Coooold in Here

01/23/2008 8:09 AM

I am questioning the placement of over head natural gas heaters in our manufacturing facility. They are 200,000 BTU Modine's. of the five heaters four are mounted as pairs. Two heaters side by side facing opposite directions. Mounted 20' off the work floor.

What I would like to know is wouldn't the intake fan of one disrupt and out flow of the the heated air of the other. Causeing some of heated air to circulate in one out and then back into the other in a continuous cycle. Not allowing efficient heating of the space below.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Coooold in Here

01/23/2008 9:12 AM

From what I've seen of factory heating it is done with no regard for efficiency, functionality, comfort, or, in fact, any other discernable consideration.

If it's any consolation my lab has walls of wafer thin steel sheet, single glazing and a radiator designed to heat the countryside ...

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2
In reply to #1

Re: Coooold in Here

01/23/2008 9:36 AM

Yeah I understand that there is no reason or form for factory heating. But when your about 1 million BTUs under what the square footage says you need, every little bit helps. The building recently purchase was built by Underarmor they had massive clothes driers in the building that supplemented the heat.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#3

Re: Coooold in Here

01/23/2008 10:22 AM

this is a second-hand story, but if they are tubes are they painted black? One fitment wasn't, the suggestion was made, scoffed at, implemented and appreciated.

just in case

Register to Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#4

Re: Coooold in Here

01/23/2008 12:25 PM

The ones I have seen were staggered slightly sideways from eachother. I did not know at the time why but your post makes me wonder if this was exactly for that reason.

When you say that factory heating is not done with much regard for effectiveness or comfort I would like to argue that that way of looking at it should change very soon if not now!

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5
In reply to #4

Re: Coooold in Here

01/23/2008 10:44 PM

hot air blowers need vertical column movers (ceiling fans down) to get good mixing or there will be lot of high heat and cold floors.

__________________
Per Ardua Ad Astra
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Coooold in Here

01/24/2008 12:18 AM

I am in the same opinion, You need ceiling fans to push this hot air down .

Register to Reply
Active Contributor
Hobbies - CNC - New Member

Join Date: Jan 2008
Posts: 19
#7

Re: Coooold in Here

01/24/2008 2:18 AM

Most overhead gas heaters that I have seen have louvered directional vanes on the air discharge side of the heater. Check that the vanes are pointed downwards, and I also suggest the use of ceiling fans to circulate the air, as 20 ft. ceilings will definitely give you a cool floor area.

best of luck :-) Gary

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#8

Re: Coooold in Here

01/24/2008 3:44 AM

How much of that space up there is needed? Wouldn't false ceilings and more modest heaters be a more efficient solution.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#10
In reply to #8

Re: Coooold in Here

01/24/2008 7:19 AM

The ceilings are at 27 feet. There is a good bit of the building that is storage of materials and finished goods. In those areas we utilize that over head space. I did say it was manufacturing not office space. I can see some one taking out the false ceiling with a lift truck.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#9

Re: Coooold in Here

01/24/2008 6:31 AM

You have to consider they are up there from a safety point of view. Also in factory's where floor plans and process are changed around they do not want to have the extra problems of large space heater relocation.

Low mounted heaters might be cozy for the area closest to them but not much use the other side of a partition or some such obstruction. The blowers of aerial heaters should be designed to disperse the hot air over the floor plan as efficiently as possible but as pointed out in previous posts some designs leave a lot to be desired.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Commentator

Join Date: Feb 2007
Location: Nashville, TN
Posts: 61
Good Answers: 4
#11

Re: Coooold in Here

01/24/2008 10:19 AM

This may not be applicable, but I have had very good results heating only the area around the operator station with infrared units. This was in very large buildings with 50 ft ceilings. We heated the space to above freezing and we used the infrared heaters to bring the operator areas to a more comfortable temp.

Register to Reply
Anonymous Poster
#12

Re: Coooold in Here

01/24/2008 10:34 AM

You might concider adding a shield or some metal duct to deflect the air downwards at an angle that wouldn't interfer with work being done on the floor. Myself I would make up something temporarly to make sure it would work the way i wanted and not blow something like paper around (if you use something lite like that) or that it didn't make a worker to warm by causing a warm (Hot) air draft on them. After a trial period I would make up something permenant at was tilted and angled the right way that works best for the building and workers.............Rescue

Register to Reply
Commentator
Hobbies - HAM Radio - New Member

Join Date: May 2005
Posts: 56
#13

Re: Coooold in Here

01/24/2008 11:05 AM

I have mounted large units at the corners and in the middle with downward throws. But for something of this size I put in IR. You have to look at the stacking height of the products and may need to make adjustments to use some heaters as well.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Cleveland, Ohio
Posts: 100
Good Answers: 2
#14

Re: Coooold in Here

01/24/2008 11:37 PM

Yes, heaters mounted side-by-side, facing opposite directions will interfere with airflow slightly. A piece of sheetmetal can we used to divide the 2 heaters.

The main problem you have is the fact that hot air rises. If you were to maintain 68 F at 5' above the floor, the temperature at the ceiling will probably be 85 F. - a huge waste of heat.

If you were to call Modine with the model numbers, they can tell you the throw of the air at any given mounting height. They can also determine the maximum angle of deflection for the louvers before over-amping the motors. If you were to install any ductwork, they can also tell you the minimum size for optimal airflow.

The best heater for your application is probably a low-intensity, tube-type heater. If you are interested, I can put you in touch with a few heater reps. who will design a system that will work.

rich@rgreenwald.com

(For 30 years, when I was a heating contractor, I installed several of these systems)

__________________
THEOILGUY55
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); aurizon (1); case491 (1); davlamb (1); garth (1); HUX (1); messager (1); N5EBA (1); ozzb (2); Randall (1); THEOILGUY55 (1); user-deleted-1105 (1)

Previous in Forum: Electrical Motor Chain Driven Conveyor Output   Next in Forum: Polystyrene or Styrofoam Sheets

Advertisement