Anonymous Poster

Earthing point location

12/24/2007 10:49 AM

In an industrial power plant including four individual power generation units and related step up power transformers, the delta side of transformers is connected to generators and star side to main substation bus bars via relevant incoming circuit breakers.

Earthing system type that is considered in main substation is impedance grounding. Also the related resistor is not connected to star point of that mentioned transformers. They installed on star point of two zigzag earthing transformers that are connected to main bus bars of substation.

Indeed the earthing point of electrical system; because of some location problems are moved from typical place to substation room.

In the other hand, all main substation incomings are equipped by many earth fault relays (51N) that shall be protected the main bus bar against probable earth faults on it.

Next investigations shown that earth fault relays are not able to do works that assigned for it.

How can you explain the reason of that protection system inability?

BEST REGARDS

MSJ

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Earthing point location

12/24/2007 12:27 PM

It is mentioned that many 51 n relays are provided and these not functioning.

Have you done sytem coordination study and shortcircuit study and relays have been set.Then only you we can comment about the performance of these relays.

__________________
Ramesh,Freelance Electrical/automation Consultant