Transformer Use... in Reverse?

02/27/2008 8:09 AM

Goodday

I am going to be testing a new 55kW induction machine rated at 440V and 93A.

The supply I have in the laboratory will be via an AC generator (driven through a synchronous machine). The AC generator gives me 260V out.

As you may have noticed, I need 440V to the induction motor under test.

To do this I thought of placing the 260V from the AC generator through a transformer (380:220). Unfortunately, the original primary side of the transformer is the 380V HV side.

Can I connect the 260V from the AC generator onto the 220V (original secondary) side of the transformer and use it in 'reverse' so to speak? Or will this saturate the core of the transformer?

I dont see how it should? The same voltage will be applied to both sides (or at least quite close to it as I am placing a slightly higher voltage on it to get the required 440V). The current will thus also be the same if it was operating under normal conditions except that the current will be flowing in the opposite direction.


Your help is greatly appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: Transformer Use... in Reverse?

02/27/2008 8:56 AM

Hello Guest,

A few more details, i am assuming by 440 volts you mean 3 phase...L-L is 440 volts,

1) What is the capacity of transformer in Kva?

2) How do you propose to start the motor? is it by a soft starter or Y/D?

3) What is the capacity of your 3 phase? single phase generator in Kva?

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Anonymous Poster
#2
In reply to #1

Re: Transformer Use... in Reverse?

02/27/2008 12:14 PM

The transformer is a 50KVA 3 phase transformer, the AC alternator is capable of 100KVA. By 440V, I do mean line-to-line. I plan to trim the AC alternator voltage output to the transformer via field control, I can get 0-260V output from it via this. Then the voltage to the motor will vary between 0 and 450V.

Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#3
In reply to #2

Re: Transformer Use... in Reverse?

02/27/2008 1:43 PM

Unless you use a VFD to start the motor, the transformer and Generator both will stretched.

You did not mention the mode of starting the motor...

Good luck.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Anonymous Poster
#5
In reply to #3

Re: Transformer Use... in Reverse?

02/28/2008 12:19 AM

The transformer may be srretched for a very short amount of time though (in terms of minutes), it is only to be run at near rated load for a short load test and then switched off again.

Reply
3
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#4
In reply to #2

Re: Transformer Use... in Reverse?

02/27/2008 4:07 PM

Interesting. Using this scheme would allow you to manually "soft start" using the field control of your generator. Is that what you had in mind?

As far as the transformer goes, it doesn't care which way the power flows. It is also my understanding that when running a transformer at a different voltage than indicated on its nameplate, that it should not exceed its insulation level, which is most likely 600VAC in the case of your transformer.

The next consideration would be steady state current. At 50kVA, the line current would be around 74A on the 380V side and 128A on the 220V side for a delta/delta set-up.

Lastly, talk to the people who made your transformer - they can give you the final word if their unit is suitable for your purpose.

Reply Good Answer (Score 3)
Anonymous Poster
#6
In reply to #4

Re: Transformer Use... in Reverse?

02/28/2008 12:21 AM

The transformer is currently wired in star-delta (220-380), thus if i had the possibility to rewire delta to a star then i could apply 147V to the 220V side and get the required 440V out on the secondary side for my motor. Do you agree?

Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#11
In reply to #6

Re: Transformer Use... in Reverse?

02/28/2008 11:53 AM

I think that you are asking about changing your generator from delta to Wye to match the transformer? (Most transformers I've worked with do not allow such an easy modification ) If so, then yes, I would agree. Although it is not an ideal situation, it is workable. It allows the connection of a neutral to the transformer from the generator. The generator would then supply 147/254 to the transformer, which in turn would supply the 440V to your motor.

Just take into account that your weak point is the transformer. To not exceed the 100% rating of the transformer, limit the current (steady state) to 113A on the low side and 66A on the high side for the voltages you want. Obviously, it is not desirable to run anything at 100% of it's rated capacity for extended periods, and 80% continuous load is usually the rule of thumb (NEC). If this cannot be reasonably controlled, remember to take the ambient temp into consideration as well. Power transformers are fairly hardy, and if you can keep it cool or allow it to cool between starts, it should serve you well.

I know this is not the absolute best solution. Given the current criteria, it is a workable one. Money, time, or both often forces one to choose such a solution. If you can, I would still recommend that you consult with your transformer manufacturer.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8
In reply to #2

Re: Transformer Use... in Reverse?

02/28/2008 5:46 AM

If the transformer is rated 50 KVA at 380 volt, that's about 76 amp per phase. So even if everything else is OK - working "wrong" way round, higher voltage than nominal, question of starting etc, it will be overloaded at 93 amp. You could ask the supplier what he thinks but I'd be amazed if he gives his blessing to higher voltage or current than nominal. He might OK the reverse working, I suppose.

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#7

Re: Transformer Use... in Reverse?

02/28/2008 4:39 AM

If the primary windings are rated for 380V, then driving them at 440V will produce greater saturation effects than connecting them to a 440V supply. (Because of the greater losses at this voltage, the effective step up ration will be reduced). This is likely to saturate the core or at least significantly increase the iron losses. Unfortunately your load is synchronous so you can't raise the frequency by 15% to compensate.

Reply
Associate
United States - Member - New Member

Join Date: Nov 2007
Location: Land of Ahs
Posts: 36
#9

Re: Transformer Use... in Reverse?

02/28/2008 9:26 AM

I've done this with smaller transformers and attained bad results. Llike everyone else has indicated you have to verify you don't exceed your kva limit or rated voltage or current.

If those factors aren't considered you have a good chance to burn the wiring inside the xfmr.

The high voltage side will have a lower current rating than the low voltage side so be sure the motor won't pull more current than the high voltage side is rated. Good luck!! I also want to do this using a pole xfmr for a tesla coil.

__________________
Is it possible to float on light waves?
Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#10

Re: Transformer Use... in Reverse?

02/28/2008 10:44 AM

HI,

Unless the transformer is rated for 50/60hz and you are using it at 60hz the increased voltage will cause damage to the transformer. As others have stated you cannot go above the kva rating of the transformer. Based on your specs I would recommend the transformer be at least 112kva 50/60hz rated and only used at 60hz.

The statement above applies to Sola/Hevi-Duty transformer and I would call the tech servcie dept of the company that built the transformer just to make sure.

Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Apps Man (1); Chankley (1); chaterpilar (2); Codemaster (1); Lendog (2); RidetheWave (1)

Previous in Forum: MOTORS   Next in Forum: how to select electrical cables for industrial use

Advertisement