Hi,
We are buying a generator for one of our projects. It is feeding a 690V, 50Hz, 3phase generator of 2600kWe.
The recommended cable size given by the supplier from the generator to the 690V switchboard is 7 x 3 x 1 core x 240sq.mm
Also we are given the In (nominal current) as 2806A and the cable current carrying capacity as 3430A.
Now if I want to use a different sized cable, say 120 sq.mm or 300 sq.mm, I presume that I de-rate these cables(that is 120 sq.mm or 300 sqmm, depending on which I choose) and use the de-rated current to come up with the number of runs.
For example if the derated current for for 120 sq.mm is 254A (before de-rating 319A), then should I use 3430/254 = 13.89 (that is14) runs instead of 7 runs ?
OR
should I use 2806/254 = 11.05 (that is 12) runs instead of 7 runs?.
As "In" should be less than or equal to "Iz" ( that is the current carrying capacity of the cable), I think it is sufficient to use 12 runs.
So my recommendation if we use 120 sq.mm is 12 x 3 x 1 x 120 sqmm.
Am I right?
Thank you in advance.