Before Synchronization — Generator Mode

11/25/2025 5:19 PM

Before synchronization, in which mode the generator should be operated in droop or isochronous?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#1

Re: Before synchronization - Generator mode

11/25/2025 7:34 PM

Droop and isochronous are modes of the governor of the engine driving the generator. If you increase the load on the generator, the mechanical load on the engine increases. In Droop, the engine will slow down, in isochronous it will still maintain a constant speed if possible.

When you parallel a generator with an existing bus, you increase the engine speed until the frequencies and phases of the generator and bus match. The generator's engine should be in droop mode. Once it is paralleled (connected), the generator's throttle is increased so that it assumes part of the load.

I hope this helps to answer your question.

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2

Re: Before Synchronization — Generator Mode

11/26/2025 10:53 PM

No need to go to isochronous governor unless you are the only or ideally the largest machine on the system.

Before synchronizing, the generator has no load, so there is no droop. Your speed/load control can be used to match frequency.

Once you parallel, you add speed so you pick up load, and your droop starts working.

Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#3

Re: Before Synchronization — Generator Mode

11/27/2025 7:57 AM

It will be dependent on the size or capacity of each generators that are going to be connected together..

If you expecting frequent load variations, I would suggest to use the Droop method especially if both generators are specification-wise identical.. The operating frequency settings for each would be a bit different, thus creating an upper and lower frequency operating limits that is acceptable during any load variations..

Otherwise use the Isochronous method where you set both generators to one identical operating frequency.... advisable only if you have a stable electrical loads..

__________________
vsar
Reply
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#4

Re: Before Synchronization — Generator Mode

11/28/2025 7:59 AM

If you have multiple generators in parallel, one should be in isochronous mode with its throttle controlling the frequency. The remaining generators should be in droop mode with their throttles adjusted for load sharing.

If you are adding a generator to an existing bus, the oncoming generator should be in droop mode and its throttle adjusted to pick up the desired amount of load.

Reply Good Answer (Score 3)