Please review my math on power consumption

03/25/2008 8:53 AM

I have a job troubleshooting a power problem, and this is my first time doing it so I wanted some feedback.

As of right now I have tried to calculate the demeand placed on the system. We're running a 30kVA SDMO generator (so in theory 30kW, but I know that's not the true output).


So, would ya'll please review my numbers and tell me if anything seems too lowballed or highballed?

I'm sorry if I cannot get spacing right, I cannot attach the excel spreadsheet I'm using and the table function doesn't seem to work (or I cannot figure it out).

Unit number Estimated total
consmuption (W) consumption
LG Split A/C 2 1130 2260
Hitachi Split A/C 2 2900 5800
Sharp Split A/C 2 2150 4300
Sharp A/C 7 1700 11900
Dell GX270* 4 400 1600
Dell 5150* 2 400 800
VSAT ** 1 300 300
HP 1320N 1 345 345
HP 1020 1 250 250
Battery Charger 2 2000 4000
Sanyo Refridigator 1 350 350
Flouresecnt lights 17 36 612
Bulb Lights 4 60 240
IBM Think Pad 2 35 70
Canon Copier (large) 1 648 648
Canon Copier (small) 1 768 768
Coffer Maker 2 650 1300
Canon Scanner 1 100 100
35643

* denotes CPU, monitor, UPS, and Voltage Regulator
** denotes sattelite modem, router, UPS, and Voltage Regulator
Sanyo Refridigator 8.8 cu. Ft. (250L) Frost Free consumption based on half consumption of 16.6 (500L) unit


Power Power Estimated
Produced Factor Production
30000 0,85 25500

With some simple reductions and requests to turn stuff off I've reduced the estimated consumption to about 26.5 kW which is still over but much less than the 35.6 kW and after implementation (as of today at least) the lights aren't flickering anywhere near as much.

And do you have any ideas about stuff that could be done? Adding fans in place of A/C units is going to happen (in theory). Another generator running as a secondary and would kick in when the demand required it is an option but the cost / maintenance requirements make it a last option. And the cost of a 40kVA unit prohibit an upgrade.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: Please review my math on power consumption

03/25/2008 10:28 AM

Hello Roldar,

Welcome to the forum.

We wish that you will contribute and learn from this forum.

Before we proceed to your question,here are few general tips to get the maximum out of this forum.

a) Please make your question as detailed as possible, (in this case details were good)...more details you give the better answer you will get.

b) Avoid writing in CAPS as that is considered as shouting in this forum.

c) If any suggestion given by the member actually satisfies you, or does not solve your problem, keep that posted.

d) The members of this forum try their best to solve the problems and do have a very good command on the subject.

e) You will be surprised to see the amount of info, archives hold here..so do a search on here or at Mr Google, and in case you don't get anything you are welcome to post your query.

f) Do not use rude remarks and country/religion/ethnic background/poiltical innuendos, in your comments.

kw = kva * p.f

By your estimation your load is 35 kw so kva = 35/0.8= 43.75

Now your major load is AC, so i would suggest a 50 kva 3 phase gen set with loads of Airconditioners equally balanced on each phase.

This way you will not have the voltage dips which are encountered when A/c kicks in and out.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2008
Location: Guinea by way of Tennessee
Posts: 6
#2
In reply to #1

Re: Please review my math on power consumption

03/25/2008 11:42 AM

Chaterpilar thanks for the info.

We're running a 3 phase unit now (240 V 50 Hz, 30kVA). I've been able to reduce, replace, or drop power to get us at the genny's 25.5kW rating (assuming a PF of .85).

Now I've been looking for info about tapping into each phase individually to balance the load as you suggested. But when I look all I find is colour codes and info about the wiring itselft, nothing about how to tap into each phase individually. As it stands now the power all goes into a big breaker box, so I'm assuming (and I may be wrong) that the box either converts 3 phase to single phase or it just drops phase 2 and 3 and runs on the first phase. Where can I find that info? My onsite resources consist of me and what I can find on the internet.

The power goes from the genny to a breaker box that appears to be completely bypassed (wires tied to the same side of the bus bars) then to a secondary breaker (but all the wires in and out are the same colour). After the office closes and I can poke around without fear of a 240V zap I'll figure all that stuff out.

Register to Reply
Member

Join Date: Mar 2008
Location: Guinea by way of Tennessee
Posts: 6
#3
In reply to #2

Re: Please review my math on power consumption

03/25/2008 12:57 PM

I was making it much more complicated than it is, but correct me if I'm wrong. 4 wires coming out, 3 hot 1 neutral. We tap leg one into 1/3rd the load, leg two into 1/3rd the load, and leg 3 into 1/3rd the load.

how close to perfect do these loads need to balance out? I'm trying to get all the constant use A/C units figured out and then the constant load for the PC's, then the seldomly used A/C units last. But does this need to be a zero sum balance?

For some reason I was stuck in the electronics lab with big oscilloscopes and the 3 phase diagram not the acutal wires and stuff.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#4
In reply to #3

Re: Please review my math on power consumption

03/25/2008 11:38 PM

Hello Roldar,

Can you check the amperes drawn in each of these "hot legs" using a clampmeter ?

Strictly speaking they should not be more than 10 % of each other.

Fo example.. A=10 amps, B=10amps, C= 9amps is ok.....but A= 20 amps B= 4 and C= 5 amps is not OK.

I feel your load is high for the generator you have...and it looks like a classic case of your office and your business growing fast....but gennie is same.

Also please check the voltages A-B B-C C-A and post...

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Member

Join Date: Mar 2008
Location: Guinea by way of Tennessee
Posts: 6
#7
In reply to #4

Re: Please review my math on power consumption

03/26/2008 6:24 AM

The electricain is now an hour late. I hope he has a clampmeter, but I have never seen one in country (not saying there aren't any just a rare find, I've only seen 4 voltmeters). If he doesn't ahve one we'll send out someone to beg, borrow, or buy one. I'll post the results however they turn out.


a 50kVA unit is out of our price range, in fact I think another 30kVA unit to run in tandem with the current one is out of or price range. But that leads me to another question. Do gensets need to be the same rating to be paired up? Or could I run a 20kVA unit with our current 30kVA unit? Evertying I've found online for pairings shows the same unit (make, model, and output), but those are also usually manufacutures websites listing how awesome their products are.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#8
In reply to #7

Re: Please review my math on power consumption

03/26/2008 8:44 AM

Hello Roldar,

Clampmeter as shown in the image.

For industries and factories it is ok, but for offices of your size, i will not suggest synchronising gensets.

I have not seen anybody parralleling 30 kva gensets...other members may differ.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Anonymous Poster
#5

Re: Please review my math on power consumption

03/25/2008 11:56 PM

Dear,

Please, keep in mind that a genset should normally be loaded upto 80% of its maximum rating. This is done to take care of the current surges caused by some equipmemnt starting during the running of the genset taking a higher starting current than what is required during running. The rating mentioned on the genset is maximum. Therefore, care is to be taken not to run it to its maximum capacity.

In the event the connected load increases by addition of some more equipments, the new genset capacity should be chosen in such a way that it is never run below 50% of its rating. It is not in the good health of a genset to run it on a very low load.

S.K. PRUTHEE

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Please review my math on power consumption

03/26/2008 4:34 AM

Hello colleagues,

for the avoidance of wet stacking a generator should be loaded atleast 30% of its rated capacity not 50%.

Good day.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: Please review my math on power consumption

03/27/2008 12:50 AM

Roldar,

I agree that you should not try to put the outputs of two generators together (this is called paralleling to us electricians). It requires some costly equipment to do correctly and can easily be done incorrectly (you will notice many threads on CR4 posted by people who have problems with this). Much easier would be to have a means of carrying part of the load on one and part on another; fancier would be to have a transfer switch which could switch some of the load onto a second generator when the first one gets overloaded.

Pay attention to the comments about % load on the generators. Their engines are going to last longer and need less maintenance if they are loaded to 80% or more of their rating (compared to 30-50%) because the engines will be at or near their designed operating temperature.

From the information in your posts I assume that you are NOT an electrician, but that you have very good technical knowledge and a healthy respect for electrical safety.

Usually people who are calculating the electrical load for a building will include typical values (in units of watts per square meter or square foot area, based on many years' experience) for the general lighting and receptacle loads. Then they will add the power loads such as air conditioning, computer servers, and similar. Your method of calculation is not "orthodox", but still is close enough to the ways I would use. Anything you can do to increase energy efficiency is good.

In your power panel, if it has circuit breakers (usually in one or two columns with handles that move to left or right) with wires attached to these breakers, and has the power wires from the generator attached either to a breaker or to the bus bars, then I can describe how the power is divided. The top breaker is on the "A" phase, the next on "B", the next on "C", then the 4th through 6th repeat "A", "B", "C", and so on until the bottom is reached. Two-pole breakers or three-pole breakers therefore automatically attached their wires to different phases. To see how your load is theoretically divided, make a chart with one column for the loads, and three for the phases. Then starting from the top and going to the bottom you would mark the phases that loads

are connected to. Add each of the three columns and you can see how well it is balanced "on paper". This is what all engineers do. (IMPORTANT--the above description assumes 3-phase power, if single phase, only use "A" and "B".)

Regards--JMM

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); chaterpilar (3); jmueller (1); roldar (3)