Fire alarm system design

03/16/2008 7:39 AM

sir,

is it necesary to install interface units at all lifts and air handling units:for fire alarm system

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: Fire alarm system design

03/16/2008 9:21 PM

I think you will need to supply a little bit more information before you're going to get the answer you're looking for.

When you say interface, if you're looking to shut down the equipment generally the easiest way is to interrupt the control circuits on AC units. This can be accomplished by using a relay controled by the fire alarm panel. As far as the elevators I'm sure something similar could be done.

If you're looking for an alarm interface that would depend on your panel. Standard that detectors, this as well as area smoke detectors can be made to communicate with a" dumb" panel using the relays in the detectors. If you're installing a new system then it would be best to obtain a matched system, that all components interface with the others. Good luck

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply
Participant

Join Date: Mar 2008
Posts: 3
#2
In reply to #1

Re: Fire alarm system design

03/17/2008 12:57 AM

thank you Mr.YWROADRUNNER,

YES THE ANSWER IS QUITE USEFUL AND FURTHER TO GO.. WE ARE USING NEW FIRE ALARM PANEL .. AND AS YOU SUGGESTED I THINK WE MAY HAVE TO USE DUMMY PANEL TO INTERFACE ALL THE SYSTEMS TO SHUTDOWN WHEN THE FIRE OCCURS.

REGARDS

PATRICK

Register to Reply
Commentator

Join Date: Jun 2007
Location: Colorado, USA
Posts: 91
Good Answers: 1
#4
In reply to #2

Re: Fire alarm system design

03/17/2008 7:22 PM

Yes you will have to 'interface' with the air systems and elevators. Depending on where you are in the world, most places with a fire code require that the elevators return to the ground floor (unless that is the one that is on fire). That way the fire teams can use it if they deem it necessary for quick access for those that search. It is always a good idea to have the air handlers shut off, no need to feed the fire, and the exhaust system to turn on. And depending on your fire alarm system, you may not need a dummy panel, it can all be completed within the system with modules.

Good luck,

__________________
Home is where the heart is!
Register to Reply
Active Contributor

Join Date: Feb 2008
Location: Mexico
Posts: 10
#3

Re: Fire alarm system design

03/17/2008 11:43 AM

Patrick:

Check NFPA 72, Fire Alarma System Installation. Refer to:

http://www.techstreet.com/cgi-bin/detail?product_id=1277285

http://www.jbpub.com/catalog/9780763746056/

__________________
Nestor, a.k.a. Agridulce
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Jsquared (1); NestorLeal (1); Patrickg2008 (1); YWROADRUNNER (1)

Previous in Forum: Sizing Electrical Cables and Switchgear   Next in Forum: electric car
You might be interested in: Lifts, Fire Alarm Control Panels, Vehicle Lifts

Advertisement