Should We Use In or Iz if Changing the Core Size of Cable

02/14/2008 5:12 AM

Hi,

We are buying a generator for one of our projects. It is feeding a 690V, 50Hz, 3phase generator of 2600kWe.

The recommended cable size given by the supplier from the generator to the 690V switchboard is 7 x 3 x 1 core x 240sq.mm

Also we are given the In (nominal current) as 2806A and the cable current carrying capacity as 3430A.

Now if I want to use a different sized cable, say 120 sq.mm or 300 sq.mm, I presume that I de-rate these cables(that is 120 sq.mm or 300 sqmm, depending on which I choose) and use the de-rated current to come up with the number of runs.

For example if the derated current for for 120 sq.mm is 254A (before de-rating 319A), then should I use 3430/254 = 13.89 (that is14) runs instead of 7 runs ?

OR

should I use 2806/254 = 11.05 (that is 12) runs instead of 7 runs?.

As "In" should be less than or equal to "Iz" ( that is the current carrying capacity of the cable), I think it is sufficient to use 12 runs.

So my recommendation if we use 120 sq.mm is 12 x 3 x 1 x 120 sqmm.

Am I right?

Thank you in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Jan 2008
Location: Bath, UK
Posts: 53
Good Answers: 2
#1

Re: Should We Use In or Iz if Changing the Core Size of Cable

02/15/2008 8:06 AM

If you take your max. current divided by your derated value you already have your safety factor, so as you say: 2806/254= 11.05, especially if you use 12 runs.

However you must check the current rating environment, is it the same spec for each cable? Usually two cables with the same cross section as a single cable together will carry more current between them compared to the larger cable. They have a bigger surface area which is important to capacity & cooling.

Some cables may have special instructions for multiple parallel runs in trunking, check with the supplier / manufacturer.

On the information supplied 12 runs sounds fine, however look at the protection of each cable / run.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Should We Use In or Iz if Changing the Core Size of Cable

02/15/2008 9:28 AM

Hi JohnBob,

I guess you are referring to the SKIN effect when you say that cables with more surface area carry more current for a given cross section.

What is the reason you think cables are only made in circular shape?

Register to Reply
Associate

Join Date: Jan 2008
Location: Bath, UK
Posts: 53
Good Answers: 2
#3
In reply to #2

Re: Should We Use In or Iz if Changing the Core Size of Cable

02/15/2008 12:41 PM

Well actually they are not just made with a circular cross-section, we have worked with some 3 phase [aluminium conductor, underground armoured] cables where the conductors are made up of 3 x 1/3 circle quadrants [packed into a 'circle']

I am no cable specialist, but at an exhibition a cable manufacturer was telling me of lightweight cables with a hollow centre [a tube effectively] the centre being taken out as it has a lower power carrying capacity / density. Also the hollow centre helps with cooling so they have a high capacity for the weight.

One answer; from a mechanical viewpoint going round corners with a square cable would be difficult! & cause stress if twisted & cut through the insulation. [well true ]

Seriously - a square cable would have a flux density at the corners I guess, producing heat and so increasing losses, but please educate me! thank you.

Register to Reply
Anonymous Poster
#4

Re: Should We Use In or Iz if Changing the Core Size of Cable

02/19/2008 1:38 PM

omg, in case you weren't paying attention, the 2806A was listed as the Nominal Current. This means that 2806A is the current that it runs at in normal condition and is NOT the Maximum current. I personally would not try to derate down to such a smaller cable. you are going to come into line loss and possibly heating issues because of going from such a large conductor down to a smaller conductor. however, if you must do so for physical cable flexibility or availability issues, I would use the 3430A rating number to determine the number of conductors/cables you need to use. also, with multible conductors you are going to come across more problems with emf radiation or interference (ie. harmonics). just some things to consider. I would call the equipment(generator) manufacture and talk to their engineers before changing the cable size because there is a chance it could mess with the governor.

V

Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 24
#5
In reply to #4

Re: Should We Use In or Iz if Changing the Core Size of Cable

02/20/2008 6:47 PM

Hi V & JohnBob,

Thanks for joining this discussion.

JohnBob - the hollow cable sounded interesting. I hope some more cable experts can add their reasons as well in this discussion.

V- The generator supplier also supplies the main switchboard to which the generator is connected and so the incoming circuit breaker in the switchboard is sized by him. So when they give us the nominal current, I presume that the circuit breaker will trip if it exceeds this nominal current. So dont you think that 2806 is enough for cable sizing. Thank you.