Rated Current Calculations

01/05/2008 2:19 AM

hi, this is my first post on CR4, i've been visited this site for a couple of months, and i really like it. good working people.

since i have a v.good knowladge about Electrical engneering, is there anyone can help me with rated current cal. for air blower with these spac.

app. : centrifugal blower

motor type: Cage rotor

rated power (Kw) : 1200

power supply (V) : 4160

full load speed (rpm) : 3575

full load current : 195

eff. @ 100% : 96.1

eff. @ 50% : 96.2

P.F @ 100% : 91.7

P.F @ 50% : 91

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#1

Re: Rated Current Calculations

01/05/2008 6:48 AM

Hello Abo,

Are you certain you have the spec right? The supply voltage seems odd to me! Is it a 3 phase system? What does it say on the spec plate of the unit! Can you post a picture of the said plate?

Happy 2008

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Rated Current Calculations

01/05/2008 7:54 AM

From the details i feel its 2 pole machine suitable for 60Hz Supply.As pointed out Voltage mentioned is incorrect.Alos effiecy at half load is more than full load which is not the case for most motors unless specially designed .The formula is

Rated kw÷√3×Voltage×Full load Eff×Full load PF

with given figs if u calculate current is approx 188amp assuming it is 4.16KV

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#3

Re: Rated Current Calculations

01/05/2008 8:51 AM

As long as you are talking about a motor, its rated power is a mechanical one, thus the current will be the the mechanical power divided by the rated efficiency, rated power factor, square root of 3 (supposing a three phase system) and rated voltage, that is 189 (A) rather than the 195 (A) present.

Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#4

Re: Rated Current Calculations

01/05/2008 9:42 AM

Welcome,

You need to clarify your question a bit. The data is good, but you already have full load current which could be taken as rated. Or are you talking max continuous current? Or starting current?

You did not specify service factor. Typically 1 to as much as 1.5, which would tell you how much current you can draw safely under continuous conditions.

Register to Reply
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#5

Re: Rated Current Calculations

01/05/2008 11:38 PM

The rated current is 195 Amps. i.e. the full load current.

It is possible that the motor is capable of higher than that, i.e. the full load current may be the full load current driving the fan at full fan load, but you can use that as the rated current.

Best regards,
Mark Empson

http://www.LMPhotonics.com | http://www.LMPForum.com

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Rated Current Calculations

01/06/2008 9:45 AM

The rated current mentioned in the name plate is the current drawn by the motor when delivering full out put.The actual current will be less depending upon the loading as well the margin considered while arriving at the rated power for motor.Normally minimum 10% over fan BHP will be considered so the fan power required will be 1100kw and current drawn will be this KW divided by root 3 pf and Efficiency at 90% load and the voltage.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#7

Re: Rated Current Calculations

01/06/2008 1:14 PM

Since you have as you say "v. good knowladge about electrical engneering, could you please explain to a layman:

  1. How can efficiency @ 50% rated voltage be better than @100% rated voltage?
  2. What is exactly "rated current cal"?

Beside, if you are asking about FLA, isn't it already in your specs? enlighten me please.

Wangito.

PD: What you obviously lacking is the knowledge about using the spell checker.

__________________
Never trade luck for skill.
Register to Reply
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#8
In reply to #7

Re: Rated Current Calculations

01/06/2008 1:35 PM

It is normal for the peak efficiency of an induction motor to be at less than 100% load. Most machines have a peak efficiency at around 75% load, so 50% is not impossible.

Best regards,

Mark Empson
http://www.LMPhotonics.com | http://www.LMPForum.com

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#9

Re: Rated Current Calculations

01/03/2011 3:28 AM

Seems to calculate. I = P/1.73/U/cos*/efficiency. therefor calculated @ 50% data: I = 1200000/1.73/4160/.91/.962 = 190.47A regards.

__________________