Optimizing Overcurrent Protection for a 4200 kW Slip Ring Induction Motor

06/04/2024 10:45 PM

The optimization of overcurrent protection for a 4200 kW wound induction motor, which drives a raw mill in a cement plant, is under review. The motor specifications are: 4200 kW, 6.3 kV, 471 Amp, 994 RPM. The objective is to ensure the motor trips at 100% load with a delay of 10 seconds. Additionally, a 1400 kVar capacitor bank is integrated with the motor.

Simulation results from ETAP have revealed the following:

  • At the MV motor protection relay and energy meter, the current is 114 Amp with a power factor of 96%.
  • At the motor terminal, the current is 471 Amp with a power factor of 85%.

It appears that the capacitor bank, positioned between the motor terminals and the MV feeder output, is influencing the current readings. The capacitor bank supplies part of the current, leading to a noticeable discrepancy between the current measured at the relay/energy meter and at the motor terminal.

Given this configuration, it is proposed that the reference for overload protection (I>) for the relay should be adjusted to 414 Amp. This adjustment takes into account the current supplied by the capacitor bank, as indicated by the ETAP simulation results. Therefore, 414 Amp should be considered the 100% load current for relay, instead of 471 Amp ( mentioned at motor nameplate ).

Feedback and insights from the forum on this approach would be highly valued, particularly regarding the accuracy of using 414 Amp as the reference for overcurrent protection in this scenario.

Thank you!

and

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#1

Re: Optimizing Overcurrent Protection for a 4200 kW Slip Ring Induction Motor

06/05/2024 11:24 PM

Without a doubt, with a motor that valuable, the overcurrent sensing should be on the motor terminals. That way the overcurrent relay sees the actual motor conditions the motor designer anticipated when designing the machine. To measure the current before the capacitors, with no confirmation of each capacitor’s serviceability, is a recipe for poor manufacturing reliability.

Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#2
In reply to #1

Re: Optimizing Overcurrent Protection for a 4200 kW Slip Ring Induction Motor

06/06/2024 9:04 AM

Thank you for your feedback. Your point about the importance of overcurrent sensing directly on the motor terminals is well taken. This ensures that the overcurrent relay accurately reflects the motor conditions anticipated by the designer, rather than potentially inaccurate readings influenced by capacitor serviceability.

To validate our concerns, we conducted a sample test on the Mill main drive, recording data over a 15-second interval. The results are summarized below.

Sample Data (Energy Meter Readings):

SR #

VOLTAGE

AMP

POWER (ELECT)

P.F

PART LOAD

DATA SOURCE

16234404.6419996.12%96.13%ENERGY METER
26237395406595.27%93.06%ENERGY METER
36236400.2411695.22%94.23%ENERGY METER
46235407.1418595.19%95.81%ENERGY METER
56235409.3420795.18%96.31%ENERGY METER
66231401.4412395.18%94.39%ENERGY METER

Load Projection (Estimated) if overload setting reference is 471 Amp:

SR #

VOLTAGE

AMP

POWER (ELECT)

P.F

PART LOAD

DATA SOURCE

76235400411995.36%94.30%ESTIMATED
86235415427495.36%97.84%ESTIMATED
96235430442895.36%101.38%ESTIMATED
106235445458395.36%104.91%ESTIMATED
116235460473795.36%108.45%ESTIMATED
126235471485095.36%111.04%ESTIMATED

We observe that the motor operates up to 111% of its rated capacity for an indefinite amount of time, unnoticed by the relay since the threshold for overload is 471 Amps according to the nameplate of the motor. This is a point of significant concern. Additionally, current sensing is performed before the capacitor, potentially leading to inaccuracies in protection.

Your expertise and any further insights on this matter would be greatly appreciated.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3
In reply to #2

Re: Optimizing Overcurrent Protection for a 4200 kW Slip Ring Induction Motor

06/06/2024 11:00 AM

To meet your goal of tripping your motor off in 10 seconds at 100% load will require you to significantly lower your trip current setting. For example, a standard Class 10 Overload Relay will trip in less than 10 seconds at 2500 amperes, when set at 421A motor rated current.

At this point, I assume you may be questioning the setting and design of the overload sensing relay? No relay is designed to protect a typical induction motor, wound rotor or squirrel cage, so that 10 seconds of operation at rated amperes results in a trip. Relays are designed to replicate the effects of amperes flowing in the stator windings, to predict the temperature in the windings. That is all. 10 seconds will add some heat, but the temperature will not rise a measurable amount. The motor designer recognizes this, and designs the machine to achieve a normal service life under those conditions.

A machine this size no doubt has at least 6 embedded temperature detectors, likely RTDs. If it was my motor, I would purchase a motor protection relay that monitors all 6, and set the motor trip setting according to the relay instructions. MultiLin is a respected name in motor protection, I think GE owns them now, I’m sure Siemens and ABB also have similar devices.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4

Re: Optimizing Overcurrent Protection for a 4200 kW Slip Ring Induction Motor

06/10/2024 5:59 AM

You are right taking 414A for setting the relay.

Please bear in mind that if you have to remove the PFCC at the motor terminals, the relay setting needs to be increased to prevent motor trip < 100% load.

Further, how do you prevent this protection tripping the motor during starting as well as during short time / permissible overloads??

__________________
Raghunath
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aghvel Niazi (1); raghun (1); rwilliams (2)

Previous in Forum: MV/LV Transformer Winding Configuration   Next in Forum: Can Aluminum Shield Magnetic Fields?

Advertisement