Duty Cycle

01/09/2008 11:25 AM

i wana know about the duty cycle...on electrical equipments duty is always written like Duty= s1.. i know duty cycles are from s1 to s8. what does it mean duty s1??? similarlly S2, s3 ...etc

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Duty Cycle

01/09/2008 2:26 PM

Duty cycle refers to the time when a motor is doing 'work'.

From Here http://answers.yahoo.com/question/index?qid=20070820053208AASG63E

and Here http://books.google.com/books?id=8mQewRR_3q4C&pg=RA1-PA54&lpg=RA1-PA54&dq=electrical+duty+cycle+s1&source=web&ots=TcpNtxF5j-&sig=U-8BpKyH9BshzD-_MuCldbNundQ#PRA1-PA56,M1

"The eight - S1 - S8 - IEC duty cycles of operating electrical motors

IEC (the International Electrotechnical Commission) uses eight duty cycle designations to describe an electrical motors operating conditions:

S1 - Continuous duty. The motor works at a constant load for enough time to reach temperature equilibrium.
S2 - Short-time duty. The motor works at a constant load, but not long enough to reach temperature equilibrium. The rest periods are long enough for the motor to reach ambient temperature.
S3 - Intermittent periodic duty. Sequential, identical run and rest cycles with constant load. Temperature equilibrium is never reached. Starting current has little effect on temperature rise.
S4 - Intermittent periodic duty with starting. Sequential, identical start, run and rest cycles with constant load. Temperature equilibrium is not reached, but starting current affects temperature rise.
S5 - Intermittent periodic duty with electric braking. Sequential, identical cycles of starting, running at constant load and running with no load. No rest periods.
S6 - Continuous operation with intermittent load. Sequential, identical cycles of running with constant load and running with no load. No rest periods.
S7 - Continuous operation with electric braking. Sequential identical cycles of starting, running at constant load and electric braking. No rest periods.
S8 - Continuous operation with periodic changes in load and speed. Sequential, identical duty cycles run at constant load and given speed, then run at other constant loads and speeds. No rest periods."

__________________
Perfection is a subjective and abstract concept.
Register to Reply Good Answer (Score 2)
Member

Join Date: Jan 2008
Posts: 7
#2

Re: Duty Cycle

01/10/2008 2:26 AM

Dear friend,

You can refer IS:325 wherein all required details are given. Or else, you can refer catalogue of a reputed manufacturer like Siemens, Crompton Greaves, ABB, BBL, Kirloskar Electric etc.

D.D.DESAI