I want know is thier any std or method to design a earth-mat for power house.
IEEE80 it only specific about substation Earthmat design.
is step and touch pot. voltage not required for earhmat design for power house.
This topic has been discussed many times.May be referring to the earlier threads will be helpful.
Refere IS 3043 for LV system earthing design.Step & Touch potential is not predoming for LV system since GPR is much less.
Hi every body,
How far Earth mat if effective designed for corporates interior facilties. The copper electrode earth pits required for neutral terminals of the UPS (Uninterrupted Power Supply) have to be seperate, & for server connected as well