C’mon Doorman, Throw Us A Bone!

10/06/2025 4:22 PM

I have a question for the forum. This is likely to seem disjointed, maybe even rambling, because an actual question is not well formed, so for that I apologize up front. It is a certainty I will need to fill in some details, don’t hesitate to ask for specifics.

Regarding a backup or emergency power supply for a residence. In place today is a 75 kW diesel genset, about 8 years old (presumed to be 240vac) This is in a remote wooded area in northern Montana USA. This is an area I have personally experienced mains power service interruptions of several days (four days was the longest I recall), mostly in winter.

The genny is sized to have accommodated an anticipated restaurant/bar sort of business that never came all the way to operational.

Now the sort of question: A new user profile for the facility is considered, becoming a residence. So, this wildly oversized genset is inappropriate of this use… Unless…

How about adding a battery array and inverter? I am imagining a solar hybrid inverter, but not intending to install PV now. If (when) an outage occurs the batteries run the place for three, four, five days. When depleted, head on over to the generator shed, fire that big boy up, charge up the 48 volt LiFePO4 batteries, good for another five days, only ran genny for 8 hours or so.

Sounds good on paper, but I am seeing some potential problems.
1) 75kW ≈ 60 running, figure about 10kW for the house (while running generator, run dishwasher, clothes wash/dry, vacuum rugs… deferred domestic chores), so about 50kW (210A @ 240VAC) that it is desirable to consume… this is where it starts to fall apart for me. I am not finding inverters available that can draw that much power to charge the batts. Are there any? Break it up, more inverters? This means more battery storage used to power more inverters.

I have a headache, so enough to start. As I said, not much of a real question, I am hoping this sort of gives a 10,000 foot overview of this considered project.

__________________
Semper Ubi Sub Ubi
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1206
Good Answers: 54
#1

Re: C’mon Doorman, Throw Us A Bone!

10/06/2025 11:18 PM

I did a simple calculation on my house and found 4kw on average and 10kw peak for the all the stuff we run. We have a gas range, hot water heater and central heating. Add those in if you're all electric and figure in the times they are active.

I have an 11kw generator if the power is out and that has been more than enough. I have 10kw in batteries charged by my solar and they are good for about 2 to 3 hours after dark.

__________________
Most people are mostly good most of the time.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 231
Good Answers: 16
#2

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 7:36 AM

Where we live, 75kW would be a 3-phase supply. There are off-the-shelf systems from DYE, Sunsync, Victron, etc. that you can get. A 50kW system would probably be sufficient? In a 3-ph setup, you're looking at ~75A input current from your genset. The DYE example can do 50A+50A into a battery of 160V upwards, limited by the 50kW input constraint.

In real life you'll probably not average 10kW every hour, but you'll want to cater for those 4 days in winter when solar doesn't work and the grid is down. So, just increase the batteries, most inverters can manage a few batteries. And 10kW*4days*24hrs= 960kwH, which is a lot, and will take a long time to charge! Personally, unless the generator is very far away, I'd settle for a 2-day battery life and walk over to start the genset more often and then run it for a shorter period (remote start/stop is sometimes tricky to retrofit cost-effectively on older machines).

It seems that high-voltage batteries are more efficient, but you'll have to check the data sheets carefully for low-temperature operations. The few people I know playing in this ~50kW space had installed 3x1-phase inverters and normal low-voltage (48V) batteries, but their use-case was very different to yours, so it is difficult to say. It also depends on your redundancy requirements and cost appetite...

Keep us posted as you move along, I'm really curious as to the route you end up taking. Our high fixed (connection) fees means that more and more people are looking at going completely off-grid electrically, and we want to see and learn from what others are doing.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5
In reply to #2

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 12:07 PM

I would like to believe the consumption could be held to about 10 kWh/day *. However, the wild cards here are refrigeration and (seasonally) the furnace blower motors.

In the USA, citizens seem quite happy to stick a plug into every available outlet in the house. Mrs. Doorman likes these decorative tabletop night light/scented wax warmer things; there are 3 in my house right now, each sporting a 15w incandescent bulb. 45 watts/hr, 24 hrs ≈ 1kWh a day right there. Add the other little parasite loads, prolly consume another kWh/day, perhaps two. Then add in parasite standby loads from televisions, computers, clothes and dishwashers, battery chargers, garage door operators, motion activated lights… Our society sucks a lot of power! Identify and remove these loads from the battery backup environment.

Footnote *: As noted in OP, a number of routine house chores should be deferred. As well, lock out/tag out all of those power hungry counter appliances - toaster over, microwave, rice cooker, coffee maker, waffle machine… all of them. Hands off until mains power is restored.

__________________
Semper Ubi Sub Ubi
Register to Reply
2
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#3

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 7:41 AM

Diesel engines like 90% or so loading, less than that they become maintenance headaches. (Epstein Island had them, couldn't keep them running and eventually spent several million running a cable to St T). Don't ask how I know this.

I think you will need a separate charger and inverter rather than a combo unit.

LiPo are nice but Nickle Iron (Edison) are invincible. Can't over/under charge them. Just change the electrolyte as needed (Potassium Hydroxide) Available on Amazon.

Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#4
In reply to #3

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 11:39 AM

Yes, loading up the genset to 80-ish percent as a routine is one of the (not clearly defined) goals of this discussion. It seems extremely wasteful and ill-advised, from many perspectives, to operate a generator at 5%-10%.

I fear that the machine preventative maintenance has been severely neglected. I have requested a copy of (or at least a hands on review of) the PM log and companion fuel reports… the reluctance to provide this leads me to believe there are many blank pages. The genset may be nearly worthless.

If this is the case, the machine can be replaced with something more appropriately sized… unless discussion here with you guys advises the 75kW is about right.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 9:01 PM

I would sell the big generator and use the money to buy a smaller appropriately sized unit...keep it simple...I would build an underground house to save energy, or at least partially underground...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1206
Good Answers: 54
#7
In reply to #6

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 9:15 PM

I agree bro. I did m homework and settled on the 11KW genset and the 10KW of batteries. I can run the electric dryer for a couple of loads with that and not have a problem. 75KW could run a machine shop!

__________________
Most people are mostly good most of the time.
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1206
Good Answers: 54
#8

Re: C’mon Doorman, Throw Us A Bone!

10/07/2025 9:31 PM

Where are the batteries? Inside a bunker out of the cold I hope.

LiFePo Is good. Safe enough for a boat.

Charging system? 240 to ?.

Then, inverters. I think 10kw or 15 for marginal extra use would be fine. It's the charging system that seems to me to be the problem here. The draw can be limited to the inverters supply, but you want to charge up fast and pull down over days.

Fortunately LiFePo is pretty tolerant of partial charge and BMS devices are easy to obtain. My boats batteries can charge off a regular Pb battery charger or alternator with no problems. But what switch-gear and voltages and currents are going to go into this battery bank?

__________________
Most people are mostly good most of the time.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#9
In reply to #8

Re: C’mon Doorman, Throw Us A Bone!

10/08/2025 9:13 AM

“Then, inverters. I think 10kw or 15 for marginal extra use would be fine. It's the charging system that seems to me to be the problem here. The draw can be limited to the inverters supply, but you want to charge up fast and pull down over days.”

Yes. This issue, exactly, is for me the largest fuzzy part. How to utilize the generator efficiently to charge up the batteries. It is quite possible to continue piling batteries, enough energy storage for +/- a week… but how to recharge that battery array in a short period of time?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1206
Good Answers: 54
#10
In reply to #9

Re: C’mon Doorman, Throw Us A Bone!

10/08/2025 10:31 AM

If I want to fast charge my boat batteries, I have to connect them as a 48v series arraignment and charge them at with 50+v. That limits the current to their 50AH current rating (and the limits of the BMSs). In that config I can charge all four at once in one hour. But charging stops when the first battery is fully charged and it's BMS cuts power.

If I charge at 12V (14V actual) I connect them in parallel but then I need 200A at 12V to charge in one hour. I usually only have a 12A charger for that, so, it takes 8-12 hours to charge them back up.

My house batteries are connected through a battery "gateway" switch gear. It only switches between sources and loads, the loads being PGE or the house, and sources being PGE or the batteries or the solar . They charge and discharge at the same voltage/current configuration. They take from sun up till Noon to charge and will last two to 3 hrs draw after dark.

You need to switch between charging and drawing modes somehow. Or you need to charge one bank of batteries while you draw on the other. Either way you need switch-gear.

What is the geometry of the batteries? What are the generators output voltage(s) available? What is the maximum current the generator can deliver? Can you change the geometry of the batteries?

Is the generator loud? Could you run it all night and charge the batteries then use the batteries all day? What if you just run the generator until you have full batteries and then run on them for a few days and then do it again?

__________________
Most people are mostly good most of the time.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#11
In reply to #10

Re: C’mon Doorman, Throw Us A Bone!

10/08/2025 11:38 AM

Battery array exists now only within this discussion; restated, there is no battery storage in the existing scheme. I would be able to set this up in any configuration.

Loud? My request to observe genset operate was declined… This is a 75kW diesel genset inside a dedicated powerhouse (I dunno, about 12’ by 20’), so I presume it is pretty loud. It would be my desire to run genset in daylight; noise seems to carry further at night when it is snowy and cold… I desire that very few of the area residents are aware that I am operating a generator. In fact, I would be pleased if nobody were to become aware it even exists.

Characteristics of existing genset are unknown. Property tour was conducted by a real estate broker, within a pretty small time window.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#12

Re: C’mon Doorman, Throw Us A Bone!

10/09/2025 3:45 AM

You mentioned back-up/emergency power supply.

are you talking about a alternative to a genset, or adding a battery array et al to the genset?

About the genset, there’s a difference between a Prime/Continuous Power vs. Standby/Backup Power genset. You mentioned stand by? Where it sounds like it’ll be used rather often.

Also I gather is one thing you need to avoid, is getting something because it appears ‘cheap’ and then expanding upon it to get what you need instead of buying what you actually need and can use.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#13
In reply to #12

Re: C’mon Doorman, Throw Us A Bone!

10/09/2025 6:39 AM

Good points!

I am investigating several mini goals here. Installed today is a presumed intermittent use emergency genset, not intended for 24 hr weeks on end running, and a single 300 gal (estimated) fuel tank. There are no batteries in place today: power drops out, ATS changes over, genny starts up.

In the historically most likely event of occasional mains disruption of a few hours, I am looking at battery supply in lieu of the genny starting up. When mains returns, the inverter ATS returns to normal, recharges the battery bank from mains supply.

If the mains power loss is of the rare 3 or 4 day type (or the even more rare 8 days), I need to be able to charge up the battery bank. I desire a charge time of about 8 hours.

As the thread title should lead you to deduce, I don’t have very many informational bones to toss you guys. I don’t have a good power audit on the building, I have almost no good info about the genset. I am hoping critical system consumption is about 10kWh/day, but it’s prolly more like 20kWh a day with peak demand of about 5kW.

I’m with ya on the dollars. This is a terrible project to cheap out on; I’m seeing $25 to $50 thousand on gear/batteries, about the same for labor. Rule of thumb - double your WAG estimate and you might be about halfway to the end price.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#14
In reply to #13

Re: C’mon Doorman, Throw Us A Bone!

10/09/2025 10:31 AM

I had a simular situation… (not really knowing what I was getting into) I bought a used 3 phase planer from a high school, I thought it, thinking, I’ll just get a 3 phase generator.

well, I didn’t get a generator yet, the market has since bacame saturated with used 3Phase generators and they really dropped in price… but am I saving money, or should I sell the planer and get a smaller single phase planer. I haven’t decided yet.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#15

Re: C’mon Doorman, Throw Us A Bone!

10/10/2025 4:20 AM

We had a loss of power here Wednesday night for about 4 hours after the water company doing some repairs managed to dig up an underground power line. Several roads were affected &, because this is a rare occurrence, it was like the end of the world with neighbours out in the street trying to find out what was happening.

Luckily, I had installed some emergency lighting years ago so I wasn't plunged into darkness but had to break out the butane gas camping stove to brew tea.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jul 2017
Posts: 236
Good Answers: 9
#16

Re: C’mon Doorman, Throw Us A Bone!

10/10/2025 5:30 AM

Hi Doorman, there are a few points which are unclear or hazy to me.
1: it would appear this is a business property which you are thinking about converting to a private house

2: your assumption that it's a single phase 240vac is probably wrong, more like a 440vac three phase. (see table below.)

3: a 75 kW Gen would be for a house Overkill to say the least, not to mention fuel consumption / noise / modification costs etc.

4: There are combi Back-ups now on the market where the Gen, Invertor and Storage battery are all in a compact unit, might be worth looking at. or at least downgrade to around 15 - 20 kW Power. That should be enough for a large house.

5: As the building was intended for use as a Restaurant, it could be that the Gen is already hooked up the house..

6: From your comments, it would appear that you have not personally seen the property and depending on the Real Estate agent. As the seller seems to be holding back on info regarding the Gen, makes you wonder what else is being held back.

3 Phase Generator Size Guide

Generator SizeApplicationTypical Coverage
30-50 kWSmall CommercialRetail stores, small offices
60-100 kWMedium CommercialRestaurants, medical offices, schools
125-250 kWLarge CommercialHotels, supermarkets, data centers
300-500 kWIndustrialManufacturing, warehouses
600-2000 kWLarge IndustrialHospitals, factories, high-rises
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#17
In reply to #16

Re: C’mon Doorman, Throw Us A Bone!

10/10/2025 10:22 AM

Good morning!

In an effort to clear away any fuzz, responses by the numbers:

1) Yes, refer to paragraph #3 in original post.

2) Okay

3) Yes

4) I’ll check this out… from your description, this sort of setup is prolly on the small side for my desired use.

5) Yes, it is

6) I have visited the site; the tour was very brief, the subject emergency power system is but one small part of the entire property. Another, more focused, tour is somewhere on the event horizon.

__________________
Semper Ubi Sub Ubi
Register to Reply
Power-User

Join Date: Jul 2017
Posts: 236
Good Answers: 9
#18

Re: C’mon Doorman, Throw Us A Bone!

10/10/2025 1:02 PM

Re #4 in my list of questions and referring back to your original post, why would you want to have 4-5 days worth of Battery power before the gen kicks in ?
If you have a small battery capacity, say 1 day back-up, the Gen could kick in and start recharging the battery pack before it gets emptied, bit like a PHEV Hybrid car, runs on stored energy until the energy level falls to a preset point then the Engine kicks in and keeps the car running and recharging the battery at the same time.
Way far cheaper than investing a ton of money just to have 4-5 days worth of power available in batteries and you still need a Gen in case the power outage lasts more than 4-5 days.
Re the maintenance records of the existing Gen, most commercial Gens have a hourmeter fitted showing how long it ran for. My guess would be very low, especially if the Restaurant never went into business so basically no need to run the gen if the place was never opened.
It would help if you had the details of the Gen, then you could check out the market to see what value it would have on the used market. Having a new Inspection - Service would also increase its value. You might get enough to pay for a smaller 240v Gen more suited to your house size, without having to invest any money !
Have you calculated how much power your house would need, not counting charging batteries?
Have you taken into account if you would ever need 3 phase outside of using mains electricity ?
You could also put up a small wind turbine or two depending what sort of winds you would get there !
from your description the area gets a lot of snow, kills off the Solar but not the wind.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#19
In reply to #18

Re: C’mon Doorman, Throw Us A Bone!

10/10/2025 3:03 PM

The 4-5 days is arbitrarily voiced here, an indefinite quantity. An auto start scheme has been considered, but I would prefer the genset not run at night. The option of auto start hasn’t been shelved, but is not a first choice option.

Turbine(s) and/or PV have been considered, and remain viable options. These are also not first choice options, rather I am concentrating on a more ‘Control your own destiny’ sort of path.

Hour meter shows 92 hours, engine is very clean. Coolant, air filter, and engine oil are all dirty. I believe (I am well known as being cynical) neglect is the uniform of the day in the genset maintenance department.

3 phase is present at the site, but I believe the only utilization is in the sawmill (yes, this property has an operational sawmill!). It won’t ever be necessary to run the mill is the mains are down.

As I said in OP, thanks to all here at CR4 for your interest and comments about this not-very-well defined project. I realize it is difficult to offer advice when there isn’t some sort of a goal that is visible.

__________________
Semper Ubi Sub Ubi
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: