Question On MCCB Tripping

02/04/2008 4:08 AM

I AM A panel manufacturer aand i supplied a distribution panel with 250A mccb AS incomer.... this [anel is fed from 250A MCCB from the electrical room....my client called me with the complaint that the 250a mccb in the electrical room is tripping frequently but the incomer mccb of my panel is never tripping.... so i went to the site and checked the site.... i found each phase in my panel takes 120A, 128A and 135A at a particular instant........my client consultant says that my panel is overloaded .... he says that as my panel is taking around 120a in each phase ..... the total 3 phase current is around 360a... 120+128+135 =383a.... and his breaker capacity is only 250a........ he says this is the reson why his mccb in the electrical room is tripping.........and all the mccbs used are 3 pole 36ka....... as far as i know each pole of a 250a mccb can draw 250a maximum .. so all the threee poles can take 250 each..........if i am correct what should be the evidence i should give to prove my point

Register to Reply
Pathfinder Tags: MCCB
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Question On MCCB Tripping

02/04/2008 9:07 AM

OK

  1. how about starting with a clip-on ammeter on each phase, to see what is really going on?
  2. Or how about installing current transformers and a power cube on the inlet to this panel so that the incoming current can be monitored?
  3. How about looking for other systems tied on to the upstream breaker that the Client hasn't mentioned?
  4. In an environement where there is no discrimination, why does it matter which breaker trips, so long as one of them does?
  5. If both breakers are the same rating, why are two of them needed?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 18
#2

Re: Question On MCCB Tripping

02/04/2008 11:14 PM

You are correct as MCB in each phase can draw 250 amps load. You can just replace MCB in electric room from where you have taken power and show it to consultant there would not be any tripping.

The caus of tripping in MCB at electric room could be different and it has so many reasons one is that is has dust accumalated inside and second its thermal O/L charaectristic is having problem. So simply you can replace it and charge cost from client.

C.S. PANT

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Question On MCCB Tripping

02/04/2008 11:57 PM

"my client consultant says that my panel is overloaded .... he says that as my panel is taking around 120a in each phase ..... the total 3 phase current is around 360a... 120+128+135 =383a.... and his breaker capacity is only 250a........ he says this is the reson why his mccb in the electrical room is tripping........."

Wow!

Your client has completely wasted his money if he paid for that consultant! That is something that a complete novice (or Mechanical Engineer) would say, not an Electrical Engineer.

You are absolutely correct; a 250A circuit breaker means that EACH POLE can take 250A. He is a moron. In reality though, if you are in the US you can only legally load that MCCB to 80% of that rating, but that is still 200A; far more than your measured load. Where does it say that? Well, in ANY Electrical Engineering text that is describing circuit breakers!

Here are more reasonable things to check:

  1. What is the load profile? Is it motor starters and do they start Across-the-Line (DOL)? If so, what is the Instantaneous (Magnetic) Trip setting of each of those MCCBs? If they are not adjustable, it could very well be that the upstream MCCB has a lower factory setting than yours, so it is tripping on starting current.
  2. What is the history on that upstream MCCB? If it is old and has tripped many times before, it can build up what is called a "thermal memory" and will trip easier and easier every time until such time as you can no longer get it to hold in at all.
  3. Are you sure the cables going from the upstream MCCB to your panel have been properly checked out? If so, what method did they use? If it was not a megger (which charges the circuit to 500 or 1000VDC and measures leakage to ground over time), then the testing may have not picked up damaged insulation or a bad connection somewhere. A quality electrical installer would have kept testing records after the initial installation.
  4. Does the upstream MCCB have ground fault (earth leakage) protection built-in whereas yours does not? If so, does it use the Residual Current sensing method? That 12% current imbalance you indicated may be causing it to trip if it is set lower than that, regardless of what the thermal trip setting is.

There are a lot of things it could be, but for sure one thing it is not is a 383 Amp overload!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#4
In reply to #3

Re: Question On MCCB Tripping

02/05/2008 6:17 AM

Dear all

This issue has been raised because India doesn't have and doesn't Believe in PE Concept any one can practice any branch of engineering as a consultant with out formal engineering qualifications .still Out Dated BS standards are referred hardly IEC or IEEE standards are referred for design existing Indian standards are based on good old British standards which Briton itself has discarded.you would be surprised switch Gare's manufactured for cu Cables are modified for AL cables by adding an extension box at site and installed

crm

__________________
Run silent run deep
Register to Reply
Participant

Join Date: Feb 2008
Posts: 3
#5
In reply to #3

Re: Question On MCCB Tripping

02/05/2008 9:25 AM

THANKS FOR THE ANSWER ....

1) the load used is heaters and heat exchangers... and there are some 2hp motors with some light load....... about the trip setting ,i ve also asked the consultant to check the same ....as the electrical room was locked at the time of my inspection i was not able to see the type of breaker............. but he is still clinging upon the fact that the total current in the 3 PHASE MCB calculation is sum of all the 3 phases.... i was really stunned to hear that.... and that too from a well know consultant in uae "DRAKE AND SKULL" the guy is not an indian but soemwhere from egypt or lebenon....

2)the mccb is not an old one .. and it jhas jus recently developed the habbit of tripping

3)i havent yet checke dthe cables

4)i ll check if there is any ELR connected to the upsteram MCCB


THANKS A LOT FOR THE RESPONSE

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#8
In reply to #5

Re: Question On MCCB Tripping

02/05/2008 10:01 PM

In that case first find out what make of MCCB ,Model,type contact Manufacturers application manual if possible ask for tripping character curve from manufacturer which would help you in trouble shooting and then you can confront the consultant and save your skin.Thats what i do here in India you need to maintain data base on all components you use in your product.most of the information is available on web sites of component manufacturer like ABB,GE etc.good luck

crm

__________________
Run silent run deep
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6
In reply to #3

Re: Question On MCCB Tripping

02/05/2008 9:31 AM

"That is something that a complete novice (or Mechanical Engineer) would say"

HEY!!! I resemble that remark!!! If it weren't for mechanical engineers, EEs would have nothing to do (or laugh at).

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#7
In reply to #6

Re: Question On MCCB Tripping

02/05/2008 9:35 AM

By the way, I did want to add that just because the breakers are "identical ratings" it does not mean that they will trip identically (even if they were manufactured side by side).

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Participant

Join Date: Dec 2010
Posts: 1
#9

Re: Question On MCCB Tripping

12/14/2010 10:59 AM

can i know rated current of motor as this is a major reason for overload.To protect the motor against any overloads it is necessary to adjust L function of your circuit breaker to a current higher than or equal to the rated current of motor i.e I1 ≥ Ie.

Adjust this L function of your breaker, i think the motor overload problem will get solved,

This is Pawan Jha

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

C.S.PANT (1); crm (2); JRaef (1); pawan113bch (1); PWSlack (1); Ried (2); vipinonline (1)