LV Switchgear - IEC 61439 - Temperature Rise

08/14/2026 11:58 AM

The specification says, " LV Switchgear Bus bar temperature rise shall not exceed 45°C under rated current".

The ambient temperature is around 45°C.

It means the maximum permitted operational temperature under normal service conditions is 90°C (permitted temperature rise + Ambient temperature).

As I understand IEC allows the maximum copper busbar operational temperature under normal service conditions is 105°C.( 35°C ambient + 70°C temperature rise).

Is there anywhere mention the derating factor for the stringent temperature rise than the IEC allowed 7070°C temperature rise?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7431
Good Answers: 295
#1

Re: LV Switchgear - IEC 61439 - Temperature rise

08/14/2026 12:43 PM

“The specification says…”

Proper and professional business practice dictates that if a referenced model code (in this case, presumed to be IEC) is MORE restrictive than customer specifications, the model code should be used as a minimum.

Proper and professional business practice dictates that if a referenced model code (in this case, presumed to be IEC) is LESS restrictive than customer specifications, the customer specification should be used as a minimum.