Low Voltage Switchboards

12/09/2025 12:05 AM

Why some vendors provide CTs at the load side of the breaker of the incoming panel and some vendor at the line side of the breaker of the incoming panel? what is the difference; does it have cost impact for the vendors?

Register to Reply
Pathfinder Tags: CTs Line side Load side
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#1

Re: Low Voltage Switchboards

12/09/2025 10:49 PM

In the olden days, locating the CTs on the load side of the breaker would allow you to access the CT connections with less risk of electrocution, with the breaker open.

In other cases, CTs on the line side can be used for bus differential protection schemes, where the differential zone includes the circuit breaker, providing extra protection in the case of a fault within the breaker casing.

In a switchboard, it is most likely finding space to mount the CT, a matter of economics in layout and equipment construction. If just simple overcurrent and metering, it most probably is cheaper to put them where they end up. Conventionally, they are mounted on the load side of a breaker, where safety ground clamps can ensure that there is no primary current if the CTs have to have their secondary windings open circuited.

Register to Reply Score 1 for Good Answer