kVA Off a Pole-Bolted xfrmr

01/09/2008 8:17 AM

HI all.
I am trying to calc the the KVA of a 100A service off a 25 kVA transfomer. I am using 3 1/0 Al for a total run of about 200'. It's a 120/240 system set up as a delta connected load side.

In order to get the kVA, would I just multiply 100A X 240V and then divide by 1000? This would be 24 kVA, which would be too much for this XFORMER, right?

The load is for the phone company(ATT) and I would venture a guess that there is no way they are going to be using the full 100A.

TIA

__________________
gisdude
Register to Reply
Pathfinder Tags: kVA
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#1

Re: kVA Off a Pole-Bolted xfrmr

01/09/2008 10:10 AM

Your formula is for a single-phase installation. Since you metioned delta connection, this sounds like 3-phase. If it's connected 3-phase, you need a √3 factor in your calculations.

How are you getting the 120? Even if you have a neutral center-tap on one phase (sometimes called a "high-leg" system), you still need 4 wires to get all 3 phases plus the neutral.

Also, is the transformer a single 3-phase unit, 2 1-phase units connected open-delta, or 3 1-phase units connected full delta? If the installation is multiple units, what is each can rated?

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Associate

Join Date: Jun 2007
Location: Sacramento, CA
Posts: 33
#2

Re: kVA Off a Pole-Bolted xfrmr

01/09/2008 2:45 PM

this is a 120/240v delta system, only one can on the pole.

you ARE correct, I do need the 1.732 in the calc. it seems as though when I do the calc, it comes out to 24kVA. this seems pretty hi for such small load. I do know for a fact that these "b-boxes" are really small amps, prolly 40-50 range, but I'm calc'ing out for the 100 amp breaker, per regualations.

thanks