Tension Variation - Electrical Power

01/08/2008 10:42 AM

My elevator maintenance company (provider) tells me, after each service call, that the cause the 600V, 3-Phase motor that drives the elevator stops working is because of the variation in the line voltage…

  • Does Hydro Quebec have some standard to respect, like for 600V is there a absolute lower and maximum limits to respect, further more is there some variation limits between phases.
  • On the other hand, does equipment builders have some reasonnable variations limits that they shoud comply whit and what are they
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Tension Variation - Electrical Power

01/08/2008 11:01 PM

Equipment (in North America) such as a motor, is generally designed to operate with +- 10% voltage variation and maintain nominal speed and torque (NEMA Standard MG-1). But if you run it at either limit continuously, the life of the motor will be shortened. Utilities are typically required to maintain +- 5% nominal voltage for most customers, but are "allowed" to get away with up to a 10% swing for short durations, i.e. a few seconds.

One problem is, the Utility is only required to maintain that at the terminals of your incoming service. You may have a problem after that, but it would not be their fault. For instance if you have too much of a load on your service, they have to be told and they will charge you more of course. So often times, people try to get away with not upgrading a service when they should and the end result is things like this. You may also have inadequately sized conductors feeding the service panel for the elevator, which causes a voltage drop. You may also have a loose connection somewhere. The list goes on and on.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Tension Variation - Electrical Power

01/09/2008 2:02 AM

Does the motor fail and they repair or rewind ?Elevator motor comes under a different category.The motor starts and stops frequently and correctly designed motor with a different duty cycle is to be used.If its a question of voltage do u always have low voltage? as Rightly said motors are designed for 10% Voltage and can continuously operate at +- 10%.I think motor name plate details can reveal lot of Information.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Nov 2007
Posts: 53
Good Answers: 1
#3

Re: Tension Variation - Electrical Power

01/09/2008 2:28 AM

Hi Brim, #s 1 and 2 gave good advice. You need to measure the voltage and current at the input of your motor, under operating conditions, to determine if it is being supplied properly or whether there is a load or motor problem. On all phases by the way.

__________________
Clintb3252
Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#4

Re: Tension Variation - Electrical Power

01/09/2008 2:57 AM

What does the voltage variation mean? If it's under or over voltage, your facilities should be ok because manufacturer made their goods based on approved standard, except the under/over beyond the standards. Fellas here have explained to you the voltage tolerance.

But if it's transient voltage, electronic components in PLC, PC, Drive, etc without proper protection devices, will fail. AC motor should be ok against this transient. Then power metering system should be developed to accomodate this such situation.

Transient will cause PLC to "lock out".

If its voltage imbalance, the motor's temperature will get hot. 3.5% imbalance will significantly increase the temp. to about 25%. Voltage imbalance shall be limited to below 1% at all voltage levels.

Anyway, what cause the motor to stop? Circuit breaker trip, TOL work, etc, briefly does your system provide "alarm/fault history"?

Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#5

Re: Tension Variation - Electrical Power

01/09/2008 12:25 PM

Another thought - when applying all of the good suggestions for testing that previous posts suggested, it might be wise to have a disinterested 3rd-party electrician do them - one that knows you won't be having him in to do service work. The service provider may be giving you insufficient information. After all, he has an interest in further service calls... Couldn't hurt.

__________________
Veni, vidi, video - I came, I saw, I got it on film.