230V as grid voltage

02/03/2008 7:38 AM

why do we use 230V or 110V as grid voltage? why can't we use 250V or 210V as grid voltage. what is the reason for choosing 230V or 110V as grid voltage?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: 230V as grid voltage

02/03/2008 11:37 AM

A interesting question. According to some sources Edison's original lightbulb was designed to work with around 100 V DC. It seems like many other standards 110 V AC was selected arbitrarily to match the voltage that Edison was working with.
There may be some validity to this, AC voltage is rated in terms equivalent energy transferred to a heating element (pure resistance). The actual peak voltage of 110 V AC is approximately 155 V (the US standard is actually 120 V the original standard was 110 V changed sometime in the 1950s) .

Many other countries have chosen 220 V as a standard for small appliances and lights. The reason the US is stayed with 120 V AC as a typical plug outlet voltage is probably because it's safer. Voltage does not kill you, the current passing through your body is what kills you. The relationship between voltage current and resistance is represented in the equation I=E/R therefore if you double the voltage the amount of current passing through a given resistance double's, in this case the resistance is represented by your body to the return path of the current, the return path can be phase to phase or phase to ground.

In applications that require a lot of power i.e. energy, large motors, large electrical heating elements etc. higher voltages are used ,a second factor that comes into play here is wire size, briefly any conductor (besides superconductors) has resistance, the more current passed through a given conductor size the hotter the conductor gets. Resistance generally increases with temperature, easy to see that soon you have a meltdown. The only way to decrease resistance is to make the conductor larger. Where the energy demands are large the size of the conductor gets impractically large.

To the point of your question the lowest practical voltage is the safest, where humans can come in contact with it. Most household appliances draw less than 15 amps at 120 V, the current is easily handled by relatively small gauge wire.

Devices devices that require more energy i.e. air-conditioners, electrical heated houses, dryers, typically run off of 220 V. Twice the energy transfer through the same size wire. So my answer would be the voltage was selected arbitrarily, and retained for safety reasons, and that it is practical for most small businesses and residences.

PS. The actual grid voltage for long distance power transmission from power plants to local distribution stations is in the hundreds of thousands of volts.

As far as why we can't use a different voltage the only reason is that the the voltage delivered must match the voltage the equipment was designed to work on. If you exceed a given range either by too high or too low voltage the end device will fail. I.e. supply 110 V lightbulb with 220 V and it will be very bright for a very short period of time.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Good Answer (Score 4)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#6
In reply to #1

Re: 230V as grid voltage

02/04/2008 7:47 AM

RE: the bit about higher voltage being more dangerous because it pushes more current. True if you assume that the breakdown voltage is constant, but it isn't. There are a lot of factors that will determine if a given voltage can establish a current flow through an insulating object. For example, standing on a concrete floor in sneakers in a dry environment and 120Vac probably won't kill you. Try the same stunt in bare feet and you're in for a nasty and possibly fatal shock. Do it with water on the floor and you're morgue meat.

Of course going to 240Vac makes the problem worse. At 480Vac you're pretty much in the hospital at best. That's why US code specifies rubber mats under breaker boxes with 480Vac.

__________________
Eric
Register to Reply
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#17
In reply to #6

Re: 230V as grid voltage

02/05/2008 12:31 AM

Hello ca1ic0cat:

You're absolutely right. In fact it has been dramatically demonstrated with the advent of repairing high tension lines while they're still hot! A tinfoil suit, a helicopter, and a lightning rod and your business. Just don't get near anything that'll complete the circuit.

PS goofed again forgot to market off topic before I post.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Score 1 for Off Topic
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#13
In reply to #1

Re: 230V as grid voltage

02/04/2008 1:28 PM

Regarding the 110 Volt and 220 originals, you may wish to look at a previous thread ("Voltage multiples of 11"). Essentially, when the change to AC was started, the early power companies modified the meters using rectifiers, and chose used consistent values for the readings to minimise operator errors.

The basic theory is as follows:
DC values included 100 and 200 Volts. As the rectified value of a sine wave is 0.6366 of its peak, and the RMS value is 0.7071 of its peak, that meant that you need to increase the RMS Voltages to (0.7071/0.6336) x the original DC Voltages, or by a factor of 11%.

This survives pretty-much unchanged in the HV distribution system. For the consumer system, I believe that at some point it became possible to tighten the control tolerances; that allowed transmission systems and user equipments that had been designed for 110 and 220 Volt wide-tolerance operation to be used safely with higher nominal supply Voltages. The higher nominal working Voltages were adopted because they allowed the existing wiring to deliver more power.

Confused? I've barely started.

Fyz

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#14
In reply to #13

Re: 230V as grid voltage

02/04/2008 5:36 PM

"As the rectified value of a sine wave is 0.6366 of its peak"

Perhaps there's a word (or two) missing there?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#22
In reply to #14

Re: 230V as grid voltage

02/05/2008 9:40 AM

Corrrect, I should have written "full-wave rectified".

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#25
In reply to #22

Re: 230V as grid voltage

02/05/2008 10:47 AM

... but do you mean the time-averaged value? Sorry to be picky, but you stated "rectified value of a sine wave ...". Giving a value for RMS is fine, as it's implicit (reader either knows it, or can easily look it up).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#26
In reply to #25

Re: 230V as grid voltage

02/05/2008 11:03 AM

Yes, I was assuming the basic performance of electro-mechanical meters, which is all that would have been available at the time. So the meter in question is linear in its current (or Voltage) response, and averages this AC input (as its fundamental frequency is 100-Hz or 120-Hz).
N.B. the other available instrument would have been a square-law type such as a moving-iron meter, but if these had been used by linesmen you wouldn't have used rectification in the first instance.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#15
In reply to #13

Re: 230V as grid voltage

02/04/2008 11:22 PM

Confuse definitely. As soon as I get a chance I'm going to look at the thread that you suggested. Rectified value has me somewhat confused. If my memory has not totally failed yet I did a demonstration for a class sometime ago. First I measured the outlet voltage with a standard DMM. Next I connected a capacitor to the outlet using diodes to convert to DC, then measured the DC charge on the capacitor and it was in agreement with multiplying the measured AC voltage by the square root of two. Of course this would be expected as that is basically how a standard DMM works. To me this would suggest that the .707 would be the rectified value. I've never tried the experiment with a true RMS meter but I would not expect any difference, as I should have had a virtually uncorrupted sine wave. So I may be missing something here but I can't quite see where the other value comes from.

PS. Having gone out on a limb here as I don't have the diodes to repeat the experiment tonight, I'll pick up some tomorrow just to see if I am wrong, and repeat the experiment using a true RMS meter.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#23
In reply to #15

Re: 230V as grid voltage

02/05/2008 9:48 AM

If you have a capacitor, you are peak detecting; this would not have been used because it would have been so sensitive to switching pulses, etc.
However, I should have written "full-wave rectified".

I wouldn't wish to use a meter that relies on peak detection for AC measurements. Even the old Avometers used something approximating full-wave rectification, but with the resistor used for AC modified from the DC value to improve the approximation. Modern electronic meters should give true RMS - though there may be issues due to limited sampling frequency with some waveforms

Register to Reply
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#28
In reply to #23

Re: 230V as grid voltage

02/06/2008 12:03 AM

Hello physicist:

And I thought this was going to be a short thread. A lot of interesting topics have been covered here, from warship electrical to the first meters. You seem to have some insight into the original meters. I did a brief search to find out when the first diode tubes came into service ,seems to be circa 1904, with the cat whisker diode appearing sometime in the 1920s. So my question is where these first rectified meters using tubes, and how portable where they ?

A brief comment and question on DMM's. As far as modern electronic meters measuring true RMS they certainly are available as well as standard meters. My experience with my true RMS fieldpiece has shown it to be a little touchy. I have checked power input to machine that was not running and had a unusually high voltage reading that was fluctuated considerably. There were three other large machines utilizing VFD's that I'm sure were fed off the same transform. I observed approximately a 40 V difference between the standard meter and the true RMS, both readings were within tolerance for my equipment , I tend to believe the standard meter in this case. So the question, is the limited sampling that you were referring to in your post related to my flaky readings?

Many times in the past I have been led on a wild goose chase by overly sensitive DMM's only to have the problem solved with a simple wiggy. I am leery of toolbelt true RMS meters for reading voltage other than output voltage from a VFD or similar device (or at least when other equipment generating non-sinusoidal waveforms is on the same panel). So if you or anyone has an opinion on my phantom voltage readings I'm certainly interested, as I said this was a nonissue as I was within limits, I can't imagine the RMS meters reading being correct,but I could be wrong.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#30
In reply to #28

Re: 230V as grid voltage

02/06/2008 5:25 AM

The problems are often the electronic controls of motors putting large spikes back on the mains, a good scope will let you see some but not all of them - simply too fast, unless you have some sort of storage scope.

There are special units made to monitor voltage spikes on the mains, such a unit is a better bet.

I bet you will see a lot of extra noise from VFDs and the like and your sensitive meter is trying to compensate and give an accurate reading......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#32
In reply to #30

Re: 230V as grid voltage

02/07/2008 8:36 AM

Hello Andy: I'm beginning to think Edison was right, I suppose it's too late to convert to DC. Sooner or later I'm going to run into one of these flaky voltage readings that are outside of my tolerance range and I'll have to figure out which one is right. Like you I figured the voltage difference was generated by the other VFD's, I think it was more of a "signal" than a usable voltage, or least I hope so. There were plenty of other motors running not driven off VFD's that I assumed would have filtered out any noise, thinking back on it all the motors were three phase hence nothing would return on a neutral to a common earth ground , maybe I had a big antenna.

BTW: you're not in an exclusive club. I've gotten hit a couple of times by either 277 V or across both legs and got the full 480, it hurts! A learning experience never trust a electrician to know what line and load means in a fusible disconnect, I now teach anybody I am training look or put a meter on IT before you grab a fuse.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#33
In reply to #32

Re: 230V as grid voltage

02/07/2008 8:57 AM

Modern meters (DMMs etc) have such a high impedance, it's very easy to be fooled into thinking there's something there, when it's just the local FM station.

If I get a suspicious reading, I generally look for a resistor (with the lowest value I can get away with, commensurate with its power rating and the volts I think I may have, so it won't glow if there's really some power there), and very carefully clip it across the connections, then measure again. It usually goes away.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#35
In reply to #33

Re: 230V as grid voltage

02/08/2008 5:17 AM

Try one of those relatively new contactless testers, they beep and light up when the are near to a cable with mains on......really good!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#36
In reply to #35

Re: 230V as grid voltage

02/08/2008 5:26 AM

But can they tell the difference between 'real' mains & pickup?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#37
In reply to #36

Re: 230V as grid voltage

02/08/2008 9:34 AM

Absolutely, but do not ask me how!!! I am really impressed with them.

Another one of them I use (a bit older by 5 years of so) is also a screwdriver. This one you put only the tip on the wire and hold it by the sides, it will indicate if voltages are present above 50 volts AC or DC. If there is nothing indicated, you touch the opposite end to the screwdriver and if it then lights, you have a voltage between 5 and 75 volts. It beeps too at the same time the led lights!!! Needs a battery as do most of these modern devices.....

Just holding the screwdriver bit near to the door seal of a microwave oven, without touching the other tip, will show leaks of microwave energy if there are any......

You can test fuses with it, in fact there are many uses for the Multi tester.

(the others are just AC voltage testers, some from 12 volt upwards. One is not suitable for the USA as it tests only above 200VAC....)

Multi Tester

Contactless Voltage Proofer 1

Contactless Voltage Proofer 2

Contactless Voltage Proofer 3

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#38
In reply to #35

Re: 230V as grid voltage

02/08/2008 11:47 AM

I think they use physically small capacitive sensors - so are only sensitive to the electric potential (the part that hurts you directly). Regarding earlier Edisonian comments - can they sense DC** as well?

**Which would also be sensitive to sampling of impulse noise - but much easier to filter, of course.

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#39
In reply to #38

Re: 230V as grid voltage

02/09/2008 3:46 AM

You wrote:-

**Which would also be sensitive to sampling of impulse noise - but much easier to filter, of course.

Yes but it would only causes short pulses of irregular timing and size, whereas mains causes the LED to light and the beeper to beep continuously as long as you are close to the source!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#34
In reply to #32

Re: 230V as grid voltage

02/08/2008 5:15 AM

I follow your line of thinking completely.

With regard to the meter testing, its a good starting point as long as you know that you have a return path to measure against.

I prefer those modern plastic testers that you hold in your hand, that only need to go near to a live connection and they light up and beep!! No contact needed!!

But probably the best way is to use both, meter first, tester second!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#31
In reply to #28

Re: 230V as grid voltage

02/06/2008 6:09 AM

When I know nothing about the source, the only measurement device I truly trust is a combined resistor and temperature sensor. Any reasonably-designed meter would be adequate for standard power systems; unfortunately, not all available meters satisfy the basic requirements**.

Regarding rectification, I believe you are correct in your statements. Prior to that, commutating rectifiers (rotating or vibrating) could have been used. I saw some of the former when I was involved in standards work, but it was only in passing, and unfortunately I cannot remember anything about dates. [These units were said to be less sensitive to temperature, orientation and movement than moving iron meters]

**The signal should be very well filtered before being sampled (the sampling rate being in excess of twice the frequency at which the filter response drops to a negligible level). I'm not involved in the field these days, but for high performance 50/60 Hz meters, I would expect a 3-dB bandwidth of 1-kHz or more, and attenuation to at least -70dB from half the sampling frequency. Perhaps one of the electrical-engineering fraternity could comment?
BTW, some meters that nominally meet this requirement may be susceptible to electro-magnetic interference. Caveat emptor

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: 230V as grid voltage

02/03/2008 11:48 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#3
In reply to #2

Re: 230V as grid voltage

02/03/2008 11:56 AM

Hello John
That's cheating, however I wish I would've thought of that it would've saved me a lot of typing.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: 230V as grid voltage

02/03/2008 12:06 PM

Cheating, maybe, but hell - you spelt it out really clearly - brownie point awarded!

(Edit: I seem to have done the same as you - assuming you gave yourself an "off topic". I pulled myself down 1 vote, but once you've submitted, you need 4 collaborators to help pull it fully OT!)

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Off Topic
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#5

Re: 230V as grid voltage

02/04/2008 3:13 AM

What Wiki doesn't mention is why 230V is the mains voltage. Of course this is the single phase voltage, while the real power is delivered at 3-phase. Keeping in mind the higher the voltage the better, the limit was the VIR (vulcanised india rubber) insulation used on cables at the time.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 12
#18
In reply to #5

Re: 230V as grid voltage

02/05/2008 3:52 AM

Hi BabyGuinness - can you give your comments on my post - Single core or three core cable.

I would like to your expert comments on the following:

1) If there is a single core cable and another 3-core cable both of same size, say 150 sq,mm - Can I use these interchangeably in my power connections as incomers to say a load.

The current rating given for a single core cable of 150 sq.mm from supplier catalog is 389 Amps and for that of 3 core 150 sq.mm is 272 Amps.

{I was told by someone today that the current carried by a three core cable is 272 x3 = 816 Amps. So I am now confused. }

When I sized the cable for a 3ph load say motor, I used kW/(1.732 x 440 x p.f x Eff) to get the Full load current. Then divide this by the current the cable can carry (let us ignore the cable de-rating in this question to keep it simple.)

For example if my FLC is 1500 amps and if I use 3c 150sqmm, then i require (1500 /272 = 5.51) 5.51runs, which is 6 runs. Here I will terminate first core of all the 6 runs in Red phase, second core of all 6 runs in Yellow phase and third core of all 6 runs in Blue phase.

But if I use 1c 150sq.mm, then I will use (1500/389 = 3.85) 3.85 runs or 4 runs. But in this case I will go 6 runs as well as I have three terminals (Red, Yel, Blue) to terminate. Am I doing things correctly?

{I was told by someone today that the current carried by a three core cable is 272 x3 = 816 Amps. So I am now confused. }

Need your help

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#20
In reply to #18

Re: 230V as grid voltage

02/05/2008 4:43 AM

The reason the current rating per core is lower for the multi-core cable is the proximity of the conductors.

If you had 3 individual cores of the same cross-sectional area (CSA) as the 3-core conductors, and packed them tightly together (as per wrapping them in an outer sheath!) you would have to de-rate them so you ended up with the same rating as the 3-core.

The current rating is generally quoted for the whole cable, fully loaded, but on its own in free air. As soon as you go running 2 or more (single- or multi-cores) together, you have to de-rate.

You don't get owt for nowt.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#21
In reply to #20

Re: 230V as grid voltage

02/05/2008 9:37 AM

Base cable rating is for free air installation, and then there are "de-ratings' for installation in conduit, underground, wrapped with other phases, etc. etc.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Anonymous Poster
#27
In reply to #20

Re: 230V as grid voltage

02/05/2008 7:03 PM

Hi John,

Thank you. So what is the criteria for going for one 3 core or 3 single core cables apart from cost.

Thank u

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#29
In reply to #27

Re: 230V as grid voltage

02/06/2008 3:37 AM

This isn't the place for going into all the ins & outs of de-rating.

Refer to our local wiring regulations (you don't say where you're from - the IEE publish the "regs" applicable in the UK and many other countries - tho' I understand this is being merged (harmonized?) with something more Europe-wide ).

Your company should have a copy of whatever regs apply. It contains extensive tables for cable rating and de-rating, depending on cable construction etc., and factors such as those mentioned by Ried in post #21.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#40
In reply to #18

Re: 230V as grid voltage

02/15/2008 11:08 PM

The info given by "someone" to you is wrong, it will not be 272 X 3 for 3core cable.

It will be 272 only ( i.e per phase).

Hope this helps.

Good luck.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#41
In reply to #40

Re: 230V as grid voltage

02/16/2008 3:43 AM

Thanks - I should have stated explicitly in my #20:

"The current rating is generally quoted for the whole cable, fully loaded, but on its own in free air" - and it is quoted as the current per phase, i.e. per core.

John.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Oct 2007
Location: NW Ohio
Posts: 411
Good Answers: 25
#7

Re: 230V as grid voltage

02/04/2008 8:14 AM

Funny how battery powered hand tools keep upping the voltage. What will be the limiting factor?

__________________
Goodness has nothing to do with it.
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#8

Re: 230V as grid voltage

02/04/2008 8:29 AM

I've often wondered about this convention as well; although they are all nominal. In the US, house wiring is normally called 220/110, or 230/115, or 240/120. They're all the same. What is screwy, it that in the US Navy, the power and lighting system is 450/117, the lower voltage used for receptacles and lights. Why 117 you ask........I have no idea. I know you could order transformers in the stock system that were 450/117 or 440/115. Maybe having an ungrounded 3-phase system has something to do with it. Each phase to ground reads about 55-60 volts to the hull, depending on where on the ship you take your measurement.

__________________
Eschew obfuscation.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #8

Re: 230V as grid voltage

02/04/2008 9:51 AM

That is the NATO standard since the 50's for NATO warships..... nothing more nothing less. You need to talk to the NATO designers of yesteryear to find more infos.....

Having 3 phase with no ground (the warship IS ground) and no neutral saves a lot of weight of the extra cables, but needs star/delta transformers to get the 117volts for domestics and lighting!!! They are heavier, but not as heavy in total as a neutral would have been.

This also means that generator phase to phase loading is always equal (except maybe if a fault occurs of course!) and no excessive neutral currents either all on one cable!!!

All major motors for pumps etc. are 3 phase and as such do not need a neutral anyway.....

I got hit once by 440 AV 60Hz, its a real killer, I made sure NEVER to repeat the experience!!! R-Y-B are also the color of the stars I saw!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#10
In reply to #9

Re: 230V as grid voltage

02/04/2008 10:14 AM

USN ships use delta-delta step down transformers for lighting and receptacles. The only place a wye connection is used is on carriers and amphibs in their avionics spaces for testing. However, back in the 80s when I was redesigning sub-tender galleys to install "Burger King" type equiipment, we had to buy 450/220-110 delta-wye transformers to meet the power requirement.

__________________
Eschew obfuscation.
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#12
In reply to #10

Re: 230V as grid voltage

02/04/2008 12:03 PM

To add to my comment about the delta-delta transformers, load centers used three single-phase transformers connected delta-delta primary and secondary to form a bank. Single phase transformers are used so that one can be removed due to battle damage and still enable to bank to provide 58% power.

__________________
Eschew obfuscation.
Register to Reply
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#16
In reply to #12

Re: 230V as grid voltage

02/04/2008 11:57 PM

Hello kyoto:

I'm just curious here, were you using the same panel (or transformer bank) to supply both three-phase and single phase 117 V AC power throughout parts of the ship? The reason I'm asking is the open Delta you're referring to (using two transformers to replace three after battle damage) has a Stinger leg, no problems phase to phase but certainly a lot hotter phase the neutral. Just curious, I would sure hate trying to figure out what breakers were on the Stinger while somebody was shooting at me, heck it's hard enough for some electricians to do it without anybody shooting at them.

PS. If I'm reading Andy's post right you are using a separate transformer to get to 117 V, thus doing away with the neutral and the potential Stinger. So I may have answered my own question.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#11
In reply to #9

Re: 230V as grid voltage

02/04/2008 11:13 AM

This is a bit like CTA transit system grounding for elevated stations. Trains run 600VDC nominal voltage, with rails being the DC negaive return concuctor. Therefore they (try to ) electrically isolate the support structure from earth ground. Which means that passenger station power is also isolated from earth ground. the station power comes in from the utility through an ungrounded Wye-Wye isolation transformer, and everything is grounded to station structure instead of earth ground. Secondary transformers for 120VAC power are wye/delta similar to what takes place on the "NATO" standard ship power.

This is a very timely post, as I am trying to understand the differences and similarities between US National Electrical Code grounding conventions and the UK IEE earthing conventions. Thanks to the intelligent responders to this post for history and technical background.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19

Re: 230V as grid voltage

02/05/2008 4:23 AM

If I remember what I was taught in Physics many years ago, the AC voltage that we read on a meter is the "equivalent" voltage in DC that would allow the same amount of "work" to be done.

No more no less.

In this case, the same amount of "work" could be of a purely resistive heater in say boiling a fixed amount of water from a fixed cold temperature.....

A DC voltage of say 120Volts should take exactly the same time as say an AC voltage of 120 volts as read on a meter.

As someone else already pointed out, the "peak" voltage of the AC if measured on say an Oscilloscope, would be significantly higher than the meter reading......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#24
In reply to #19

Re: 230V as grid voltage

02/05/2008 9:57 AM

True of modern meters; intermediate meters (e.g. "AVOs") made corrections that gave the correct RMS value for AC provided that the signal was sinusoidal. But at the time that the initial values were created, linesmens' meters were as simple as possible; I'm not certain whether this was mainly for reasons of reliability, or to avoid the risk of taking readings with incorrect settings. (Even I'm not old enough to have experienced this directly).

Register to Reply
Register to Reply 41 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (7); Anonymous Poster (1); BabyGuinness (1); beriberi (1); ca1ic0cat (1); chaterpilar (1); JohnDG (9); Kyoto (3); Physicist? (7); Ried (2); v_srini (1); YWROADRUNNER (7)

Previous in Forum: Synchronising Panels for Perkins 2806   Next in Forum: CAPACITOR SIZES FOR CAP-START and/or RUN MOTORS

Advertisement