault loop impedance in ohms (Ω).
Uo is the nominal line voltage to earth in volts (V).
Ia is the current in Amperes (A) required to trip the circuit breaker for the relevant disconnection time