Neutral Grounding

12/27/2007 2:12 AM

why neutral grounding is done through resistance & why resistance of resistor is of low value.

__________________
nilesh
Register to Reply
Pathfinder Tags: resistance grounding
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: ngr

12/27/2007 2:29 AM

Hello nileshkonduskar,

Not all electrical systems use the low resistance in the Neutral to ground connection.

The reason is mostly to prevent extremely high fault current in transformers, and alternators.

It is also so that a sensor may be connected across the resistor, and the ground current easily monitored.

Please have a read here:

http://postglover.com/lowresistance.html

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: Neutral Grounding

12/27/2007 11:20 PM

Hello nileshkonduskar,

It is necessary for the designer to calculate (or measure) the earth fault loop impedance and make sure that it does not exceed the maximum specified in the wiring regulations. Having low grounding neutral resistance results in a small earth fault loop impedance and circuit can be protected, during faults, within a limited time.

For a radial system:

The earth fault loop impedance = resistance of the phase conductor+ resistance of the protective conductor + resistance of the grounding neutral

regards,

AMSG

Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#3
In reply to #2

Re: Neutral Grounding

12/27/2007 11:39 PM

Generally the relays are tripped on fault current and will be sensitive if the ressitsnace from neutral ground is low an dhence current high. So more sensitive to neutral voltage and trips the circuit.

Only used when you have tripping system on earth falut/ overcurrent etc. To ensure safety.

__________________
Best Regards, Shivaram
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#10
In reply to #2

Re: Neutral Grounding

01/02/2008 8:08 AM

The loop resistance should take into consideration while calculating grounding resistance. But practically its bit difficult to calculate the value, since datas are not available at the initial stage of the project. Hence, the NGR is considered is the only restricting element for ground fault. Practically the actual earthfault current is little less than the calculated current. If the fault is not Bolted the current may further reduce. Its a general practice to consider only NGR value even at later stage of project.

__________________
BNDas
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#4

Re: Neutral Grounding

12/28/2007 4:40 AM

This is an "off the wall" response.

Are you sure it's a resistor not an inductor?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#5
In reply to #4

Re: Neutral Grounding

12/28/2007 8:51 AM

I don't recall seeing an inductor in that application.

The grounding resistors, I have seen a few pictures where parts of them have been destroyed due to extreme fault currents or a bad mounting location resulting in corrosive type damage, some of these resistors are quite old, usually on low shaft speed hydro generators, can't recall seeing them at shaft speeds above 1200rpm.

The protective relay used measures the voltage across the neutral grounding resistor.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #5

Re: Neutral Grounding

12/28/2007 6:49 PM

Hello CoronaCameraMan,

Inductors in a ground connection are sometimes used at AC to DC conversion stations, where Earth return circuitry is used - generally that type of DC supply is Volts DC (+) to Earth, and Volts DC (-) to Earth, with a common Earth return..

In that situation they are used for monitoring harmonics in the DC circuit Power output through the Earth conductor, and also via feedback loops and controllers, for reducing the harmonics present in the DC output from the AC to DC conversion station.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#7

Re: Neutral Grounding

12/30/2007 12:25 PM

Hi,

Your post is not clear, so I'll give you another answer. Some electronic instruments have a resistor in the Earth connection (where the green wire goes). It is to reduce the effect of "ground loops", which can cause measurement errors. I assume it's low value (≈ 1 ohm) is keep some measure of safety.

S

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8

Re: Neutral Grounding

12/30/2007 3:10 PM

There are also a number of code issues involved.

In some countries (Canada) there is a trend to solidly ground systems.

However, the first ground fault trips the breakers (that was the idea, right?).

So, you don't want your plant to go down on the first ground fault and you can tolerate a corner grounded system. But that is a fault condition that you must alarm, so you can repair it on a scheduled down day.

Now, for the 10 amp grounding resistors, it is not excessive power for a fault detection system and gives a reasonably stiff neutral connection to ground. This is good, because when you energize the high voltage side of the transformer you want to discharge the capacitive coupling between primary and secondary as quickly as possible. Also, the 10 amp grounding helps absorb transient voltages from noisy machinery and devices keeping the neutral close to ground in normal operation.

And then there is always the tradition. You can't fight tradition, without being declared a heretic!

Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#9

Re: Neutral Grounding

01/02/2008 7:46 AM

Hi Everybody,

Wish you happy new year...

The function of the neutral earthing resistor is to lower the ground current to a certain value, accordingly, protecting the transformer against failure in the insulation level that might occurr as a result of sever ground current.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); biswanath.das (1); CoronaCameraMan (1); GW (1); Randall (1); shivaganti (1); Sparkstation (2); StandardsGuy (1); TITO60 (1)

Previous in Forum: AC Engine Alternator Conversion Project   Next in Forum: Steam Turbine Generator Set

Advertisement