01/12/2008 4:35 AM

1. While designing for Cu. bus bar what de-rating factors should be considered? 2. How Enclosure area effects the derating of busbars ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Derating factors for Cu. busbar

01/12/2008 12:24 PM

Proximaty effect

skin effect

grouping factor

Intial temperature

Final temperature

Purity of copper for electrical work

Enclosure sizing

Ventilation of the room where switch gear is to be loacted

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#2
In reply to #1

Re: Derating factors for Cu. busbar

01/12/2008 2:42 PM

Altitude above sea level (relative air density), emissivity and absorptivity are also factors to be considered.

Reply
Anonymous Poster
#3
In reply to #1

Re: Derating factors for Cu. busbar

11/05/2008 7:49 AM

can you please provide the details for derating factor for cu and aluminium bus for the factors mentioned in the above, otherwise pl mention the weblink for the same.

regards

g.nagarajan