DG Set Selection Points

03/18/2008 6:19 AM

We want to have an 1000KVA Dg set for our plant. I know capacity of DG set (1000KVA). What are the other points to be addressed while selecting the DG Set i.e. Engine type

Speed High/Low

Cooling Air/Water

etc. - etc.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#1

Re: DG Set Selection Points

03/18/2008 6:45 AM

Ooooh. Loads more:

  • Voltage
  • Frequency
  • Number of phases
  • Fuel type
  • Environmental conditions
  • Size
  • Weight
  • Mounting location
  • Access
  • Fuel tank location
  • Fuel pipe route
  • Exhaust pipe route
  • Local noise emission limits
  • Etc., etc.
__________________
Innuendo is not Italian for a suppository.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2
In reply to #1

Re: DG Set Selection Points

03/18/2008 7:28 AM

Pl check if the DG is for prime or standby power. If the selected size DG is capable to cater starting of highest load while other loads are running.

__________________
BNDas
Register to Reply
Active Contributor

Join Date: Feb 2008
Location: Faridabad India
Posts: 20
#3
In reply to #2

Re: DG Set Selection Points

03/18/2008 7:36 AM

I have checked this. As i have written that capacity wise i have taken all considerations. I want to know other factors which effect the selection of DG set like

Engine type - if any specifeied

cooling - water / air

Speed - High/low

etc-etc

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4
In reply to #3

Re: DG Set Selection Points

03/18/2008 8:03 AM

Have you checked if the DG require harmonic filter? in case DG loads are non linear type.

__________________
BNDas
Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#5
In reply to #3

Re: DG Set Selection Points

03/18/2008 11:21 PM

Please give me your e-mail iD i will send you generator aplication and installation document which will be handy to select your generator you check cummins web site they have welth of information on selection of Generators which can be downloded.

crm

__________________
Run silent run deep
Register to Reply
Anonymous Poster
#9
In reply to #5

Re: DG Set Selection Points

04/28/2009 2:24 AM

good day sir,

please send me the dg selection guide to the email id : syedalik@rediffmail.com

regards,

syedalik

Register to Reply Off Topic (Score 5)
Participant

Join Date: Apr 2009
Posts: 1
#10
In reply to #5

Re: DG Set Selection Points

04/28/2009 3:03 AM

Good day,

please send the dg selection guide to my email id :syedalik@rediffmail.com

regards,

syedalik

Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#8
In reply to #3

Re: DG Set Selection Points

03/22/2008 9:26 AM
  1. As mentioned elsewhere, fuel efficiency & fuel cost should be factored in. Ditto for maintenance requirements - zero kW is available when servicing. Also factor in the availability of spares & service personnel (try 02:00 am on Easter Friday & see who'll respond!)
  2. Depending on your application, you could consider 2x500kVA in stead of 1x1000kVA.
    • Some diesels are not so effective when running on less than 30% load - in such a case a 250kVA load will jump from 25% load to 50%.
    • Also efficiency at full load is typically better than at partial load.
    • Thirdly, depending on application, it is sometimes better to have 500kVA available in case of failure, as opposed to total loss of power (redundancy). As an example, my company seems to have standardised on 250kVA units. We can then have one spare that we can install within 12hrs in most places. We could not keep a 1000kVA spare, nor move it so easily.
    • It is expandable.
  3. Look at the startup requirements. In one of our applications, we let the various aircons come in sequentially, so that the start-up current of the compressors would not exceed the rating.
  4. Keep it simple when you can. I prefer air cooling, but it is expensive and not suited to very dusty/dirty environments. Ensure your cooling system is rated for your worst case temperatures, and for you altitude as well. (Ensure your building does not just re-circulate the hot air!)


Talk to the manufacturers!

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#6

Re: DG Set Selection Points

03/19/2008 12:54 AM

1000 kVA is small for low speed, so at 50 Hz it will be 1500 RPM (4 pole generator). This should be a 12,000 hour before top overhaul, and 25~30,000 hour before total overhaul level speed. If you went with 1000 RPM 50 Hz (6 pole generator) this would add another 15,000 hours to the total overhaul, but the top end overhaul is the same. But a 1000 RPM machine is double the cost, much larger and heavier (maybe 50% larger in bulk). Use water-cooled, individual cylinder heads that one man can lift (some engines have one head for each 2 or 3 cylinders). Inline 8 cylinder is smoothest, but you will not find a inline 8 cylinder in this size except for low speed. Avoid any V-8 configuration as these naturally shake. V-12 or V-16 is smooth. If you have poor quality fuel (heavy fuel) then use the low speed 1000 RPM. For nice number 2 diesel fuel 1500 RPM is OK. Cooling systems are 80% of failures, so, it might be possible to get an air cooled 1000 kVA (check Deutz), but these are expensive and very sensitive to ambient air temperature. Careful with altitude derating for: Power, radiator fan, and air cooling.

__________________
If it eats, it's going to be trouble!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#7
In reply to #6

Re: DG Set Selection Points

03/19/2008 9:08 AM

PetroPower:'s all suggestions are excellent except, I will suggest you to go by heatexchenger cooler. Its trouble free and gives a good cooling during high ambient.

__________________
BNDas
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: DG Set Selection Points

02/04/2014 3:27 AM

Dear Mr.achawla77,

You have stated " WE WANT TO HAVE AN 1000 KVA ......."

From your statement, it conveys a message to this Forum, that you have arrived at the capacity of the DG Set.

It is not clear, from your message,

1. What is the Highest Load - Motor H.P to be started, whether it is to be started on Load or after starting the Motor the motor is loaded.

2. The type of Starter that is used.

3. What is the Percentage of coming on the Generator, If it is less than 60%, Fuel economy will be a problem.

DHAYANANDHAN.S

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!