Anonymous Poster

busbar size

01/05/2008 5:24 AM

main busbar current rating inside the panel (PMCC) is 2500A. what should be the main bus bar size.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Sep 2007
Location: Here, there and everywhere...
Posts: 61
#1

Re: busbar size

01/05/2008 10:45 AM

Go to the US Copper Development Association www.copper.org.

__________________
An EXPERT is a 'has been', that is a drip under pressure - My Boss
Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#2

Re: busbar size

01/05/2008 11:53 PM

According to MiddleEast Specifications we use a bus bar size of

1. 2 Nos X 80mm X 10 mm

Regards

Dhilju

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: busbar size

01/06/2008 2:07 AM

Busbar design for MCC/PCC/SwitchBoards,there are many aspects.

1) Thermal current

2) Short circuit current.

3) Limitation in Temperature rise inside the PCC

4) Ambient temperature.

5) Sleeved Busbar/Unsleeved busbar

6)Enclosure Dimension

Based on the above input only the sizing can be arrived at.

For Higher rated currents

Rough thumb rule would be 0.6 amps per sq mm in case of Aluminium and 1.25 amps per sq.mm for Copper.

The calculations have to be made based on the above inputs.cross sectional area to be calculated for thermal current and short circuit current seperately .the higher cross section is between the two calculations have to be considered.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Participant

Join Date: Mar 2008
Posts: 3
#4
In reply to #3

Re: busbar size

03/24/2008 8:44 AM

Rough thumb rule would be 0.6 amps per sq mm in case of Aluminium and 1.25 amps per sq.mm for Copper.

The calculations have to be made based on the following inputs

1) Thermal current

2) Short circuit current.

3) Limitation in Temperature rise inside the PCC

4) Ambient temperature.

5) Sleeved Busbar/Unsleeved busbar

6)Enclosure Dimension

cross sectional area to be calculated for thermal current and short circuit current seperately .the higher cross section is between the two calculations have to be considered.

Kindly describe the calculation based on which the cross section of bus bar are calculated for thermal current and short circuit current seperately

Reply
Participant

Join Date: Jul 2009
Posts: 4
#6
In reply to #3

Re: busbar size

08/14/2009 8:21 AM

DEAR SIR,

PLEASE GIVE THEROTICAL CALCULATIONS/METHOD FOR BUSBAR SIZE CONSIDERING YOUR POINTS.

Reply
Anonymous Poster
#5

Re: busbar size

05/06/2008 8:44 PM

Hi

When we calculate the Bus Bar sizes, we will design it for meeting the Temp Rise limits, Short Circuit Current Withstand Strength in terms of Mechanical & Electro Thermal Stresses. What about the Bus Bar Bracings short circuit withstand capabilities? The Bracings / Bus Bar Joints are to withstand the Short Circuit Making Currents and not just the Breaking since that current is allowed to let through the Bus Bars. Any thoughts?

Anil Sabaji

Reply