Bus Bar Calculation

01/03/2008 5:35 AM

hi friends ...happy new year to all

can anyone plz tell me the formula to calculate the current for bus bar when we are having a demand load of 11.93 KW .ie the current rating for bus bar supporting 11.93 KW load ..plz answer right now if u r online

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: bus bar calculation

01/03/2008 6:45 AM

What voltage?

Current = Power / Voltage

(Amps, Watts, Volts)

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Anonymous Poster
#4
In reply to #1

Re: bus bar calculation

02/28/2008 11:40 AM

Would you help me to size the bus bar for following load:

type of bus bar= Aluminum bus bar

I=86000ADC

V=240

Total lenght=1300ft

load consist of 40 electrolytic Cells connecting in series to the bar.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #4

Re: bus bar calculation

02/28/2008 6:50 PM

Sorry, my friend, this is out of my league.

Please register with CR4, and ask the question (use the ASK A QUESTION button up on the top right corner). If you register, you're much more likely to get a good answer.

I'm pretty sure that you'll get a good response if you register. Looks like you've done a good job of expressing your problem, you've just got to get the rest of CR4 to notice it & take it seriously.

[For your information: I have education & background knowledge that could lead me to an approximate answer (informed guess ) - but no formal training or experience in high current stuff. Biggest wire I use/specify regularly is 2.5mm2].

Good luck & best regards,

John

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Commentator

Join Date: Sep 2007
Location: Here, there and everywhere...
Posts: 61
#2

Re: Bus Bar Calculation

01/03/2008 10:58 AM

Go to the Copper Development Association in the US.

www.copper.org

__________________
An EXPERT is a 'has been', that is a drip under pressure - My Boss
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#15
In reply to #2

Re: Bus Bar Calculation

12/29/2009 12:57 AM

Thank you very much for the guidance. it is very informative.

Regards

Register to Reply Off Topic (Score 5)
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#3

Re: Bus Bar Calculation

01/03/2008 8:32 PM

Hi,

For 11.93KW load, find out the total current depending upon the voltage system.

With 415V, 50Hz system, the total current will be approximately 16.7A.

If you use Cu for Bus bar, the current density is taken as 1.2A/Sq.mm. So the Area of Cross section required to caryy the current is = 16.7/1.2 Sq.mm. In Indian Standards, we use a minimum size of 25x3 Sq.mm of Cu.

And if Aluminium, it is 25x6 Sq.mm minimum. (Current density: 0.8A/Sq.mm)

You may transfer the data to your country standards.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Anonymous Poster
#6
In reply to #3

Re: Bus Bar Calculation

05/13/2008 6:18 AM

first of all thank u for ur information , one more request in u sir, pl tell me the methods of calculating the current carrying, and the factors considering and other information, and calculating the current density for various materials

pl reply me on rocky4u712@indiatimes.com

Register to Reply
Anonymous Poster
#7
In reply to #3

Re: Bus Bar Calculation

05/17/2008 3:48 AM

Dear sir

I have small doubt about how to calculate bus bar size for 3000A ACB INCOMER

and 400A out going-5 Nos

and 800A bus coupler

thanks and regards

K.Kajajohn

Register to Reply Off Topic (Score 5)
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#16
In reply to #7

Re: Bus Bar Calculation

12/29/2009 1:03 AM

Dear Kajajohn..

first you have to decide.. whether copper or Aluminium busbar is used..

Then the current., Voltage, frequency, Load factor, acceptable Temperature rise of busbar in the enclosure.. Ambient Temperature, short-circuit withstandlevel.. type of protection device and the relay settings for the busbars...Application - whether inductive loads or harmonic loads...

Well all the components ratings are decided on the above basic factors

Register to Reply
Anonymous Poster
#17
In reply to #16

Re: Bus Bar Calculation

01/04/2010 2:37 AM

Alluminium Bus bar

415 Volts

8000 Amp

50 Hz

45 deg C

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#18
In reply to #17

Re: Bus Bar Calculation

01/04/2010 3:19 AM

Dear Guest,

What is the Transformer KVA rating,/ No of transformers ? Please tell your scheme in brief. I have application engineering till 6000A for Aluminium. But for currents like 8000A, i have observed copper busbars. I think a lower dimension Cu busbar can carry higher currents compared to aluminium of the same dimension.

Register to Reply
Anonymous Poster
#8
In reply to #3

Re: Bus Bar Calculation

05/31/2008 8:56 AM

Dear sir,

Current density for Cu and Al busbars are mentioned as 1.2 A/sqmm and 0.8 A/sqmm resp. Could you please give some reference for these data?

Are these data mentioned in IS?

Register to Reply
Anonymous Poster
#9
In reply to #3

Re: Bus Bar Calculation

07/18/2008 4:08 AM

would you pls tell me how to calculate current density or it it constant for all loads.i have doubt with it

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#10
In reply to #9

Re: Bus Bar Calculation

07/18/2008 4:19 AM

The current density is the current through the bus-bar, divided by its cross-sectional area. The limit of current density depends on the material from which the bus-bar is made, and the geometry.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Anonymous Poster
#11
In reply to #10

Re: Bus Bar Calculation

07/18/2008 6:46 AM

Of course yes. But i want to determine the area of bus bar which is current of the load/current intensity of bus bar for copper. SO i would like to know the current density of copper bus bar i have 1600A load so i need to determine bus bar area for this ok.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#12
In reply to #11

Re: Bus Bar Calculation

07/18/2008 11:35 AM

I don't have that data. Try here, here or here.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Anonymous Poster
#13

Re: Bus Bar Calculation

09/23/2008 1:59 AM

FIRST U HAVE TO CONVERT KW INTO CURRENT. IF U HAVE 3PHASE LOAD THAN THE FORMULA IS 11.93 X 1000/420 X 1.732 X .8 THE CURRENT WILL BE 20A

Register to Reply Off Topic (Score 5)
Anonymous Poster
#14

Re: Bus Bar Calculation

06/17/2009 8:05 AM

Bus-Bar Material - Alluminium

Length of Bus-Bar - 25mm

Thickness of Bus-Bar - 6mm

Then How much amp. and current will draw by Bus-Bar?

Our Company Name: Universal Packaging Solutions

E-mail: upacksolutions@gmail.com

Contact Person : Raju J. Madhad(09825793052)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19

Re: Bus Bar Calculation

12/28/2025 5:55 AM

Click here , as many people can.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (9); JohnDG (4); mixit (1); PWSlack (1); shanbhag (3); user-deleted-1098 (1)

Previous in Forum: POWER CABLE SELECTION   Next in Forum: Cable Problem

Advertisement