hi friends ...happy new year to all
can anyone plz tell me the formula to calculate the current for bus bar when we are having a demand load of 11.93 KW .ie the current rating for bus bar supporting 11.93 KW load ..plz answer right now if u r online
Re: bus bar calculation
01/03/2008 6:45 AM
What voltage?
Current = Power / Voltage
(Amps, Watts, Volts)
02/28/2008 11:40 AM
Would you help me to size the bus bar for following load:
type of bus bar= Aluminum bus bar
I=86000ADC
V=240
Total lenght=1300ft
load consist of 40 electrolytic Cells connecting in series to the bar.
02/28/2008 6:50 PM
Sorry, my friend, this is out of my league.
Please register with CR4, and ask the question (use the ASK A QUESTION button up on the top right corner). If you register, you're much more likely to get a good answer.
I'm pretty sure that you'll get a good response if you register. Looks like you've done a good job of expressing your problem, you've just got to get the rest of CR4 to notice it & take it seriously.
[For your information: I have education & background knowledge that could lead me to an approximate answer (informed guess ) - but no formal training or experience in high current stuff. Biggest wire I use/specify regularly is 2.5mm2].
Good luck & best regards,
John
Re: Bus Bar Calculation
01/03/2008 10:58 AM
Go to the Copper Development Association in the US.
www.copper.org
An EXPERT is a 'has been', that is a drip under pressure - My Boss
Engineering Fields - Electrical Engineering - New Member India - Member - New Member
12/29/2009 12:57 AM
Thank you very much for the guidance. it is very informative.
Regards
01/03/2008 8:32 PM
Hi,
For 11.93KW load, find out the total current depending upon the voltage system.
With 415V, 50Hz system, the total current will be approximately 16.7A.
If you use Cu for Bus bar, the current density is taken as 1.2A/Sq.mm. So the Area of Cross section required to caryy the current is = 16.7/1.2 Sq.mm. In Indian Standards, we use a minimum size of 25x3 Sq.mm of Cu.
And if Aluminium, it is 25x6 Sq.mm minimum. (Current density: 0.8A/Sq.mm)
You may transfer the data to your country standards.
Assistant Electrical Inspector, Govt. of Kerala, India
05/13/2008 6:18 AM
first of all thank u for ur information , one more request in u sir, pl tell me the methods of calculating the current carrying, and the factors considering and other information, and calculating the current density for various materials
pl reply me on rocky4u712@indiatimes.com
05/17/2008 3:48 AM
Dear sir
I have small doubt about how to calculate bus bar size for 3000A ACB INCOMER
and 400A out going-5 Nos
and 800A bus coupler
thanks and regards
K.Kajajohn
12/29/2009 1:03 AM
Dear Kajajohn..
first you have to decide.. whether copper or Aluminium busbar is used..
Then the current., Voltage, frequency, Load factor, acceptable Temperature rise of busbar in the enclosure.. Ambient Temperature, short-circuit withstandlevel.. type of protection device and the relay settings for the busbars...Application - whether inductive loads or harmonic loads...
Well all the components ratings are decided on the above basic factors
01/04/2010 2:37 AM
Alluminium Bus bar
415 Volts
8000 Amp
50 Hz
45 deg C
01/04/2010 3:19 AM
Dear Guest,
What is the Transformer KVA rating,/ No of transformers ? Please tell your scheme in brief. I have application engineering till 6000A for Aluminium. But for currents like 8000A, i have observed copper busbars. I think a lower dimension Cu busbar can carry higher currents compared to aluminium of the same dimension.
05/31/2008 8:56 AM
Dear sir,
Current density for Cu and Al busbars are mentioned as 1.2 A/sqmm and 0.8 A/sqmm resp. Could you please give some reference for these data?
Are these data mentioned in IS?
07/18/2008 4:08 AM
would you pls tell me how to calculate current density or it it constant for all loads.i have doubt with it
07/18/2008 4:19 AM
The current density is the current through the bus-bar, divided by its cross-sectional area. The limit of current density depends on the material from which the bus-bar is made, and the geometry.
07/18/2008 6:46 AM
Of course yes. But i want to determine the area of bus bar which is current of the load/current intensity of bus bar for copper. SO i would like to know the current density of copper bus bar i have 1600A load so i need to determine bus bar area for this ok.
07/18/2008 11:35 AM
I don't have that data. Try here, here or here.
09/23/2008 1:59 AM
FIRST U HAVE TO CONVERT KW INTO CURRENT. IF U HAVE 3PHASE LOAD THAN THE FORMULA IS 11.93 X 1000/420 X 1.732 X .8 THE CURRENT WILL BE 20A
06/17/2009 8:05 AM
Bus-Bar Material - Alluminium
Length of Bus-Bar - 25mm
Thickness of Bus-Bar - 6mm
Then How much amp. and current will draw by Bus-Bar?