Limiting Tension for Conductors and NESC

01/24/2008 12:01 PM

Hey guys. I just ordered the NESC HANDBOOK, 2007. I THOUGHT that it would have tables for limiting tension for conductors(ie, Alton, Peach etc). But all the tables in that book are not in it. Should I have gotten a different book? I looked on the IEEE site and it looks as though there is a version they have, which is what I should have bought.

Anybody have a resource other than the NESC? Or do I got to blow another $100 on this book as well?

TIA

__________________
gisdude
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#1

Re: Limiting Tension for Conductors and NESC

01/24/2008 1:46 PM

I'd Google for the tables you want specifically and that might help you track down the appropriate book for your needs.

Register to Reply
Associate

Join Date: Jun 2007
Location: Sacramento, CA
Posts: 33
#2
In reply to #1

Re: Limiting Tension for Conductors and NESC

01/24/2008 3:00 PM

I tried that. It just takes me to OTHER references of the table. Weird how the tables aren't put up.

__________________
gisdude
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3

Re: Limiting Tension for Conductors and NESC

01/25/2008 10:28 AM

Actually, the NESC does define limiting tension for overhead conductors but it is done indirectly by defining wind and ice loading, sag and swing clearances, safety clearances, structure loading, etc. for various voltages, construction grades and Rules.

Sags and tensions for open supply conductors, for example, is defined in NESC, "Conductor sags shall be such that, under the assumed loading of Rule 251 for the district concerned, the tensions of the conductor shall be not more than 60% of its rated breaking strength. Also the tension at 60° F (15°C), without external load, shall not exceed the following percentages of the conductor rated breaking strength:

Initial unloaded tension 35%

Final unloaded tension 25%"

(And there are exceptions).

By the way, if your NESC "Handbook" is ANSI C2 it's the same as the one on the IEEE site. The NESC is published by the IEEE and is the responsibility of IEEE Accredited Standards Committee C2.

Nothing is ever easy.

Good luck.