Auto Changeover Schemes

02/05/2008 3:50 AM

In 2 incomer (ON) & 1 buscoupler (Off ) scheme , during auto changeover there will be first a break in the system and then the buscoupler will be closed. I want to know if motor feeders get affected due to this break????

Also , we are having a captive power plant , the system is paralleled at source end that is we get supply from the common bus , then why at distribution ends (11 kv) the paralleling is not allowed.also, in manual changeover the system is momentary paralleled.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Auto Changeover Schemes

02/05/2008 8:35 AM

<...In 2 incomer (ON) & 1 buscoupler (Off ) scheme , during auto changeover there will be first a break in the system and then the buscoupler will be closed. I want to know if motor feeders get affected due to this break????...>

It depends. If the relays in each starter cubicle remain with their contacts closed during the changeover, then there's a good chance that the motors will see only a brief interruption to the 3Φ supply and continue running, depending on what they are turning. If the contacts open, then those affected will require re-starting.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Auto Changeover Schemes

02/05/2008 8:52 AM

If you are asking whether or not the motor control circuit will drop out, that depends upon where its control power comes from. If your control power comes from the 3 phase mains that are being switched, then yes, your control system will drop out and the motor will need to be restarted by what ever method was used to start it originally.

I have used a UPS in the past to power the control circuits of a motor that I want to keep "energized" during a swing of 3 phase sources. Works ok as long as the load on the motor can handle the drop in torque from the motor during the loss of 3 phase power, a fan comes to mind as a suitable load for such a setup, and in fact it was a couple of large ventilation units I did this on in a food plant.

Also... of paramount importance is verification of proper phasing to ensure correct motor shaft rotation!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: Auto Changeover Schemes

02/05/2008 10:39 AM

Paralleling at the load end is prohibited to protect your equipment, not the utility's. A fault on the line would pass fault current through your service until both lines were deenergized. The fault current on the 11KV feeders can be well above the short circuit capacity of your service equipment. The paralleled incomers will also prevent the proper operation of any automated restoration. If a fault occurs, the supply breaker at the bus will trip. If the feeders are paralleled at the distribution end, the control system will see that the line is still energized, and assume the breaker failed to fully open. It will then automatically trip the next upstream protective device, deenergizing the entire bus.

For my customers who desire a closed transition for return to normal, I have a set of line switches installed between their incomers (in parallel with the buscoupler). When they want to transfer, I close the line switches. If a line fault occurs, most of the short circuit current passes through my switches instead of the customer's service equipment.

Once the transfer is complete, the line switches are opened to separate the incoming feeders.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Participant

Join Date: Jan 2007
Posts: 1
#4

Re: Auto Changeover Schemes

02/07/2008 12:28 PM

Motor feeders shall require manual intervention to start again since bus voltage shall go dead momentarily during change over. You can consider providing reaccelaration feature facility on feeders which are critical and require start without manual intervention. Auto reaccleration feature requires hardware of timer or alternatively through numerical relay if provided in feeder. In case large number of feeders are to be provided with reacceleration feature then group starting of motors is to be considered.

Reply
Member

Join Date: Jan 2019
Posts: 9
#5

Re: Auto Changeover Schemes

01/18/2019 6:20 AM

To know about auto changeover scheme working please go through below link

https://electengmaterials.wordpress.com/2019/01/17/auto-changeover-scheme/

Thanks & Regards

Reply Off Topic (Score 5)
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

k k bhatia (1); North of 60 (1); Phanibabu (1); pwr2thepeople (1); PWSlack (1)

Previous in Forum: electric arc furnace   Next in Forum: Finding a Single-Phase Motor to Use Instead of 3ph Motor
You might be interested in: Stock and Strip Feeders, Solids Feeders, Parts Feeders

Advertisement