Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/09/2008 6:33 AM

Dear Sir,

We are using a 22kW motor to drive our rotating kiln. The maximum current of the motor is 42A. (We are using eddy current coupler with the gear box.) No load current of the motor is 15.7 Amps and when loaded it is only takes 18.5 Amps. So it is clear that we don't need such a big motor (22kW) to drive the kilns. If the load is constant, what is the most suitable size of the motor for our kiln?

Jan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Finding suitable size of the motor by comparing no load and load currents

01/09/2008 6:59 AM

Shaft power = torque x angular velocity.

Bear in mind that the torque can go up depending on what is happening inside the kiln.

Motor power = shaft power / motor efficiency.

Supply current = motor power / voltage / power factor.

What is the supply voltage?

What is the business objective in fitting a smaller motor?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Finding suitable size of the motor by comparing no load and load currents

01/09/2008 7:07 AM

Hello jcl

The other thing to remember is: How old is your existing motor?

If you motor is many years old, it will be a large framed one, with a large diameter shaft, run quite cool, just be not working hard (giving long life, no bearing worries), and be able to cope with sudden load changes.

If you replace with a more modern motor, it will be much smaller, small diameter shaft, run hot enough to fry an egg on the casing, working fully all the time, (will need repairs and bearings more often), and sudden load changes may give the motor a "heart attack".

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#3

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/09/2008 11:25 PM

Hi jcl,

First when you want to design some machine or some system that was drived by motor, You have to calculate the load of that machine or system, then the load of shaft of motor, and finally must to choose correct motor.

Please see carefully on motor's name plate 42A current with what the voltage is and what the voltage is using. And your machine was running with maxi load and maxi speed or not, what the current start is with maxi load? These informations are found easily in operation manual of your machine.

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Anonymous Poster
#5
In reply to #3

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 12:26 AM
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#4

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/09/2008 11:29 PM

10KW CONT.duty is fine!

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 1:31 AM

You have number of issues involved here, as others before me have pointed out.

First off, a motor uses energy from the supply to do work and the energy it absorbs consists of the work performed plus the losses in the system. So if you are only doing enough work to require 18.5A then that is all it will take, regardless of how oversized the motor is, leaving only the losses as the area to potentially save energy. Losses in an AC motor system consist of the following:

  • Load losses, i.e. mechanical losses in the power transmission system such as friction (and in your case the eddy current clutch, discussed later)
  • Copper losses, i.e. the resistance of the copper wire used in the stator windings.
  • Magnetic Losses, i.e. the internal eddy current losses due to the magnetization of the steel laminates in the core and rotor.
  • Wndage losses, i.e. the mechanical energy it takes to create cooling air flow over the motor to keep it cool and any wind created by the load.

Of all these losses, ONLY THE MAGNETIC LOSSES ARE AFFECTED BY HAVING AN OVER SIZED MOTOR . All of the other losses will be essentially the same or so close they are not worth considering. The magnetic losses will comprise about 18-24% of the total losses, depending on the design efficiency of the motor. So if that existng motor is relatively old and is 85% efficient, your absorbed power is roughly 10kW (as pointed out by someone else). So then your total losses are roughly 1.5kW, which means your magnetic losses are at most, 350W. If you reduce the motor to 10kW and use a newer motor which is 90% efficient, your total losses are 1kW, which means your magnetic losses (which will be lower in an energy efficient motor) will probably be 180W. So on paper, it appears that you cut your losses by almost 50%, but in reality you went to all that expense to save 170W and now you have a marginally rated motor that will be more easily overloaded. Evaluate the economic benefits with that in mind. For instance how much money would you lose in production if the motor trips on overload and you must wait 30 minutes per day for it to cool off and reset?

A better place to look for energy savings may be in that eddy current clutch. If you use that to throttle back speed or torque, consider using a Variable Frequency Drive instead. The eddy current clutch is probably 80% efficient (if that) and a VFD is around 97% efficient, so you will get an immediate gain of at least 15+% in overall efficiency, so n this case 1.5kW!. In addition, the VFD will change the motor utilization curve to have it deliver only the HP that the load requires, so your magnetic losses will be reduced as well, without having to buy a new motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Participant

Join Date: Jan 2008
Posts: 2
#12
In reply to #6

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/11/2008 7:06 AM

Dear JReaf,

Thank you very much for your very good explaination.

Acctually I am trying to reduce the electrical consumption of the factory. So I thought I could reduce the electricity bill by replacing small motors to our 5 kilns (soon it will be 10 kilns)

The motor specificatins are as follows,

Output : 22kW

Current : 42.5 A

Voltage : 380 V ( but our supply voltage is 400V, I think it is also another problem)

Speed : 1470 r/min 50 Hz Ins Cl. B

Rating : S1

Spec of Magnetic Clutch,

Excite voltage : 70 V

Excite current : 2.88 A

Ins. : B

Rating : S1

So according to the infomation I have given, do you think I can't save much electricity by changing motors for 5 kilns.

Please advice.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #12

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/11/2008 7:46 AM

"Acctually I am trying to reduce the electrical consumption of the factory. So I thought I could reduce the electricity bill by replacing small motors to our 5 kilns (soon it will be 10 kilns)"

Reducing energy consumption and reducing the energy bill are not always the same thing. Replacing the motors will not likely do much to reduce the energy consumption; if you run the kilns 24/7/365 then a small incremental improvement in efficiency may add up over time, but that must be weighed against the cost of replacing the motors. Include the labor, downtime and risk of further downtime if there happened to be a valid reason for having 22kW motors in the first place that you may be overlooking. Don't forget that you are second-guessing the original engineering decision, something that comes with risks if you don't have all the facts as to why the original engineer decided on those motors.

But if your energy BILL includes penalties for having poor power factor, then you may be able to reduce the bill even if the energy stays the same, because it is likely that you have poor power factor with such a light load. So if you choose not to replace the motors, at least look into Power Factor Correction capacitors.

As I said earlier, I would also evaluate the need for the clutch drive system. They are notoriously inefficient but may have been put in when VFDs didn't yet exist or were too expensive. Replacing those with VFDs would be an immediate way to save energy and may not require the replacement of the motors (if done right) or the addition of PFC capacitors, they will take care of both issues as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#16
In reply to #12

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/12/2008 2:19 AM

Acctually I am trying to reduce the electrical consumption of the factory. So I thought I could reduce the electricity bill by replacing small motors to our 5 kilns (soon it will be 10 kilns)

The solutions of Mr.JRaef are perfect, you should do it.

I want tell more about your opinion. The power of motor is 22kw, this mean the max. load of it is 22kw it depents on your load, if your load is P~400V*18.5A~7.4kw, mean your motor power is output also 7.4kw,.... Just image that after you install new motor with power 400V*25A~10kW, and you measure current again the result will be 18.5A too. If your kilns runed with max load this means you can not add any workpieces into your kilns or your kilns contained max designed weight,...( I don't belive that) and your current is 18.5A too, please tell this to kiln manufacturer for improving 5 kilns that will be installed in the near future and you will save some money: machine cost, electricity bill, place cost(smaller machine is cheaper than and smaller dim).

You can use the rate of electricity bill and sale (or production quantity) to improve your project instead of only electricity bill. In our factory, I had rearranged lightings system by turn on some needed ereas while producing or improved productivity,....

Good luck and success

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Anonymous Poster
#17
In reply to #16

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/12/2008 2:27 AM

ha ha, just seem that there are some unneccessary parts in your factory. reducing lighting is just suitable only for your factory, man

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#15
In reply to #6

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/11/2008 9:46 PM

Hello JRaef

Your answer is consistently good, so I gave you a Good Answer tick too.

Cheers and Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Member

Join Date: Jan 2008
Posts: 7
#7

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 2:19 AM

Dear friend,

You can measure directly KW consumed with the help of a LOAD MANAGER and then divide it by eff. of motor say 0.9 which will give you theoratical value of KW required. You can select nearby standard rating in such a way that motor is loaded to 80%.

With regards

D.D.Desai

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 5:55 AM

Dear friend.

There is an almost linear relation between the motor output power and the speedreduction of a motorshaft.

Take a look at the motors nameplate, it gives the RPM at full load.

I expect it to be 2935 RPM (3522 for 60Hz) at a load of 22 kW.

At no load the speed will be 3000 RPM (3600 for 60 Hz).

This means that the motor speed decrease with (3000-2935) / 22 RPM/kW

(ita est 2.95 RPM / kW)

Now let run you motor at the usual applicable load and measure the shaft speed with a tacho meter or stroboscoop.

If you measure 2950 RPM (3540 for 60 Hz) then the difference between 3000 and 2950 gives 50 RPM

So the motor gives 50/2.95 equals to 16.9 kW.

I suppose that you motor is a 2 pole motor. If it has an other pole number, the numbers will change.

Register to Reply
Participant

Join Date: Jan 2008
Posts: 1
#9

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 7:19 AM

dear sir,

15kw motor will fulfill your requirement but it will take 21Amps when loaded.your power factor with 22kw motor is 0.6 but this will improve your power factor to 0.8

Register to Reply
Associate
Jordan - Member - New Member

Join Date: Aug 2007
Location: Saudi Arabia
Posts: 25
#10

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 2:02 PM

I will add a single point may it had been forgetten by others.

very important to descide when you select the motor there is another factor to be considered not only the motor KW , you need it for continuous duty, short duty,intermitten duty.......etc

for example you can't use 20 KW motor of a pump or fan to replace a lift or escalator burned motor with the same KW. it will not work for a long time and will burn

Register to Reply
Power-User

Join Date: Jun 2005
Posts: 394
Good Answers: 1
#11

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/10/2008 2:53 PM

I developed a spreadsheet to estimate power draw based on motor amp draw vs full load amp draw. Using typical full load power factor and efficiency numbers I come up with a power draw estimate of 4.3 kW at 18.5 amps. Actual power being drawn by the mechanical load is more like 2.9 kW (a lightly loaded motor is not very efficient).

Register to Reply
Anonymous Poster
#14

Re: Finding Suitable Size of The Motor By Comparing No-Load and Load Currents

01/11/2008 12:08 PM

If it is a 3 phase Induction Motor,the thumb Rule is....kW of the motor = 1/2 the maximum load current.In your case,10 kW should be quite OK.

Injineri.RC

New Member

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); D.D.DESAI (1); Howetwo (1); jcl (1); JRaef (2); MUKULMAHANT (1); nam70 (2); os708090 (1); PWSlack (1); ramandeep (1); rudy.leurs (1); Sparkstation (2)

Previous in Forum: Old Type 132 kV Disconnector   Next in Forum: kVA Off a Pole-Bolted xfrmr

Advertisement