EARTH LEAK UPS SYSTEM

12/19/2007 6:28 PM

WOULD some one help me how to solved problem earth leak 24 VDC system.The are a hundreds sensor equipment 24 volt Dc on the system. but system in line service and alarm some time appear and some times disappear. some of the sensor installed out side building and some of the on them in site building. The platform offshore is just finish on commisioning.

Your cooperate, fully appreciate.

Frans

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: EARTH LEAK UPS SYSTEM

12/19/2007 6:36 PM

Hi, Frans,

Please register, as (among other things) you'll be able to get e-mail updates of any replies.

What in your system is detecting this fault and triggering the alarm?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Anonymous Poster
#3
In reply to #1

Re: EARTH LEAK UPS SYSTEM

12/21/2007 4:21 AM

The alram just come from the comman alarm.The voltage when I take measurment on the termianl + = 20 volt dc, and - terminal just 5 volt dc. The system it self is floating 24 volt dc. DC power divided to DCS, SIS, radio communication, Crane, transformer sensor, protection system VCB,ACB, wet gas computer, down hole, HPU, sand filter, fiber oftic, ame others.

that is it.

Frans T

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: EARTH LEAK UPS SYSTEM

12/19/2007 8:22 PM

Hello Guest Frans,

Best to register at CR4 as already suggested above.

You do not provide sufficient information to ensure you may be correctly answered.

For instance, if the earth leakage is happening on a regular basis, it may well be the tide going in and out at that sea platform, which are giving you the problem.

Is there a dog or other, with a weak bladder problem, urinating on a cable, or several ?

Or it could be showers of rain.........

Reply here with .....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Commentator

Join Date: Feb 2007
Location: Wales UK. Tel. +44(0)1446 741180
Posts: 72
#4

Re: EARTH LEAK UPS SYSTEM

12/21/2007 5:01 AM

Try searching for the fault with a Vigilex earth fault tester. The device when connected superimposes a low frequency pulse on to the 24Volt supply referered to earth. Each branch can then be traced for earth faults with a portable hand held device that incorporates a current transformer probe and electronics to make this pulse visible on a meter. It then becomes a process of elimination.

This pulse will only be present on any circuit with an earth fault, circuits not returning this pulse can be eliminated from the search.

__________________
INDI-LINK makes 'Light' of 'Current' events, a veritable window into wiring.
Reply
Anonymous Poster
#5

Re: EARTH LEAK UPS SYSTEM

12/21/2007 10:16 AM

It may be caused by lightning , by which the cable may be getting damaged . You may try with some lightning arresters to save the cable

Arunava Mukerji

Reply
Anonymous Poster
#6

Re: EARTH LEAK UPS SYSTEM

12/22/2007 1:39 AM

Hi Frans,

Happy New Year everybody,

1st you should contact the UPS manufacturer to test the UPS.

2nd connecting a different types of loads to UPS is not so good, try to avoid that, usually you should keep each system connected to a seperate earth pit specialy LV data loads.

good luck