What is voltage drop in cable sizing, causes, effects and applications
Re: Electrical
02/04/2008 4:24 AM
Good Answers: 42
Re: Electrical
02/05/2008 2:51 PM
Your question is not clear. If you really want to have a discussion and proper advice please ask a proper query. Please take a little time and energy to put the query properly and also read the answers and give feed back, after receiving the answers.
Any load carrying cable will have an IR drop . So IR drop is to be calculated, depending on the distance of the load from the source and size of cable. The effect of IR drop is getting reduced voltage at the load centre. Heating of the cable will depend on load current carried by the cable. (I²R) So proper size of the cable is to be used depending on the resistance of the cable.(Cross sectional area and length of cable)The size of the cable will decide the permissible voltage drop . So depending up on the permissible voltage drop and current rating and temperature rise the cable size should be selected