Anonymous Poster

Electrical Useage

04/02/2008 7:22 PM

What is out there that can shut off a conveyor, just a motor, gearbox and belt 480v or 110v so when production is done it isn't left on all weekend or having to go around thru the plant and check all them, without spending alot of money

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Electrical Useage

04/02/2008 7:38 PM

A timer switch or timer relay? For the 480 motors it would not be in the 480 line but in the start stop station control circuit.

Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#2

Re: Electrical Usage

04/02/2008 9:58 PM

As stated in #1, timers will work, and should be easy to wire into the start circuit. There are also proximity sensors that could sense the presence of a person or people in selected areas. This would even shut off the conveyor at lunch breaks. just be sure that the start signal is not automatically turned on when a person returns to the area being monitored. good luck.

__________________
Bob
Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3

Re: Electrical Useage

04/03/2008 12:50 PM

Jeez there must be an isolator switch..it just needs someone to switch it off.

It doesn't need complication..it needs education.

There must be a foreman/site manager or someone responsible!

Del

__________________
health warning: These posts may contain traces of nut.
Reply Score 1 for Good Answer
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Electrical Useage

04/03/2008 3:38 PM

What I have used very effectively is a load monitoring relay, something that looks at true kW is best, power factor will work too if you know what you are looking for.

When the conveyor is empty but left running, the motor load goes down. When it does, a load monitor will detect it and start a timer after dropping to a pre-determined threshold. So if it is left running empty for more than a reasonable amount of time, the timer drops out the motor controller for the conveyor motor.

There are several devices like this on the market. The Motortronics RX Series motor protection relay has all of these functions built-in to one device, plus it would act as the overload relay. The Emotron MS20 does it as well. You can also do it with a separate load monitor and a timer, or a programmable relay with an analog input from a kW transducer.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 4)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Electrical Useage

04/03/2008 11:58 PM

Guest,

I like the load sensing relay, because it is independent of the conveyor's layout or components. As others have noted, starting it up automatically is something to be careful with.

Another possibility is a photo-eye which is aimed down the length or at a shallow angle across the area where items are loaded onto the conveyor. When a box or tote is put on, it breaks the PE beam, which will reset the off-delay (if the conveyor is running) or start it (if it is off). PE's are readily available with built-in timing functions, so the output can become the maintained input to run the motor(s). One could also add a Hand/Off/Auto switch to this so the conveyor can be kept on, or kept off, or be under PE control. You wouldn't need to worry about accuracy in setting a motor load sensor and you wouldn't need a separate means of starting it. Only concern would be to ensure that a nearby conveyor's PE didn't happen to falsely trigger the wrong conveyor (it has happened to me when starting up automatic systems).

--JMM

Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2007
Location: Montana, USA
Posts: 357
Good Answers: 6
#6

Re: Electrical Useage

04/04/2008 12:01 AM

As has been previously suggested a simple electro-mechanical timer, controlling a relay would be the easiest and, probably, cheapest way to achieve your desired effect. I have such a timer controlling the fan over my wood stove in the garage, and it would be very simple to use it to control a relay with which to switch higher voltage.

__________________
This is it... so live it up!
Reply
Guru
Popular Science - Cosmology - New Member Popular Science - Paleontology - New Member Popular Science - Weaponology - New Member Popular Science - Evolution - New Member Popular Science - Genetics - New Member Popular Science - Biology - New Member

Join Date: Nov 2007
Location: The Nevernever as much as possible, Earth when I have no choice.
Posts: 665
Good Answers: 11
#7

Re: Electrical Useage

04/04/2008 12:09 AM

Del the Cat said it best: TURN THE THING OFF!! There has to be someone in charge of the plant.

Unless people wander in off the street and just start working.

Pay the last man there a little extra to turn off the lights and the conveyor when he leaves. You will more than make this up in savings on electricity.

Dragon

__________________
Ignorance is the beginning of knowledge. Heresy is the beginning of wisdom. The ignorant heretic is the wisest of all.
Reply Score 1 for Good Answer
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#8

Re: Electrical Useage

04/04/2008 7:47 AM

add timers to control circuits

Reply
Participant

Join Date: Oct 2007
Posts: 4
#9

Re: Electrical Useage

04/04/2008 8:15 AM

There are two ways of doing it, and both have been mentioned on some of the responses.

Option one: Educate the crew to swith off the conveyor as they leave the process area.

Option two: The use of a time delay on the control circuit would help to swith off the conveyor after a pre-set time when product flow is not detected.

The first is the least expensive of the two, and does not require any equipment to be scheduled down for the modification of controls.

Reply
Power-User

Join Date: Jan 2008
Posts: 127
Good Answers: 5
#10

Re: Electrical Useage

04/04/2008 2:59 PM

If you are going to switch the conveyor off automatically you may as well have it turn on on demand as well, if you have a sensor mounted each end of the conveyor to sense product coming onto and leaving and connect them to a vsd with a timer added to the out feed of the conveyor to time product off the conveyor you can automate the process, just need to remember safety. Or get staff to do their job.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#11

Re: Electrical Useage

04/05/2008 9:25 AM

A NC sensor with a gate at the end of the conveyor! If the boxes are not taken off the conveyor before they reach the gate, the sensor goes open thus cutting the hold in circuit! To re-arm, remove the box and press the start button!

This is what we do with the tomato conveyers!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Reply
Guru
Popular Science - Cosmology - New Member Popular Science - Paleontology - New Member Popular Science - Weaponology - New Member Popular Science - Evolution - New Member Popular Science - Genetics - New Member Popular Science - Biology - New Member

Join Date: Nov 2007
Location: The Nevernever as much as possible, Earth when I have no choice.
Posts: 665
Good Answers: 11
#12
In reply to #11

Re: Electrical Useage

04/05/2008 12:21 PM

Truman, Brilliant, and in the long run probably cheaper than paying some one extra to shut it off.

Dragon

__________________
Ignorance is the beginning of knowledge. Heresy is the beginning of wisdom. The ignorant heretic is the wisest of all.
Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#13
In reply to #11

Re: Electrical Useage

04/05/2008 12:55 PM

Didn't I see that play by the Giants just before half time in the super-bowl?

__________________
Bob
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#14
In reply to #13

Re: Electrical Useage

04/05/2008 3:54 PM

The famous double switch and up through the middle play!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Reply Off Topic (Score 5)
Associate

Join Date: Aug 2007
Posts: 48
#15

Re: Electrical Useage

04/07/2008 2:00 AM

All the control cicuits mentioned so far are part of specific requirement, which varies as per the need. It is said necessity is the mother of invention. First spell out your clear requirements and solutions flows out automatically. Human control is always last say in any machine control.

Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); bob c (2); D.Laxman Das (1); Dragonsfarm (2); ekiechle (1); Grochy (1); GUS THE BUS (1); jmueller (1); JRaef (1); Mr. Truman Brain (2); Skeeter (1); user-deleted-1105 (1)

Previous in Forum: Ground Fault Detect   Next in Forum: What is size limit

Advertisement