Instrument Earthing Resistance

01/14/2008 5:14 AM

Dear all,

We are doing a project as steam header installation with metering station including PLC panel which is located in island.

We have installed a PLC Panel in the site and made two earthing such as one is Panel earthing and another one is Instrument earthing.For Panel earthing resistance, we achived by less than 10 ohm.

But we could not able to achive the client requirement as less than 1 ohm for Instrumnet earthing resistance.

We already put 6 earth rods (every rod as 2 m length).Still we could not get.

So please suggest me to get the Earth resistance as less than 1 ohm.

Thanks and regards,

karthik.

__________________
Karthik_PE
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Instrument Earthing resistance

01/14/2008 5:32 AM

Irrigate the ground with seawater.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#2

Re: Instrument Earthing Resistance

01/14/2008 12:01 PM
__________________
Innuendo is not Italian for a suppository.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3
In reply to #2

Re: Instrument Earthing Resistance

01/15/2008 3:04 PM

I fully subscribe to most of all said in the thread before me. But specifying 1 Ohm separate ground, as if that would be a solution is bordering on insane. Even if you measure it within spec now, it wont be in the next heatwave, when the ground dries out completely. Nor will it do its duty, when somebody puts in a heavy equipment ground nearby. It maybe even be done for your neighbour you being unaware. Production equipment HAVE to be grounded. Instruments do not (when they use low voltages), or provided ground independent path back to wherever. The equipment is off-the-shelf including converters for sensors and instruments of the preceding generation. As soon as your instrumentation run is independent from the ground bounces of the sensor end you are home free. In the office you reconvert back, and your installation should be invisible.

Convincing the customer is another thing entirely.

Register to Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#4

Re: Instrument Earthing Resistance

01/16/2008 1:05 AM

HI

Increase the number of earth rods such that you will get the resistance less than 1 ohm . The spacing between 2 earth electrodes should be minimum 6M. Also check the earth cable size , make the size a bit larger to achive the desired resistance .

Regards

Dhilju

Register to Reply
Participant

Join Date: Jan 2008
Posts: 4
#5
In reply to #4

Re: Instrument Earthing Resistance

01/20/2008 7:51 PM

Thanks ,We are also following the same.

We have Drived earth rods at 4 places, every places 3-4 Rods were used.

All together we connected and we got 2 ohms.

Because the site condition is like as free sand.

This site is last 3 year back only converted as land before it was sea.

Still we are increasing the no of earthing places and connected to Parallel.I hope we will get less than 1 ohm.

Thanks and regards,
karthik.