I have a job troubleshooting a power problem, and this is my first time doing it so I wanted some feedback.
As
of right now I have tried to calculate the demeand placed on the
system. We're running a 30kVA SDMO generator (so in theory 30kW, but I
know that's not the true output).
So, would ya'll please review my numbers and tell me if anything seems too lowballed or highballed?
I'm sorry if I cannot get spacing right, I cannot attach the excel spreadsheet I'm
using and the table function doesn't seem to work (or I cannot figure it out).
Unit number Estimated total
consmuption (W) consumption
LG Split A/C 2 1130 2260
Hitachi Split A/C 2 2900 5800
Sharp Split A/C 2 2150 4300
Sharp A/C 7 1700 11900
Dell GX270* 4 400 1600
Dell 5150* 2 400 800
VSAT ** 1 300 300
HP 1320N 1 345 345
HP 1020 1 250 250
Battery Charger 2 2000 4000
Sanyo Refridigator 1 350 350
Flouresecnt lights 17 36 612
Bulb Lights 4 60 240
IBM Think Pad 2 35 70
Canon Copier (large) 1 648 648
Canon Copier (small) 1 768 768
Coffer Maker 2 650 1300
Canon Scanner 1 100 100
35643
* denotes CPU, monitor, UPS, and Voltage Regulator
** denotes sattelite modem, router, UPS, and Voltage Regulator
Sanyo Refridigator 8.8 cu. Ft. (250L) Frost Free consumption based on half consumption of 16.6 (500L) unit
Power Power Estimated
Produced Factor Production
30000 0,85 25500
With some simple reductions and requests to turn stuff off I've reduced
the estimated consumption to about 26.5 kW which is still over but much
less than the 35.6 kW and after implementation (as of today at least)
the lights aren't flickering anywhere near as much.
And do you have any ideas about stuff that could be done? Adding fans
in place of A/C units is going to happen (in theory). Another generator
running as a secondary and would kick in when the demand required it is
an option but the cost / maintenance requirements make it a last
option. And the cost of a 40kVA unit prohibit an upgrade.