Quantam III dc drive field troublshoot

01/09/2008 6:56 PM

200 hp Dc motor produced a gnd across are building 480v,after looking at drive the field fuses FS1 FS2 blew on drive this drive has the optional or expaned field board with 20 amp fuses the motor,s field was gnd- to the motor case so it went out for repair My question is should i be looking for a burned field regulator board or something else on the drive it never tripped or blew a armature fuse(main fuse ) thanks for any tips on this guy.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Quantam III dc drive field troublshoot

01/09/2008 8:49 PM

Is this motor critical to your operation? If so, order a spare, install it when it gets there and then send the old one for a look see at the OEM who built it.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Quantam III dc drive field troublshoot

01/09/2008 10:19 PM

Hello Chy2007

Could you give some details re:

  1. Motor make, model, serial#
  2. Motor normal voltage and current, as applied to the field winding
  3. Motor normal voltage and current, as applied to the armature winding
  4. Field controller: Make, Model, serial #

You state: "the motor,s field was gnd- to the motor case", do you mean the field winding was broken down = shorted to the Motor casing/Chassis or frame?

If so, was it caused by rodents, ants, water or other?

It's quite difficult to analyse a fault condition, from thousands of miles away, without the necessary facts, every bit helps.

If you are getting that motor field windings re-wound, I would be doing a very careful test of that Field winding Controller, which I am assuming is an electronic Controller, thus will probably have been damaged.

It always pays to keep a good spare of those Controller parts, cost is very small for good spares, when measured against the machinery being out of commission..

Kind Regards, appreciate your reply with........

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Participant

Join Date: Jan 2008
Posts: 3
#3
In reply to #2

Re: Quantam III dc drive field troublshoot

01/09/2008 10:41 PM

500v arm, and 300 fieldv, thanks for the reply all info i donot have on hand Normally with this drive trouble with the armature has occured and the result is a shorted scr with a few 450amp fuses Ac power is filtered on main

Register to Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#4

Re: Quantam III dc drive field troublshoot

01/09/2008 11:36 PM

Your motor field probably failed first, This will clear your field supply fuses, (FS1-2) It may or may not have damaged the field reg board and power cube. If you can power up drive (no motor connected) and fuses do not clear, your power cube is not shorted.

Next step would be to prove field reg board is working when motor is connected. I do not know the Quantum drive specifically. Basically if you power up drive and have output volts close to 300V it is probably OK.

You need to confirm that your drive is properly set up to safely control the motor. You should not be burning up motors if the drive is set up properly. You should confirm the current limits and overload settings. Also confirm that the motor field volts are at nameplate.

Add cooling blower to motor, and if your motor sits idle confirm your motor field has an "economy" or "reduced output" setting to prevent overheating when not rotating.

There are many possibilities, but it sounds like you are over working the motor, or do not have adequate motor cooling.

Register to Reply
Participant

Join Date: Jan 2008
Posts: 3
#5
In reply to #4

Re: Quantam III dc drive field troublshoot

01/10/2008 4:42 PM

Thanks for the reply Mevel123 when the drive powered back up the field voltage was high around 600v I think after start-up it will regulate to 300 I believe this was the case another time when we lost a scr or 2 spare motor is around 30,000 so i have ben told there won"t be a spare. thanks for your feedback ang sugestions

Register to Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#8
In reply to #5

Re: Quantam III dc drive field troublshoot

01/11/2008 10:10 AM

600V is very high. Please note that SCR's are used in the armature circuit, as well as in some field supplies. They fail due to over current or over heating. Most drives of your size require a blower on the scr assembly- It is important to have adequate cooling on the scr's as well as the motor. With power off you should confirm the fins on the heat sinks are not clogged with dust. Also confirm your drive's power module fan is working.

You need to confirm that the motor field volts are correct with motor connected. It sounds like your model is a current regulating device. This means without motor connected it will go to full DC volts. With a cold field the volts will be less than rated, and after heating up (the motor field) the output volts should settle at rated. Please note that even 50 extra volts on a 300V field is enough to shorten the life of the motor, and you need to confirm the volts after motor field is hot. Good luck

Register to Reply
Anonymous Poster
#6

Re: Quantam III dc drive field troublshoot

01/11/2008 4:18 AM

DC Field are very highly inductive devices, and extremely high inductive overvoltages= L di/dt inductive voltages are developed during switching On , OFF and other normal operations. All DC field windings need to be fitted with permanently connected discargew resistances. These are Voltage dependent resistances VDRs and should have thermal ratings to suit the size of application.Even spark gaps can be fitted in certain installations.In absence of a VDR the Dc field windings can develop interturn shorts .

Subodh Kumar

Register to Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#7
In reply to #6

Re: Quantam III dc drive field troublshoot

01/11/2008 10:00 AM

You are correct, however his DC drive's field regulator has (or should have) similar protection, already built in. Also if the induced voltage caused the input fuses to clear, it would have to of shorted the power cube first, by exceeding it's rated back voltage.
This did not happen. What you say is important if he has been disconnecting the motor field (via switch) with power on, but I am not sure this was the case.

Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Chy2007 (2); Mevel123 (3); North of 60 (1); Sparkstation (1)

Previous in Forum: Motor Overload Protection   Next in Forum: need book on dc ac analog digital
You might be interested in: Fuses, Gate Drive Transformers, PCMCIA Hard Drive Cards

Advertisement