03/13/2008 10:46 PM

I changed out a set of service valves today on a 5 ton Heil H/P and added a bi-flow line drier to the line set. I weighed in the charge of 210 oz or about 13.13 pounds. The A/H on this system was changed out 2 days ago so coil and filter is as new. The temp. outside was 68 and inside 70 I checked pressures in cooling the were 62 low side and 175 head. But when I checked it in heat the low side was about 70 and the head just kept going up it was right at 400 psi. If I energized the r/v it would drop back to 62 & 175. This is a R-22 system. Any ideas? I'm thinking expansion valve but every one of those I have seen go bad would pull the low side down.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: High head normal vaper line in heat only

03/15/2008 1:02 AM

Hello Guest

You neglected to mention whether the machine was functioning correctly, before changing the service valves. If You can provide a little more information it would be appreciated.

I will check with a friend tomorrow who has been having similar problem with a Bard heat pump, and see if he has resolved the situation. He has normal pressures in cooling mode, and sporadic high-pressure readings (410 a system) in heating mode. The machine will seem to be functioning normally, and then he will have a return service call for compressor lockout.

I have recently run into check valves that have been damaged in installation by overheating in carrier units. Without further information my best suggestion would be to check the function of any check valves, and confirmed they are installed in the correct direction.

Hopefully my friend has resolve this problem (almost afraid to call him I may get goaded into a service call, if he hasn't.) . If I have any new information I will post it tomorrow.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Reply
Anonymous Poster
#2

Re: High head normal vaper line in heat only

03/15/2008 7:40 AM

70 psig suction in the heating mode seems high.68 dgr oa temp is also quite hi. What is you indoor coil air entering db/wb. What is your air leaving temp. Do you have required air flow. Low air flow will cause hi indoor coil press. The only thing a tev knows is super heat. Check your superheat before suspecting your expansion valve. How are you weighing a charge on a split system. Is the ah and the outdoor unit of the same seer rating.

Reply
Participant

Join Date: Feb 2008
Posts: 1
#3

Re: High head normal vaper line in heat only

03/15/2008 9:49 AM

Guest,

You're posting in the wrong forum.

Try Hvac-Talk.com

Best regards

Reply
Commentator

Join Date: Jun 2007
Location: Missouri
Posts: 86
Good Answers: 1
#4

Re: High head normal vaper line in heat only

03/27/2008 3:59 PM

I ran into this once. What I found was the backup heat source was before the evaporator coil, in this case a gas furnace heat exchanger. When the heat pump was running and the back-up heat came on the head pressure would shoot way up. I set it up where the compressor wouldn't run during back-up heat and then had to set a delay to where the compressor wouln't kick back in until the heat exchanger had cooled down enough not to drive up the head pressure.

Is there anything that could be introducing an unusually high heat load before the evaporator coil?

__________________
I know the rumour is true. I started it and I don't think I would lie.
Reply