Anonymous Poster

POWER CALCULATION

03/13/2008 5:37 AM

HOW TO FIND REQUIRED KVAR WHEN PF AND KW IS KNOWN?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#1

Re: POWER CALCULATION

03/13/2008 6:15 AM

1) Turn off Caps Lock.

2) Arithmetic. Divide kW by pf.

__________________
Innuendo is not Italian for a suppository.
Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2
In reply to #1

Re: POWER CALCULATION

03/13/2008 1:52 PM

KW/pf = KVA, not KVAR.

Derivation:

KVA = √(KW2 + KVAR2)

KVA2 = KW2 + KVAR2

KVAR2 = KVA2 − KW2

KVAR = √(KVA2 − KW2)

Since KVA = KW/pf, substitute in the preceding line to get the equation at the top.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Member

Join Date: Jan 2008
Posts: 7
#3
In reply to #2

Re: POWER CALCULATION

03/13/2008 8:23 PM

Another way:

kVA = kW/PF

PF = √ (1-RF2) ; where RF = Reactive Factor

The same way, RF = √ (1-PF2)

KVAr = kVA X RF

Therfore:

kVAr = (kW/PF) • RF

Ain't that simpler?

Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5
In reply to #3

Re: POWER CALCULATION

03/14/2008 8:46 AM

Your approach will certainly work. Not knowing the training/experience of the poster, I was trying to limit the final formula to the two known values. Even so, substituting for RF in your formula gives

kVAr = (kW/PF) * √(1-PF2),

which is still simpler than my approach. It requires fewer calculation steps & reduce the possibility of a math error.

Thanks, SC!

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#4

Re: POWER CALCULATION

03/14/2008 1:10 AM

One way to find required kvar when pf and kw is known is where:= Initial Power Factor Angle, = Final Power Factor Angle (desired pf) but this is not the only way to calculate capacitor bank required for correction of pf, other factor too has to considered such as capacitor voltage, Capacitor Reactance, THD to name a few.

__________________
manirul
Reply
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#6

Re: POWER CALCULATION

03/15/2008 4:33 PM

Power factor is the ratio between KW and KVA.
There are two components of power factor, displacement power factor and distortion power factor.
Displacement power factor is caused by inductive or capacitive loads and is the cosine of the angle between the voltage and the current.
Distortion power factor is the result of electronic circuits on the supply that distort the current waveform. Switchmode supplies and VFDs are both sources of distortion power factor.

If you are sure that the quoted PF is displacement power factor only, then you can use triganometry to calculate the KVAR of the load. If you apply static correction to a motor, it is very important that you only correct 80% of the KVAR of that motor. see http://www.lmphotonics.com/pwrfact.htm

Best regards,
Mark Empson

http://www.LMPhotonics.com | http://www.LMPForum.com

Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#7

Re: POWER CALCULATION

03/26/2008 12:42 AM

Hello Guest,

Assuming your load is 200 kw @ 0.8 pf, and you need to make ithe pf 0.95,

Required kvar = 200 ( tan { cos inv (0.8)} - tan {cos inv (0.95)}).

Now you take it ahead from here...

Cheers.

PS : Avoid using CAPS as human eyes find them disorienting...!!

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers: