Total harmonic distortion

01/16/2008 1:34 AM

Guys,

Is it necessery to install filter harmonic in power line or not?

What is the criteria or maximum accepted harmonic power (The total power to generate harmonic in power system) and safe for our equipement?

Is there any regulation about this issue?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Total harmonic distortion

01/16/2008 6:19 AM

Hi,

You may use the IEEE std 519-1992, IEEE Recommended Practices and Requirements for Harmonic Control in Electrical Power Systems.

Register to Reply
Anonymous Poster
#2

Re: Total harmonic distortion

01/17/2008 12:26 AM

total distotion shall not be more than 5% .

also individual harmonic shall not increase as below:

3rd harmonic ------44% of fundamental

5th ---33%,7th ----18%,9th----7%% 11th----10%

regards

veer

Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#3

Re: Total harmonic distortion

01/17/2008 1:56 AM
__________________
Aged man is not old man...
Register to Reply
Guru
Hobbies - Model Rocketry - New Member

Join Date: Jun 2007
Location: East of Seattle, Washington state Republic of the 50 states of America
Posts: 2045
Good Answers: 36
#4

Re: Total harmonic distortion

01/17/2008 3:08 PM

It is also dependant on the use of the power. An electric heater or lights are less effected than test or computer equipment.

Just a change in perspective

Brad

__________________
(Larrabee's Law) Half of everything you hear in a classroom is crap. Education is figuring out which half is which.
Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 19
#5

Re: Total harmonic distortion

01/20/2008 2:15 PM

Harmonics are generated by switching power supplies;UPS, Inverters, Rectifiers, AC Motor drives, variable frequency drives, electronic ballasts. If you do not have such systems at your site, then you are safe.

the total power do not generate harmonics.

If you are in doubt, use harmonic analyser; single harmonic and total harmonics.

In 3 phase 4 wire supply, neutral get hot due to harmonics.

Register to Reply
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#6
In reply to #5

Re: Total harmonic distortion

01/19/2013 4:41 AM

Dear All

Any equipment to measure harmonic distortion for UPS

REgard

Register to Reply